Anonymous Poster #1

Life Assessment for Power Cable

02/05/2016 2:42 PM

What are the steps to be taken to help decide whether or not to replace a 10 km, , 132KV-1C-630 sq mm-cu -XLPE-LC-PVC- Underground cable installed 15 years ago for essential service and partially loaded?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Life assessment for power cable

02/05/2016 3:20 PM

Excess loss of current, overheating....why would you want to replace this wire?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: Life assessment for power cable

02/05/2016 3:44 PM

Gophers, maybe?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 2 for Off Topic
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#3

Re: Life assessment for power cable

02/05/2016 3:47 PM

I would look at Megohmeters. I've used them for underground cable testing in wet and dry locations, but nothing close to the magnitude you're dealing with so please follow up with more research!

With loads disconnected (the way I was taught)you can simply connect a hot and a ground or to another cable in the bundle. Flip the switch to read resistance and determine if there are hairline or other invisible damages to the cable/insulation. Don't touch as the cable is now energized with high voltage so that any leakage to ground or between cables can be identified. More advanced units that are available for rent will tell you the exact distance to areas of cable damage should hidden damage be one of your concerns.

\I'm with SolarE on this one. Why?

__________________
High Tolerance is Beautiful
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#4

Re: Life assessment for power cable

02/05/2016 6:48 PM

Calling the manufacturer and talk to their engineering department. Of course, their main interest may be selling you another cable.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Life assessment for power cable

02/05/2016 7:06 PM
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#15
In reply to #5

Re: Life assessment for power cable

02/07/2016 12:28 PM

Thanks,lyn.

__________________
Julius
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Life assessment for power cable

02/05/2016 7:08 PM

The first step is to decide why this replacement is even needed for reasons other than "it might fail", then decide if it's really worth approximately 500,000USD just for the cable, not including installation (plus zeroUSD for engineering).

Again, why are you suggesting that it be done?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Life assessment for power cable

02/05/2016 9:39 PM

15 years isn't a long period if the cable hasn't been abused.

I can think of better things to waste money on.

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 2)
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#8

Re: Life assessment for power cable

02/05/2016 10:33 PM

I think he's the guy selling the cable... It's the only thing that makes sense..

__________________
High Tolerance is Beautiful
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Life assessment for power cable

02/05/2016 10:38 PM

Would you buy cable from an anonymous poster?

Reply
Power-User

Join Date: Jun 2007
Location: Center of the Known Industrial Universe - TUGGERAH 2259 - Australia
Posts: 259
Good Answers: 52
#10
In reply to #9

Re: Life assessment for power cable

02/06/2016 1:47 AM

Don't ask the manufacturer, after 15 years, if he will guarantee the cable is still good, instead refer to his 15-year-ago warranty terms.

Don't ask any merchants whether they suggest you replace the cable, as their answers will be "YES".

If you're going to replace it anyway, don't use any product of INFINITY ELECTRIC CABLE or there will be tears before bedtime:

http://www.news.com.au/finance/money/cable-girl-scandal-could-cost-80-million/news-story/6f8af4d1590fd580b234c98f1b1ada5c

Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#11
In reply to #9

Re: Life assessment for power cable

02/06/2016 6:32 AM

He's looking for reasons to replace a cable and searching for any way to make the cable owner beleve his assessment.. Im kind of joking.. But not really.

__________________
High Tolerance is Beautiful
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#12

Re: Life assessment for power cable

02/06/2016 6:47 AM

About 20 years back I diverted a cable that had been installed in the early 50's. Initially it tested a bit low on IR but once more load was placed on it the readings were well above acceptable readings.
65 years old and it's still in use today, pity the same can't be said of me.

15 years is nothing in the life of a cable which makes me think there's more to this than meets the eye. The weak spots are usually the joints, they can be chopped out and new sections spliced in. A damn site cheaper than replacement of the whole length.

__________________
The reports of my death are greatly exaggerated.
Reply
Anonymous Poster #2
#13

Re: Life assessment for power cable

02/06/2016 7:37 AM

Take a big step to the telephone and call me. Excellent rates.

Reply Off Topic (Score 6)
2
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#14

Re: Life assessment for power cable

02/06/2016 1:53 PM

Around here underground cabling service life is based on how many repairs it has had done to it and why over its lifetime.

If the 10 KM in question has never had any service work done to it other than for accidents due to human or natural events it would be considered 100% functional and thus have no immediate warrant for its replacement.

Now however if the 10 KM cable has experienced multiple burnouts and or shorts of no determinable external causes other than defective design in a matter of only a year or so of use then yes its replacement would be worth considering.

Reply Good Answer (Score 2)
Participant

Join Date: Feb 2016
Posts: 2
#16

Re: Life Assessment for Power Cable

02/08/2016 9:09 AM

Purchase and download a copy of the IEEE 400 series of test methods. They will explain everything you need to know to about cable testing and assessment methods. That said, your cable should be have metallic barrier tape to keep out moisture, so a 15 year old cable is very young and shouldn't need any assessment much less replacement. If you have underground splices, there are testing companies that can test those off-line to make sure they don't have excessive partial discharge

Reply
Anonymous Poster #3
#17

Re: Life Assessment for Power Cable

02/08/2016 9:21 AM
  1. Is it essential that this cable not fail?
  2. Is there a redundant cable to provide the essential service if this cable fails?

If the answer to #1 is Yes (as it appears to be by definition) and the answer to #2 is No, than you need to lay a redundant cable ASAP.

Once you have the redundancy, you can check each cable in turn, monitoring it for current loss and voltage drop. If a cable starts losing more current or dropping more voltage that the spec sheet allows for the installation, then it's time to replace.

This is why you have the redundant cable, so that while one cable is being replaced, the other is supplying the essential service power.

You already knew this was an embarrassing question, or you wouldn't have posted as an anon, so think through your basic troubleshooting before coming here to ask us to do your work for you. Say goodnight, Gracie.

Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#18
In reply to #17

Re: Life Assessment for Power Cable

02/08/2016 9:58 AM

There is no way a company will install a redundant cable these days with all the cable joints required plus additional trenching or/and ducting. 630mm2 XLPE 132kV Cu cable? Reality check here gents.

BoM: Min requirements

2 terminations

18 cable joints

18 ferrules

10km of trenching, possibly with a PVC duct to install.

18 joint pits

+10km of Copper earth conductor, 120mm2 (min)

Back fill Sand or CBS

Spoil disposal.

Etc, etc

Plus labour plus permission to excavate land, if it crosses any public land. If it is on company land the cost is negligible.

Now what company is going to invest in this daft idea of replacing one single feeder for redundancy? Three yes, but one? Very questionable. If they did anything they would go over head with all the phases and save a fortune and simply upgrade their entire feeder and keep the UG cables, soaked, but not loaded, as the back up feeder.

45 Years for UG system and approx 80 yrs for OHL and UG costing about 6-10 times more in costs.

Do the mathematics and apply logic here. Hint: concrete monopole or 'H" frame wood pole line. XLPE, CU screened, XLPE, 630mm2Cu is approx 17kg per meter and I would guess in the USA around $100.00+ per meter, just for the cable and nothing else.

If doing a project, before doing anything get the facts, get all current costs, complete all risks and then consider the questions carefully, "What are our options?" What is the cost? And 'How important is this really?

Reply
Anonymous Poster #3
#19
In reply to #18

Re: Life Assessment for Power Cable

02/08/2016 10:35 AM

Perhaps we have different definitions of 'essential.'

I take it to mean 'this is a service that cannot be interrupted for even a fraction of a second or people will DIE.' Things such as Hospitals.

The OP did not identify the 'essential service' this cable was feeding, so I had to assume the 'worst case scenario' for 'essential,' the 'cannot tolerate any interruption' scenario.

Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#20
In reply to #19

Re: Life Assessment for Power Cable

02/08/2016 11:40 AM

No idiot bean counter is going to waste thousands on installing a cable for the sake of redundancy, after the fact, 15 years after the fact. The Poster provided no real answers, no facts worth bothering over. And is pulling everyone's leg.

If this was for real, the project would possibly have gone to tender, to mitigate risk, keep costs low and all due dilligence would have been completed by a consultant team.

Reply
Reply to Forum Thread 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!