12/19/2015 3:27 AM
For negative polarity Zener barrier , the cathode of the zener diode is connected to ground...So how this circuit work for DC supply?? as per my understanding ,by this connection type then the zener diode should be acting as a normal diode and all the current will go through it and no current should go to field!!! please anyone can explain for me especially I am using one with dual channel to supply smart positioner , should I select positive or negative polarity zener barrier ???and why???
Good Answers: 120
Re: Negative polarity Zener barrier
12/19/2015 8:41 AM
Per Ardua Ad Astra
Good Answers: 50
12/19/2015 9:27 AM
Are you using this Zener as overvoltage protection? Or are you using it as a shunt power supply?
See read shunt regulator
ignator -
12/19/2015 9:53 AM
This is zener safety barrier between control system in safe area and fileld instrument located in hazard area.
Good Answers: 50
12/19/2015 1:34 PM
OK, then your using the zener to clamp an overvoltage possibility. There also needs to be a fuse on the power source side, and a series resistor on the load side. The zener only conducts if the power source fails into overvoltage mode, or a fault in the hazard area occurs. So it is selected to prevent damage to the load in the hazard and safe areas. And in normal usage will never conduct current.
See example circuit
ignator -
12/19/2015 4:44 PM
A telephone call to the zener barrier supplier will provide all the information needed.
Good Answers: 225
Re: Negative Polarity Zener Barrier
12/19/2015 8:52 PM
If you're using a negative polarity Zener barrier then ground potential must be positive and the diode will be reverse biased, so it will work exactly the same as a positive potential barrier where ground potential is negative.
12/20/2015 1:52 PM
Primer for all kinds of diodes here.
Good Answers: 122
12/21/2015 10:43 AM
It works for DC supply by limiting the maximum positive voltage level allowed to be applied to the circuit.
The Zener diode does not conduct until the applied (+) DC voltage level exceeds the Zener rating then it goes into avalanche conduction mode thereby draining/shunting all voltage greater than the Zener rating to ground instead of allowing the excess voltage to enter and circulate through the circuitry.
Example: If the Zener is 24 volt rated then it will start conducting all voltage above 24 volts to ground so that the supply is protected from any overvoltage conditions above (+) 24V.