Interfac Transmitter Calibration

12/16/2015 4:26 AM

There is D/P transmitter for Interface measurment (Oil & water) found Tx Hi side is connected to process bottom tapping and low side connected to top side tank which is closed tank with balnket gas 1kpa.

found transmitter both sides are water side HP/ LP as wet leg also filled with process water . range is 0 to - 4kpa.

i wounder if such correct calibeartion ? please share your view

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#1

Re: Interfac Transmitter Calibration

12/16/2015 9:27 AM

Height of tank and location of D/P cell is critical to calibration range and must be known in order to answer the question.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: Interfac Transmitter Calibration

12/16/2015 9:35 AM

Some thoughts:

1). Since the measurement is interface, for the sake of discussion let's use 'water' for the one medium in the tank, and the word 'oil' for other medium.

2). Interface is typically a level measurement: 'what is the level of the interface between water (on the bottom) and oil (on the top)?', so units of mm H2O or m H2O water column (wc) would be nearly intuitive. But kPa could be converted to percentage of maximum level by an HMI/indicator/read-out.

3). If the tank were filled to the top (same level as the low side wet leg level) with pure water, what would a properly ranged transmitter read as a percentage of maximum level?

Hint: DP reading is high side minus low side (remember, wet leg is water filled)

4). Would this 'all water/no oil' situation represent an 'interface' of 0% or 100% or some in-between percentage?

5). If the tank were filled to the top with pure oil (no water) with a density/specific gravity of 0.8, what would a properly ranged DP transmitter read?

6). Would this 'all oil/no water' situation represent an 'interface' of 0% or 100% or some in-between percentage?

7). If the tank were half full of water, the other half oil, what would the interface level be?

8). What process condition(s) is/are necessary for this interface by DP to function?

9). What other data would be necessary to determine the proper scaling/ranging for the DP transmitter?

10). What has HiTekRednek had to say about similar situations?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Interfac Transmitter Calibration

12/16/2015 12:51 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Interfac Transmitter Calibration

12/17/2015 5:18 AM

Go back to the design documentation for the plant. In there will be an Instrument Specification document for the instrument, a mechanical Hook-up Drawing for the instrument, and a Commissioning Record for the instrument. Further, there will be periodic maintenance Calibration Check documents, dated at intervals from when the instrument was first brought into use. There may well be an HazOp Study record document that mentions it. In a well-managed facility these documents should answer all the questions.

Come back when there is anything on those documents that is not understood, please.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856