3rd Floor Water Pressure

03/02/2016 10:22 AM

Will wyeing an additional feed from the same manifold increase pressure to a 3rd floor shower? Hot & Cold manifolds each have an unused port. if I wye from the unused ports into the lines feeding the 3rd floor shower, will the pressure improve?

Register to Reply
Pathfinder Tags: Shower water pressure
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2010
Location: Wales, UK
Posts: 391
Good Answers: 18
#1

Re: 3rd Floor water pressure

03/02/2016 10:31 AM

No, the flow might increase but not the pressure.

John

__________________
Best advice I can give as you get older "Never miss an opportunity to relieve yourself"
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#2
In reply to #1

Re: 3rd Floor water pressure

03/02/2016 10:43 AM

While I agree static pressure won't increase, dynamic pressure should increase.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#3
In reply to #2

Re: 3rd Floor water pressure

03/02/2016 11:44 AM

Will an increase in dynamic pressure increase the flow through a large shower head? The flow currently simulates a gentle rain while a more stinging flow is preferred. Any way to make this happen w/o running larger diameter feeds? There is no flow restrictor in the valve or head. Thank you.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#4
In reply to #3

Re: 3rd Floor water pressure

03/02/2016 11:55 AM

Running parallel feeds from the manifold to the shower head should give you an increase in dynamic pressure at the shower head, which would increase flow from the nozzle (shower head).

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#21
In reply to #4

Re: 3rd Floor water pressure

03/13/2016 9:29 AM

Can't run parallel feeds to the shower head but can wye from existing lead to a second port on the manifold but that won't help, will it?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #3

Re: 3rd Floor water pressure

03/02/2016 12:22 PM

Adding an additional line should increase the flow...but why not just replace the existing line? If the water pressure varies between the sink or other fixtures at this same level then the line may be restricted due to scale build-up....maybe you just need a smaller shower head.....I think they all come with a restrictor ...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#6

Re: 3rd Floor Water Pressure

03/02/2016 12:51 PM

You lose about 1/2 psi for every foot of elevation.

Check your shower head. Lots of times, in the interest of saving water, there is a restrictor installed to limit water flow. If this is removable, removing it will give you more pressure.

Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#7

Re: 3rd Floor Water Pressure

03/02/2016 2:05 PM

What is the size of the main coming into the building? What's it made of?

The pressure is alway higher when no fixtures have been in use.

There is a PSI drop each floor floor must go up. Larger lines have larger drops.

Simple solutions? none. pressure increasing tanks/boosters available for $

Ask the city how much a new main line would cost and what size pressure it should be? That may be the easiest solution.

__________________
High Tolerance is Beautiful
Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#8
In reply to #7

Re: 3rd Floor Water Pressure

03/02/2016 3:23 PM

1 1/4" black plastic pipe from the well to 3/4" pex to copper manifolds in the basement w/ 1/2" pex to each fixture. Each of the manifolds has a spare port from which I can wye into the lines going to the shower. The shower heads have no restrictor plugs in them.

It 's sounding like we might need to be satisfied with what we've got, as running additional or larger lines is a big problem; there is no chase.

Register to Reply
4
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#11
In reply to #8

Re: 3rd Floor Water Pressure

03/02/2016 5:53 PM

As you're drawing from a well then replacing the existing pump with one with a greater head and higher flow rate may solve your problem, talk to your local pump supplier.

Register to Reply Good Answer (Score 4)
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#12
In reply to #8

Re: 3rd Floor Water Pressure

03/03/2016 12:37 AM

Since you are on your own well (deep or shallow?) and have your own pump system what is its present cut in and cut out pressures?

Typical modern residential should be running between 50 - 60 PSI cut out and 30 - 40 PSI cut in. IF yours is considerably lower than that and you have one of those stupid water saver restrictors in you shower head that would be a very good reason for your crappy shower pressure.

As for changing out pumps I would not go that far yet unless the one you have proves itself to be incapable of getting up to 50 - 60 PSI after adjusting the pressure switch.

I'm on my own well and I have my water system set for ~60 PSI at the house and I run a double shower head with the water saver disks drilled out which is quite a contrast from what I grew up with being back then we maybe had 25 PSI on a good day and an ancient rusted up shower head which meant most days you timed your shower to be when the animals were least likely to be drinking just so you could have enough water flow (determined trickle) to get the soap off.

Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#20
In reply to #12

Re: 3rd Floor Water Pressure

03/13/2016 9:23 AM

Pressure is fine at sinks, tub and toilet on same floor - only problem is shower. No restrictors in shower heads (Large double walk-in shower). Each fixture is fed individually from the manifolds. The valves do have scald control.

Register to Reply
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#18
In reply to #8

Re: 3rd Floor Water Pressure

03/03/2016 4:51 PM

1/2" pex is IMHO a lousy choice for anything other than short branch feeds. It has a smaller ID than 1/2" copper, and even with the fact your plumber could (hopefully!) have run this with no elbows you still have 3 floors plus whatever the horizontal run is- easily 30 feet or more.

Since this is a well fed system, Have you checked your your pressure setting as per tcmtech's post? I doubt you would find changing the pump to make any difference, but running at 50-70 psi instead of 30-50 would.

Otherwise, just install hot and cold pressure tanks right by the shower!

Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#19
In reply to #8

Re: 3rd Floor Water Pressure

03/13/2016 7:26 AM

My take on this is that you are pumping from your own well, is that correct? if so and you don't want to fit a higher pressure pump then I would put a storage tank in the roof space or if no attic on a flat roof (well insulated and covered) & equalise the hot & cold pressure, I'm no lover of tanks but unless you can UP the pressure I can see no other cure, You must make sure that both sides are equalised. Just another point are you using thermostatic valves? these will stop anyone being scolded.

Bazzer

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#10
In reply to #7

Re: 3rd Floor Water Pressure

03/02/2016 4:00 PM

"Larger lines have larger drops". A PSI is a PSI. Line size does not matter.

Friction loss will decrease with larger lines and increase with velocity.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#16
In reply to #10

Re: 3rd Floor Water Pressure

03/03/2016 7:31 AM

And that's what I meant. As in a larger line won't matter.

__________________
High Tolerance is Beautiful
Register to Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#9

Re: 3rd Floor Water Pressure

03/02/2016 3:36 PM

If you have scald protection built into the shower handle it may also be a culprit.

Remove the valve and wash what happens.

__________________
High Tolerance is Beautiful
Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#17
In reply to #9

Re: 3rd Floor Water Pressure

03/03/2016 8:29 AM

It does have scald protection; is that something that can be removed/adjusted? I'll check that when I get back home in a couple of weeks.

Register to Reply
2
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#13

Re: 3rd Floor Water Pressure

03/03/2016 5:05 AM

Have you considered a shower pump?

Do a local google search for "shower pump" and/or "power shower".

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#14
In reply to #13

Re: 3rd Floor Water Pressure

03/03/2016 5:48 AM

Those type setups require a feed tank or some form of water reservoir prior to the shower pump in order to function correctly.

If you were to simply install it inline, then - when using the shower - turning on any other taps between the mains/main pump would result in, at best - low flow from the other tap, or at worst - air being drawn into the pipe through said tap and up to the shower pump.

I would expect that an examination of any literature pertaining to those pumps would advise that they are only for use on gravity type systems.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#15
In reply to #14

Re: 3rd Floor Water Pressure

03/03/2016 6:09 AM

GA, thanks, I was tempted to buy one for my pathetic dribble of a shower. Have to investigate more.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#23
In reply to #14

Re: 3rd Floor Water Pressure

03/13/2016 9:37 AM

Was considering the shower pump until I read your entry. It's looking like the pressure I've got what is what I'm going to have to live with unless the mixer valve can be changed/eliminated.

Register to Reply
Associate

Join Date: Feb 2011
Location: Located in NY - Territory is North America
Posts: 25
#22
In reply to #13

Re: 3rd Floor Water Pressure

03/13/2016 9:31 AM

That might be my only solution. Thank you.

Register to Reply
Register to Reply 23 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bazzer Englander (1); Gene Schoonmakerfranczek (7); JE in Chicago (3); jesw55 (1); JNB (1); lyn (1); Randall (2); Rixter (1); SolarEagle (1); spades (2); tcmtech (1); WJMFIRE (2)

Previous in Forum: Relativity: Coming to Terms: Relative Velocity and Time Dilation   Next in Forum: Sugarcane Leaf Bailing & Shredding

Advertisement