Micom P63X Differential Relay Setting Calculation Derivation

01/04/2016 2:34 AM

The differential relay operating region equation from the manual of Micom is given as,

1) Idiff > K1 Ibias +Is1

2) Idiff > K2 Ibias - (k2-k1)Is2 + Is1

I would want to know how these equations are arrived at.

I made simple calculations using basic linear equations; Are they right?

Any insights would be appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Micom P63X differential relay setting calculation derivation

01/04/2016 3:37 AM

Unreadable....You might try dividing the paper up into 3 or 4 sections to enlarge, and darkening the lines by using paint program to rewrite...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Anonymous Poster #1
#2
In reply to #1

Re: Micom P63X differential relay setting calculation derivation

01/04/2016 5:40 AM

Dear SolarEagle,

Here is the readable picture,

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Micom P63X differential relay setting calculation derivation

01/04/2016 6:03 AM

Surely a telephone call to the equipment manufacturer's Technical Helpline would be far quicker?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Micom P63X Differential Relay Setting Calculation Derivation

01/04/2016 9:36 AM

The relay manufacturer designates all applicable equations pertaining to their specific relay.

Applicable equations are based on design of the relay circuitry which is proprietary information of the relay manufacturer.

I suggest you contact the relay manufacturer technical support group otherwise you most likely will not get accurate information.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: Micom P63X Differential Relay Setting Calculation Derivation

01/07/2016 11:40 AM

I think you have got the arithmetic right. But you did not define Is1, Ibias. K1 and K2 can be assumed as line slopes.

How the equations are arrived at?

Does that mean how the relay achieves that operating curve? I do not know this relay - it might have a set of rectifiers, filters and amplifiers to do the job or thousands of lines of software.

Does that mean "why does a differential relay have an operating current like this?

Well, even at normal steady load, differences between CTs of nominally same ratio: also plant like transformers with on-load tap changing are going to cause a differential at the relay, without any fault in the protected zone. This is the likely reason for Is1.

At many times normal load (current feeding a fault in plant outside the zone) the absolute magnitude of differential CT errors increases - to counteract this the differential trip point is biased up proportional to the magnitude of the through current. This would be the likely reason for Ibias, K1 dependent slope.

Finally, at very high through currents, serious saturation of CTs will occur causing more differential current error. Also, if one CT is seriously in error, the value of the bias current (say this is the mean of the current in the two CTs) adds more error. This may be reason for a second bias slope line using K2.

A last point, the relay is not perfect, when fed with currents from two CTs, one more distorted than the other, should the relay compare mean, rms or peak and over what time period?

67model

Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

67model (1); Anonymous Poster (1); PWSlack (1); SHOCKHISCAN (1); SolarEagle (1)