Open and Close Link Testing in Energy Meters

03/18/2016 4:10 AM

Good day everyone, i would like to ask for your clarification with regards to the above mentioned subject.

Frequently i encounter terms such as open / close link testing particularly in testing the accuracy of energy meters.

Is it related to online and offline testing where in the close link is conducted offline (laboratory setup) while the former is on site or energized? i am very confused on what really is the meaning of open and close link testing. Or is it related to different meter forms?

Please advise, i would like to have a healthy conversation with regards to this.

Thank you so much

Register to Reply
Pathfinder Tags: energy meter testing
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Open and Close Link Testing in Energy Meters

03/18/2016 7:52 AM

What does it say in the test protocol? Where is the boundary between a pass condition and a fail condition? What were the equipment manufacturer's recommendations upon asking these questions over the telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#2

Re: Open and Close Link Testing in Energy Meters

03/18/2016 8:35 AM

The test link when open isolates the potential circuit from the current circuit. This allows the current circuit to be energized at a much lower voltage (usually 6 v) supplied by the test panel, while maintaining the nominal voltage to the potential circuit.

In a calibration lab, this provides a significant energy savings. Consider a lab with 32 panels ( as we had at the GE meter department) each supplying the 30 amps required for full load calibration

In the field, the test link is closed. This energizes both the current and potential circuits at line voltage.

__________________
The older I am, the better I used to be
Register to Reply Good Answer (Score 2)
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Open and Close Link Testing in Energy Meters

03/18/2016 10:19 AM

You are correct, the link is there to isolate the current coil(s) from the voltage coil(s) to improve the accuracy of the testing setup by eliminating any interaction between the the voltage/current sources, wiring differences, and the meter internals (especially important with newer solid state meters).

This paper explains it very well (no endorsement intended).

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2007
Location: Haverhill, MA
Posts: 1149
Good Answers: 151
#4
In reply to #3

Re: Open and Close Link Testing in Energy Meters

03/18/2016 2:08 PM

Good answer and good link. My experience with energy meters ended with the end of electro-mechanical meters and was primarily with single phase meters.

__________________
The older I am, the better I used to be
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Oct 2015
Posts: 33
Good Answers: 2
#5
In reply to #3

Re: Open and Close Link Testing in Energy Meters

03/20/2016 9:40 PM

Hi @RAMConsult, Thank you for answering my question and also for providing the link for the paper explaining further the difference and importance of open and close link testing. As i understand form the discussion here basically the difference of open and close link testing are: (correct me if i am wrong or if a missed something)

  • Testing at Open link, current coil is only considered and energized since the voltage coil is isolated from the former.
  • Testing at Close link means that both the current and voltage source are being energized. Since at nominal or normal conditions at site, this two coils are obviously energized hence when we talk of Close link testing we can simply generalized that is conducted on site or even in laboratories / meter shop but simply both the v and i coils are energized.
  • Lastly since there are so many meter forms, the user will want to familiarize with those forms as to test meters more efficiently and of course meter base should be considered as they are different from each other.

I want to thank PWSlack, gringogreg and RamConsult for the answers that you've provided here.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #5

Re: Open and Close Link Testing in Energy Meters

03/22/2016 12:12 PM

The function of the link is to isolate the two coils for the sole purpose of minimizing the effect of their combined burden on the test-set power source and its subsequent effect upon accuracy as the number of DUTs (Device Under Test) increases.

You should ponder what happens if only the current coil is energized; i.e., how much will a kWhr meter read if the voltage input is zero? Now look at your first two bullet points and examine your logic.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Oct 2015
Posts: 33
Good Answers: 2
#7
In reply to #6

Re: Open and Close Link Testing in Energy Meters

03/22/2016 8:03 PM

@RAMConsult, Thank you for your answer, Yes as for the first bullet i've mentioned if only the current source is energized. As per gringogreg "This allows the current circuit to be energized at a much lower voltage (usually 6 v) supplied by the test panel, while maintaining the nominal voltage to the potential circuit" I'm very confuse with this since all equipment has a certain burden that needs to be satisfied in order for the device itself to run. Question is i thought that the voltage will be isolated hence it will not be energized but it says there that it will maintain the nominal voltage to the potential circuit. Please advise

Register to Reply