How Old?

03/20/2016 5:59 AM

Although retired I still tend to get involved with problem switchgear. This one has given me something to think about. The incoming supply is 1000kVA 433V. Main incoming OCB 1600A, outgoing ways 200A and 400A. The OCB's are withdrawable for isolation.

I've spoken to the OEM and their records don't go back far enough to put an age on this switchgear but we came to "about 1935". There is a live switching embargo in place just to make life a little more interesting.

The switchboard is still live feeding a factory and any shutdown will have to be as short as possible. The obvious choice would be rip it all out and replace with a new panel board.
All the cables are PILC-SWA, therefore would have to be replaced or spliced and so become yet another problem.

My gut feeling is retain the boards back section so the cables and metering won't have to be disturbed, that is so long as they test satisfactorily.
Have housings made for MCCB's that can reuse the original plug in connections. This will be quick but expensive.

Has anyone other ideas that may help?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: How old?

03/20/2016 9:24 AM

Until there is a forced outage of the plant continue to follow the embargo, otherwise follow the maxim, "If it ain't broke don't fix it!". You should use your time to plan the complete replacement of the entire board, reusing any switching/protective equipment 80+ years old is ill-advised because too much may have changed in the grid supplying it, especially the available short circuit current, which has been steadily increasing as the network in the area has grown more dense. You really can't be sure that those OCBs will operate safely/properly/reliably/fast enough under modern fault conditions.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4
In reply to #1

Re: How old?

03/20/2016 6:09 PM

Non of the existing protection will be used, modern MCCB's will take care of that.
Unfortunately one part doesn't work, nothing too important, it's only the O/C trip on OCB K4! That will take 5 minutes to repair during a planed shut down.

Due to the requirement of the insurance companies dependant manual OCB's are no longer acceptable, they can explode as the operation is slow for making load and possible faults. I've been switching OCB's for the last 45 years and I'm still alive (I think).
The problem now is a lack of people with experience of this type of switchgear. I'm supposed to be retired, a job like this comes along and I'm kicked back in to life.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#9
In reply to #4

Re: How old?

03/21/2016 12:10 AM

I hope that during switching you will be wearing high cal ppe, rated gloves and flash mask.

We sometimes lend out "bomb suits" for operating old private 11kV switchgear qttached to our network. Just have to find certified operators and somebody to develop the switching instructions.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #9

Re: How old?

03/21/2016 4:56 AM

One of the reasons I've been involved with the job is I'm authorised up to 11KV. I've yet to get access to the MV switchgear to make a decision on switching procedures. If like the LV gear there is a live switching embargo I'll get the PoCo to isolate and earth the 11KV supply before any switching operation is carried out. (Yet more expense!)

The owners of the factory know something has to be done but don't want to part with the cash. "It still works, what's wrong with it?"

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: How old?

03/20/2016 1:09 PM

Well, if plausible, I would build a new switchgear room with all new equipment and lines going back to a close location that could be completely built for a quick changeover of incoming and outgoing lines....then wait for a good time if possible, for a shutdown....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #2

Re: How old?

03/20/2016 6:31 PM

Replacement would be my first choice if it wasn't for the number of PILC cables involved. Each would have to be spliced or replaced, a time consuming and expensive job.

If I get the go ahead for plug in units with MCCB's the downtime will be about a day including testing. The metering would be retained.
Given the time constraints I can't think of another mode of attack but I'm open to suggestions.

The picture only shows ½ of the board, there's two more 1600A and six 200/400A OCB's on the other side of the wall

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #5

Re: How old?

03/20/2016 7:58 PM

I sympathize with you, there is no easy way to go...and I might add you are not alone in facing this type of a decision...It can be a bit like stepping in bubblegum on a hot day, it can become a very untenable situation...I think I would take the same approach as you and hope for the best....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#11
In reply to #7

Re: How old?

03/21/2016 5:10 AM

This is another approach. Remove the plug in connections and bolt the MCCB direct to the back section.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: How Old?

03/20/2016 3:37 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6
In reply to #3

Re: How Old?

03/20/2016 6:58 PM

I'll get my bid in, it would be a good addition to my collection of vintage switchgear handbooks. I can't say I was expecting to have to use one

I'm waiting for a 1950's Ellison 30A OCB to be delivered, once cleaned up it will be mounted on the lounge wall. The G/F isn't too happy with the idea, I can't understand why?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2006
Posts: 451
Good Answers: 16
#8

Re: How Old?

03/21/2016 12:05 AM

I am not electrical but I have had to decommission a lot of this sort of plant.

Other that the obvious electrical danger I would be concerned about PCB (Poly Chlorinated Bi-phenols) in the breakers and asbestos in the cables, gaskets, mounting boards and any where else that somebody thought a little heat resistance wouldn't go astray.

Best of luck with the outage and switch over.

BAB.

__________________
Make it so.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#12

Re: How Old?

03/21/2016 5:11 AM

The firm George Ellison Ltd is still in business:
http://www.ellison.co.uk
Its founder was also the inventor of Tufnol:
http://ahistoryoftufnol.org/companyhistory/index.html

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#16
In reply to #12

Re: How Old?

03/22/2016 7:07 AM

They were the first people I contacted. Their only suggestion was "rip it out". they then tried to sell their new switchgear.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Aug 2015
Posts: 9
#13

Re: How Old?

03/21/2016 6:32 AM

Here are another examples of ' Old ' not ' Old Parr ' .

What does it means INNOVATIVE . Yes that I dont know just now!

Steam Turbines Still Working dangerously or In danger or not modernized ! Working in a Old Factory. Hello ! Should we send them to a Museum ? The ' Older die for the Newer' may be a

some sort of FORMULA.

UKZM , Golden Land .

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#14
In reply to #13

Re: How Old?

03/21/2016 8:36 AM

I've switched that type of Metro Vic OCB's many years ago. I can't say I was happy with them back then, 30+ years on and they won't have improved.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#15

Re: How Old?

03/21/2016 10:06 AM

I can't help with a technical answer because i have no useful experience of old switchgear. But I do recall once back in the early 50's (an apprentice) I was given the job of re-filling some overload timer dash-pots with oil (different grades of oil and different depths - to give desired time delay control). "...it's in the bottle on the shelf...". It turned out to be Teepol - and not oil! and it worked.

Someone else went back and changed it to the correct oil - but it only came to light because they asked where the detergent had gone.

But to help with the logic of your problem, I ask what is the 'driving' force behind finding a solution. Is it a choice that allows you to take action with a plan in line with time and cash-flow.

Or is there some external force-majeure - when suddenly you will be landed with an instant and costly update or repair imposed by others outside your control.

My approach is to cost out the most effective and desirable solution available to you - then do it at your own pace.

Alternatively, do nothing, and limp along 'fire-fighting' hoping the fateful day will never come!

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#17
In reply to #15

Re: How Old?

03/22/2016 7:32 AM

If the company decide to do nothing then it's no longer my problem. I can get it working as original but it still won't meet current legislation.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#18
In reply to #17

Re: How Old?

03/22/2016 10:03 AM

" If the company decide to do nothing then it's no longer my problem. I can get it working as original but it still won't meet current legislation."

I think it might be your 'responsibility' so to speak - if doing nothing was based on your 'repair' getting a few more miles out of the old switchgear.

I am not au fait with the finer points of your legislation, but it seems a general principle here (UK) that regulations tend not to be retrospective - ie, hardly any of my 'old' electrical systems (home or factory) comply with today's regulations - but no action is required to upgrade anything.

That is, until additions and modifications are needed and then the new regs kick in.

If your old switchgear must comply with new regs when you service it, and the mods/repairs do not achieve this, it looks as though you must replace it with something that does.

And if you did 'fix' it, are you, as a professional engineer, 'allowed' to carry out work that does not result in compliance with the regs?

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#19
In reply to #18

Re: How Old?

03/22/2016 1:48 PM

Under BS7430 general maintenance won't affect liability unless incompetence could be proved.

Modification would be a different matter. The board would have to meet modern standards for fault clearance time and withstand.

Existing circuits will be tested but we have no obligation to repair/replace. We will issue recommendations for any remedial work. Again it would be up to the client if they act on our recommendations or not.

If we were to test under BS7671 some circuits would fail, BS7430 uses calculated and not "one size fits all" values.
For a 400A 433V feeder:
BS 7671 1MΩ minimum
BS 7430 29KΩ minimum
I've put 50 year old PILC feeders back in to service at less than the calculated value, it was a calculated risk. After a year on load the IR readings were >10MΩ

But it will be the insurance company calling the shots in this case.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

BlueAussieBoy (1); cristle (1); horace40 (2); Khinzawmyint (1); phph001 (1); RAMConsult (1); SolarEagle (3); TonyS (9)

Previous in Forum: Open and Close Link Testing in Energy Meters   Next in Forum: Transparent Conductive Spray Coating

Advertisement