Anonymous Poster

Current sensor phase angle shift

07/25/2007 5:53 PM

If I want to use the current sensor which has a 1.1 phase angle shift to monitor the main feeder line current, does the phase angle shift of the current sensor has any effect on the magnitude of current I am going to read (monitor)?

Note: I am not using this for differential protection or Watts or VARS monitoring

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Current sensor phase angle shift

07/26/2007 12:27 AM

is that 1.1 phase angle shift a lead or lag shift?

Reply
Anonymous Poster
#2
In reply to #1

Re: Current sensor phase angle shift

07/26/2007 10:13 AM

a lag shift

Reply
Power-User

Join Date: Jan 2007
Location: Berlin (Germany)
Posts: 332
Good Answers: 1
#3

Re: Current sensor phase angle shift

07/27/2007 4:33 AM

Hello,

I do not understand what you mean with "1.1 phase angle shift". Is that 1.1 degrees or plus 10 percent of the period ?

Apart from that, independant of lag or lead, the magnitude will not be influenced as long as your frequency of the monitored signal is low compared with the sensors limit frequency. If, lets say, the monitored frequency is 50Hz, the sensors frequency should be minimum ten times more.
Regards, Uwe

__________________
The sum of intelligence on earth is a constant. And the population grows and grows and .....
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#4

Re: Current sensor phase angle shift

07/27/2007 8:13 AM

Current sensor as in current transformer with additional electronics, Hall effect sensor, or what? Current transformers generally have a low end nonlinearity, as it takes a certain level of magnetizing current to make the thing work. One comment made so far is that the current sensor should have a frequency 10 times greater than the measured frequency. That comment refers to "frequency response" of the sensor. In other words, the sensor would be capable of fairly measuring 50 - 400 Hz linearly, for example. Most sensors or transformers will have a calibration curve associated with them, and if you didn't get one with your sensor, ask the manufacturer for one. The specifications may tell you that the sensor follows the curve within +/- 3% or something like that, so be aware that what you see may not be what you get. If you're trying to get more precise readings without phase shift, there are other ways to do it. Bottom line: Phase shift doesn't mean that you're not getting fairly accurate representation of mains current level. What is does mean, however, is that you're not getting accurate readings at an instant in time. So synchronizing generators to produce power and put it back onto the mains is another animal and should only be done with lots of knowledge and proper equipment, as things blow up when not done just right.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Bill (1); uweka (1)