Participant

Join Date: Jan 2016
Posts: 4

Separation Between 25 kV Power and Insulated Neutral Cable

02/04/2016 11:43 PM

Could anyone could suggest me what the separation would be from 25kv power and insulated neutral cable when routing same above ground cable tray from transformer to switchgear building. I found in CSA that power cables shall be 2D from centre to centre and there shall be separation between power cable to communication cable but whats about power cable to insulated neutral cable?

Register to Reply
Pathfinder Tags: TXNW26DC
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Separation between 25 kV power and insulated neutral cable

02/05/2016 12:35 AM

Exactly what is the specification for the power cable, especially its construction. I do hope that you're putting these cables in their own tray, totally segregated from any other cables.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Participant

Join Date: Jan 2016
Posts: 4
#2
In reply to #1

Re: Separation between 25 kV power and insulated neutral cable

02/05/2016 12:52 AM

power cables are 25 kv XPLE and I make separation between cable 2times dia of cables centre to centre. I am planing to put 2-4/0 insulated neutral cables in same tray along with power cables which are coming from same transformer 25 kv secondary. I would be separation between power and neutral cable as per csa or NEC

Register to Reply Off Topic (Score 4)
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#8
In reply to #1

Re: Separation between 25 kV power and insulated neutral cable

02/05/2016 6:54 PM

As long as your Cat-6 cables are rated for 25 kV what's the problem?

Register to Reply
Participant

Join Date: Jan 2016
Posts: 4
#3

Re: Separation between 25 kV power and insulated neutral cable

02/05/2016 12:56 AM

power cables are 25 kv XPLE coming from 3 phase of one transformer and I make separation between cable 2times dia of cables centre to centre. I am planing to put 2-4/0 insulated neutral cables in same tray along with power cables which are coming from same transformer 25 kv secondary. I would be separation between power and neutral cable as per csa or NEC

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Separation between 25 kV power and insulated neutral cable

02/05/2016 1:14 AM

If you stick with 2D, that will almost surely be conservative on account of the lesser voltage difference. (Assuming equivalent insulation.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Feb 2016
Posts: 2
#11
In reply to #3

Re: Separation between 25 kV power and insulated neutral cable

02/08/2016 8:26 AM

You need to remember the purpose for the separation. Cables are primarily separated for either voltage reasons or thermal reasons. The voltage reason doesn't apply in this case and since the neutral isn' t a current carrying conductor in a balanced 3-phase system with low harmonic content, the thermal reason doesn't apply either. So, separate the cables per the code requirements (which are based on thermal requirements) and put the neutral cable anywhere convenient in the same tray.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#5

Re: Separation Between 25 kV Power and Insulated Neutral Cable

02/05/2016 4:29 AM

Is this non-metallic tray, Mildred, or are the cables required to be 2D from any earthed part too?

__________________
Good moaning!
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #5

Re: Separation Between 25 kV Power and Insulated Neutral Cable

02/05/2016 6:48 AM

Good question, just to add the cleats are often aluminium although plastic versions are available. I've never used the plastic version so don't know much about them.

I've always run MV in aluminium trefoil cleats so find the 2D separation of conductors strange. Whatever cleat is used it must be able to withstand the magnetic repulsion during fault conditions.

Ft = (0.17 x Ip²)/S
Where
Ft = Maximum Force per unit length of cable (N)
Ip= Peak short circuit current (KA)
S = Centre to centre distance between neighboring conductors

http://www.youtube.com/watch?feature=player_detailpage&v=HmnrJa7Zk0A#t=84s

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#7

Re: Separation Between 25 kV Power and Insulated Neutral Cable

02/05/2016 10:35 AM

I'm startled that your Client's specification doesn't tell you that, Mildred. What a bummer of a contract!

__________________
Good moaning!
Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Separation Between 25 kV Power and Insulated Neutral Cable

02/06/2016 12:29 AM

NEC 2014

392.20 Cable and Conductor Installation. (B) Cables Rated Over 600 Volts.

Cables rated over 600 volts and those rated 600 volts or less installed in the same cable tray shall comply with either of the following:

  1. The cables rated over 600 volts are Type MC.
  2. The cables rated over 600 volts are separated from the cables rated 600 volts or less by a solid fixed barrier of a material compatible with the cable tray.
__________________
Julius
Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#10

Re: Separation Between 25 kV Power and Insulated Neutral Cable

02/06/2016 7:32 AM

And what has your Site Manager and Project Manager to say about this spacing. Perhaps asking the client or the consultant maybe a better advantage than arbitrarily asking people on this site.

I have no doubt that you have no idea about installing the cables from the Tfx on cable trays whether flat formation, trefoil, spaced, touching and where you should install the other cables for control; Bucholtz, alarms, tap changer etc.

Approved design drawings provide all this detail, you really should look at them and clarify any anomalies with the designer and consultant. (If a new build, and on existing build, still check with the designer and discover what standards he is using and referring to for your local build/repair).

God help, your cable bend radius if you don't know the spacings.

Register to Reply