Question on Plug Setting Multiplier in Protective Relays

01/11/2016 5:29 AM

Dear Sirs,

The plug setting is used to increase/decrease the pickup current setting and the Time Multipler Setting(TMS) is used to increase/ decrease the time delay.

what is the purpose of computing Plug Setting Multiplier(PSM)? Is it just used to calculate the operating time for the relay to trip at a given fault current using the IEC/IEEE curve equations?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Question on Plug Setting Multiplier in Protective Relays

01/11/2016 5:56 AM

This is not a good candidate for an anonymous question. Sorry.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Question on Plug Setting Multiplier in Protective Relays

01/11/2016 6:34 AM

Click HERE

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Question on Plug Setting Multiplier in Protective Relays

01/11/2016 6:34 AM

Please specify the manufacturer and part number of the equipment in question.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#5
In reply to #3

Re: Question on Plug Setting Multiplier in Protective Relays

01/12/2016 2:49 AM

Dear Mr PWSlack,

Rephrasing my question, PSM = ratio of fault current to the pick up current. Here why the fault current is included in the formula of plug setting multiplier, as we have already assumed the fault current to be the maximum load current expected.

BTW, there is no relay, I've just started studying the basics of overcurrent protection.

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: Question on Plug Setting Multiplier in Protective Relays

01/12/2016 3:44 AM

Click on the link i provided, open the first website in the list and your question will be answered.

I always thought research was a part of the study process, time have changed.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster #1
#8
In reply to #6

Re: Question on Plug Setting Multiplier in Protective Relays

01/12/2016 5:56 AM

Dear Mr. Tony,

That was a good reference, but still I have some questions. Basically PSM of any value greater than 1 is fault current and the relay should operate for PSM of value above 1. So why don't consider always plug setting multiplier as 1 and then calculate the actual time of the operation from the Time/PSM graph.

Why should one find the fault level of the apparatus to be protected? My assertion is that finding the fault level and calculating the operating time of the relay at that fault level might help in relay co-ordination to set the upstream relays. Is this right?

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #5

Re: Question on Plug Setting Multiplier in Protective Relays

01/12/2016 3:48 AM

That seems painfully evident.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #5

Re: Question on Plug Setting Multiplier in Protective Relays

01/13/2016 6:25 AM

The basic current of a traditional relay was 1 amp or 5 amp. Being a wound-coil device, other special values of basic current were possible. Operating curves are the same, being in multiples of the basic current which was given on the relay rating plate.

In converting a primary actual fault current to a relay setting one must include CT ratio and basic relay current.

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: Question on Plug Setting Multiplier in Protective Relays

01/11/2016 10:27 AM

If you're a consultant posing as a protection engineer then you're in over your head, if this is an interview question then be glad that you didn't get the job.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply