Anonymous Poster #1

Energy Meter Reading Coefficient Factor

01/03/2016 12:24 PM

Dear Experts

What will the coefficient factor for a 3Ph energy meter which is designed for CT 400/5A but it is using with CT 150/5A?

And what will be the coefficient factor for a 3 Ph meter which is designed for CT150/5 but it is using with CT 400/5A?

Thanks & Regards

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Energy Meter Reading cofficent factor

01/03/2016 12:54 PM

Depends on the ratio of garbage in to garbage out!

Algebraic Expressions - Jamesbrennan.org

ELECTRICITY METER READING

Do not pass go, do not collect $200.00. Go back to square one and start over.

Reply Score 1 for Off Topic
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: Energy Meter Reading cofficent factor

01/03/2016 1:35 PM

Experts? Here? X-spurt you mean. X is an unknown quantity and spurt is a drip under pressure.

__________________
Good moaning!
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #2

Re: Energy Meter Reading cofficent factor

01/03/2016 4:01 PM

X also equals a has been.

X wife (we'll not follow that path)

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#10
In reply to #2

Re: Energy Meter Reading cofficent factor

01/04/2016 4:44 PM

Almost got it - that's an old joke and it goes:

Definition of expert - a has been drip under pressure.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Energy Meter Reading cofficent factor

01/03/2016 2:05 PM

Exchange the CTs and skip the arithmetic?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9913
Good Answers: 1141
#4

Re: Energy Meter Reading cofficent factor

01/03/2016 2:20 PM

A power meter multiplies the current times the voltage to give power. Current is measured using current transformers (CTs). A current transformer converts the line current to a lower current which is fed to the power meter. CT 400/5A means that a line current of 400 Amps is converted to 5 Amps, a factor of 80:1. So you can do the math.

Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Energy Meter Reading cofficent factor

01/03/2016 4:06 PM

Where did these experts come from? I thought this was an after hours drinking club.

OK, maybe that's where the ex-sperts came from.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Energy Meter Reading cofficent factor

01/03/2016 4:43 PM

This information may be found by:

  • Looking in the instructions that came with the equipment
  • Ringing the equipment supplier's Technical Helpline
  • Looking on the equipment supplier's website

and in that order.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#8

Re: Energy Meter Reading Coefficient Factor

01/04/2016 8:33 AM

We do not do math home work for elementary school students.

Ask someone with more advanced math skills;perhaps a 2nd grader to help you.

If not,go sit in the corner.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#9

Re: Energy Meter Reading Coefficient Factor

01/04/2016 9:56 AM

Here is the first step to solving the equation:

400:5 CT => 80:1 => For every 80 amps of current flowing through the CT primary there will be 1 amp of current flowing through the secondary.

150:5 CT => 30:1 => For every 30 amps of current flowing through the CT primary there will be 1 amp of current flowing through the secondary.

400/150=>2.6667 (Metering error ratio caused by using a 150:5 CT instead of the required 400:5 CT.)

1) If meter reading is 120KW then 120KW x 2.6667 => correct/actual power reading

150/400=>.375 (Metering error ratio caused by using a 400:5 CT instead of the required 150:5 CT.)

Apply required math steps to solve equation.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Score 1 for Good Answer
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!