Current Reading Between VFD Line Side and Loadside

01/10/2016 5:32 PM

I am encountering a problem with our material supply fan which is keep on tripping 2-3 times a day. we can't just shut it down just for try and error system as the whole production will be affected unless we are 100% sure what was the real problem and do it one time... here is it;

Motor size: 12.5kW, Inverter cap: 15 kW, circuit breaker: 20-25 ampps

Checking readings:

Voltage: L1-L2= 432, L1-L3= 428, L2-L3=441

Line side current reading: (from breaker to inverter)

L1= .7 amps

L2= 11.7 amps

L3= 12.7 amps

Load side current reading; (Inverter to motor)

L1= 11.0 amps

L2= 10.3 amps

L3- 10.4 amps

I would say firstly the inverter was faulty. but I need second opinion please, anything could be wrong more?

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Current reading between VFD line side and loadside

01/10/2016 5:51 PM

First: What is tripping? The inverter drive? If so, what's the fault message? There aren't many inverter drives on the market any longer that don't have a fault record.

Second: Unless you have a VERY sophisticated meter, reading anything related to a VFD is pointless, you are not going to get accurate readings.

That said, the 0.7A reading on L1 is still troubling if there is really voltage on the terminals. I would suspect that you are reading by touching the wires, not the drive terminals, and you have a loose input terminal on L1 or a broken conductor inside of the drive between the L1 terminal and the diode bridge rectifier. That would cause all of the current to go through L2 and L3, which would increase by the sq. rt. of 3 on those two terminals and would be over heating the diode bridge.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#5
In reply to #1

Re: Current reading between VFD line side and loadside

01/10/2016 6:54 PM

Hi Jraef, thanks for a quick response, it was the magnetic contactor. as when found tripped they just push the button to be ON, there was a time it was from the breaker.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Current reading between VFD line side and loadside

01/10/2016 7:09 PM

The breaker is undersized, which means the wiring is also. Have a qualified Electrician sort it out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #6

Re: Current reading between VFD line side and loadside

01/11/2016 5:10 AM

If he has O/Ls on the contactor it will trip on imbalance. Shoving a bigger breaker in isn't the answer.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: Current reading between VFD line side and loadside

01/11/2016 6:28 AM

Correct.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Current reading between VFD line side and loadside

01/10/2016 5:55 PM

<...tripping...opinion...>

Could the forum please have the original poster's opinion on the error code that the inverter is displaying, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#8
In reply to #2

Re: Current reading between VFD line side and loadside

01/10/2016 11:42 PM

PWslack,

Thanks, the inverter doesn't show any code. I forget to include on my original post. The history was as per my electrician the original motor was 7.5kW only but when the production add more carding unit the air velocity must be increase to increase the cotton material supply to the units. however few months ago when they replaced the motor from 7.5 kW to 12.6 kW they didn't replace the breaker to 50A.. I considered it was wrong and will be replaced once we replace the inverter. I am wondering why the current reading of line side L1 was only .7amps on that can I conclude that the inverter was the fault triggering the breaker to tripped of or there something wrong besides this?

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #8

Re: Current reading between VFD line side and loadside

01/11/2016 6:32 AM

The whole installation is wrong. Have it redesigned and install it all correctly this time. The trip is doing its job of maintaining the facility's popularity with its fire insurance company.

Upgrading the motor without doing anything else was the cause of the problem. If the inverter and the wiring have survived the experience then write it down to luck.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#16
In reply to #13

Re: Current reading between VFD line side and loadside

01/12/2016 12:16 PM

"The trip is doing its job of maintaining the facility's popularity with its fire insurance company."

Very well said, I might like to borrow that phrase sometime, if I may.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #16

Re: Current reading between VFD line side and loadside

01/14/2016 8:38 AM

There is no copyright on it. Feel free to do so.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Current reading between VFD line side and loadside

01/10/2016 6:29 PM

A 12.5kW motor at 440V ought to have a FLC of around 23A, and the CB should be around 50A. Something doesn't compute here.

If the drive is tripping, there ought be a fault message or code. Or is it the CB that is tripping?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Current reading between VFD line side and loadside

01/10/2016 6:51 PM

<...If the drive is tripping, there ought be a fault message or code. Or is it the CB that is tripping?...>

The Original Poster doesn't say.

<...the CB should be around 50A...>

In that case it is the Original Poster's installation that is wrong, and a local qualified Electrician needs to sort it out using local wiring codes.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2006
Location: Manila Philippines
Posts: 171
Good Answers: 8
#9
In reply to #3

Re: Current reading between VFD line side and loadside

01/10/2016 11:44 PM

Very correct Tornado, anyway we will replace it soon same time we replace the inverter and the wire size will do as well. No fault message displayed on inverter.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #9

Re: Current reading between VFD line side and loadside

01/11/2016 6:29 AM

Then it is useless, and may as well be isolated until it is corrected.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2015
Posts: 335
#7

Re: Current Reading Between VFD Line Side and Loadside

01/10/2016 9:28 PM

0.7A line surely show unbalanced supply.First isolate the problem at line side. what type of drive are using? Quite cheap type, if it does not features error/fault log? Almost all drives, current, is equipped with diagnostics now.

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14

Re: Current Reading Between VFD Line Side and Loadside

01/11/2016 6:18 PM

"Contactors" don't have anything that would trip, so we can ASSume (because you didn't say) that this is a STARTER, which is a contactor + an overload relay, and it is the overload relay that is tripping, which drops out the contactor. In that case, it has nothing to do with the drive.

Now the 0.7A current reading makes more sense. MOST LIKELY, because none of us are there, what is happening is that one pole of your contactor has burned or failed open in some way. So the current through the starter is single phase. The VFD doesn't actually care, because it will manufacture 3 phases going to the mot0or from the DC that it creates from the (now) single phase AC source. So other than the input current being 173% higher on those 2 phases than it should be, the VFD is not seeing anything to trip on, at least not yet.

But before that might happen, the OVERLOAD relay is reacting to the single phase condition by tripping early. IEC overload relays have an ability to sense a single phase condition and react to it by biasing the overload trip point down. So the current is increasing to 173% of normal, and at the same time, the OL relay is lowering it's trip threshold so it turns the contactor off. If it were a Solid State OL relay, it would likely reacting immediately, but my guess is that it's an old fashioned bi-metallic OL relay that takes a while to react.

Also, having a contactor AHEAD of a VFD is not a great idea anyway and even if you need it for some perceived safety issue (there are better ways to accomplish that), there is ZERO reason to have an overload relay associated with it. The VFD is now the OL relay for the motor, all you need for the VFD is basic short circuit protection.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#15

Re: Current Reading Between VFD Line Side and Loadside

01/12/2016 12:31 AM

What is the output voltage?

Power in is approx power out.

I agree with Raef - look for single phasing input.

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#18

Re: Current Reading Between VFD Line Side and Loadside

01/15/2016 12:51 PM

By the way, if your contactor is between the power supply (substation) and the VFD, you have two other problems.

First, the VFD manufacturer is probably not happy with you turning it on and off this way. The problem comes from all of the energy rush to charge up the DC power section from which the output transistors draw energy for your motor. This rapid build up of energy into the DC section will exceed your contactor ratings, but because it is over quickly enough, the thermal overload section (a separate module) may not heat up enough to trip. Initially this may work, but the relay points (contacts) will degrade rapidly.

Second, each time you switch the power on and off, you are placing a large capacitor bank in parallel with the substation windings. So, you have a nice big L-C tank circuit which can bounce very large currents through the contacts causing them to pit and vaporize little by little until you start blowing fuses or breakers.

Generally, it is best to leave the power to the VFD most of the time. It should not be turned off and on more than twice per day. Otherwise, the inrush currents are going to make you spend some serious money.

If you already have a burnt contact (as in the low current for L1) then the arcing that is going on is what is tripping your safety device. The more it arcs, the more it heats up with surge currents.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: