Air conditioner sizing

07/31/2007 7:31 AM

dear friends

i would like to know the size of air conditioner for ship bridge with area 4*3m 2.2m heigt , four wall sides are glass and 4 crew all time in bridge , no heat source.

hesham nabil

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: air conditioner sizing

07/31/2007 7:42 AM

No heat source sounds implausible. What conditions is the ship operating in? Air conditioning is probably unneccessary at latitudes exceeding 55degrees. How well is the room insulated?

__________________
Good moaning!
Register to Reply
Associate

Join Date: Jan 2007
Location: Canada
Posts: 38
#2

Re: air conditioner sizing

07/31/2007 7:50 AM

A very small one!

In general you use 1 ton of cooling for every 400 square feet of space. Do all of the calculations you want but this is pretty accurate and it usally comes pretty close to the complex solution. You have 130 square feet. Therefore you would likely use 1/2 tons of cooling.

Register to Reply
Power-User
Engineering Fields - Marine Engineering - New Member United Kingdom - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Jun 2007
Location: Birmingham UK
Posts: 253
Good Answers: 1
#3

Re: air conditioner sizing

07/31/2007 7:54 AM

Yup! The people give off heat, the structure passes heat form the accommodation underneath, from the sun outside, from the electrics etc inside. In fact as with all calc's in this area you need to calc your heat load max - min in all latitudes, hottest to coldest. Then you need to know the number of air changes you want? Is there a toilet or smokers? Come-on give us some more details.

__________________
Reset, Reset
Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 19
#4

Re: Air conditioner sizing

08/01/2007 1:53 AM

Hi Hesham,

You could try using the u value figures from the Ashrae design manual for the structure that you are dealing with, plus add for ventilation and body load. Usually something like the following. bare glass U val. is 6.5watts per m2 * TD . Be aware though that the Ashrae figures are worked on something like an outside air speed of 5 ms. I would imagine that on board a vessel at sea you would have to allow somewhat more than that.

regards

Coben

Register to Reply
Active Contributor

Join Date: Apr 2007
Posts: 19
#5
In reply to #4

Re: Air conditioner sizing

08/01/2007 2:02 AM

OOPs, try SQM * 6.5 * TD

From the pshychrometric chart enthalpy scale

ventilation will be something like Kj per Kg dry at start less Kj per Kg dry at finish giving KJ to remove * weight of dry air * volume of air being moved by the fan/s, converted from Kj to Watts. This will include room volume plus ventilation.

regards

Coben

Register to Reply
Active Contributor

Join Date: Apr 2006
Posts: 13
#6

Re: Air conditioner sizing

08/01/2007 2:28 AM

sizing an air conditioning system requires calculations of heat loads. this process is complex to a non-HVAC engineer. however, there are certain nominal figures they use. depends on your location around the world these vary from place to place and from time to time. take the maximum load for sizing less diversity factor. your 12 sq. m. area would probably need 1 Ton of Refrigeration (3.517 kW) considering that radiation and conducted load would be the greatest loads. internal load would come from occupancy and fresh air loads. the above size is equivalent to 3.4 m2/kW (ave.) similar to a public area.

Register to Reply
Associate

Join Date: Jun 2007
Location: Lexington, Kentucky, USA
Posts: 33
#7
In reply to #6

Re: Air conditioner sizing

08/01/2007 6:22 AM

My experience in ships in the tropics is to use the biggest unit you can afford. With all the windows on the bridge, no insulation, the electronics operating 24 hrs a day and the crew entering and exiting all the time you are going to need all the cooling you can get.

Mike

__________________
"A designer knows he has achieved perfection not when there is nothing left to add, but when there is nothing left to take away." Antoine de, Sant-Exupery
Register to Reply
Commentator

Join Date: Oct 2006
Location: Northern NY
Posts: 89
Good Answers: 4
#8

Re: Air conditioner sizing

08/01/2007 6:58 AM

I'd say somewhere around 3 to 5 tons. You will be in the tropics a lot and there is a lot of solar heat gain with all the glass, and probably little or no insulation, so you'd need more capacity on account of that.

__________________
Never underestimate the power of stupid people in large groups.
Register to Reply
Active Contributor

Join Date: Apr 2006
Posts: 13
#10
In reply to #8

Re: Air conditioner sizing

08/01/2007 4:34 PM

i beg to disagree that 5tons would be appropriate. this is not a freezer or cooler room! 2.4 sq. meter per TR? you must be kidding! take your calculator: at 400 cfm per tr nominal air flow with ambient at 95 deg F, what's you load? Q=m*cp*delta T. my question is (i am not a sailor) does the heat while on sea even in the tropics reach 95 deg. F? I have been in the desert of Saudi Arabia, where ambient dB would be as high as 115 deg. F, i could not justify a 5 TR air conditoner for 12 sq. meter of floor area.

Register to Reply
Participant

Join Date: May 2007
Posts: 3
#9

Re: Air conditioner sizing

08/01/2007 9:54 AM

On a bridge of this size, we use a 1 ton air conditioner. Typically there is little to no insulation in the top or sides. The large glass areas make the job even tougher. Remember you will need to also take into account what percentage of the time the outside door will be open. In reality, it takes a whole lot more than you would typically plan for.

Register to Reply