Hello Everyone,
Our cold storage is equipped with a 6-Stage 150 KVAR Automatic Power Factor Controller Panel with capacitors of 5, 10, 10, 25, 50, 50 KVAR. The Panel works perfectly well when the plant is operational and Power Factor is near unity both on the panel and on the electric meter during operational hours. However during shutdown hours power factor reduces drastically.
The PF read by APFC Panel and Electric Meter are different during shutdown hours. APFC Panel reads Power Factor as 1 during shutdown hours, however electric meter usually reads anywhere between 0.2 to 0.5 depending on what load is connected.
Recently, we started to manually keep the 5KVAR capacitor on during shutdown hours and since then our PF has improved significantly as determined by the electric meter readings of Power Factor (which is usually between 0.80 to 0.95 with no -ve sign), KVAH, and KWH. The panel however indicates that we are overcompensating and there is a difference in the PF of the panel and the meter as was the case earlier.
Load connected during Shutdown Period are lighting, fans, and pumps (Borewell).
My Questions are -
1) What is likely causing different readings on the meter and panel (Note:- All loads are connected directly with the main electric panel to which the APFC panel is also connected).
2) Should I be concerned with the overcompensating warnings of the panel.
3) What are some ways in which I can further improve my power factor. Will replacing the 50 KVAR capacitors with a smaller ones, say 1 KVAR help?
Thank you