19 comments
Rate Comments: Nested
Associate

Join Date: Mar 2016
Posts: 26

Leroy Somer R450M AVR Problems

03/18/2016 4:02 AM

I have 8 Perkins 4000 Series Gas generators driving 1000KVA Leroy Somer LSA50.1 alternators synchronized to produce around 6.5MW / 400VAC / 50HZ.

My problem - One alternator is grabbing more load than the others. Thus 7 alternators would say vary their load between 320KW and 340KW, depending upon load demand and time of day, yet the problematic alternator (AREP excitation - new) would fluctuate between 220KW and 390KW, a MUCH to big variance.

I have tried everything to try and balance this generator on the grid, to no avail. I've installed and calibrated a new Leroy Somer R450M AVR, set excitation voltage, droop, voltage and stability, but still the alternator does not stabilize.

Voltage is 100% stable at 400VAC. When I monitor the generator I can see the power factor vary between .88 and .95, and I can hear the engine speed up and slow down as the demand increases and decreases, albeit to my fine ear.

I am at a loss and wonder if someone on this forum can shed some light.

John Meyer, currently in Niger Delta, Nigeria

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Leroy Somer R450M AVR Problems

03/18/2016 7:54 AM

Why is it a <...a MUCH to big variance...>? What test criterion determines this? What were the equipment manufacturer's recommendations upon having discussed this matter by telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#5
In reply to #1

Re: Leroy Somer R450M AVR Problems

03/18/2016 12:23 PM

Hi,

Firstly, I inherited these machines, that were originally installed by Daewoo (manufactured by Coelmo Italy), and have, since 2013, kept them going, largely through spending days and nights fault finding, reading manuals and applying my own electrical background.

Suffice to say that there are no benchmarks that I can work from and the test criteria is zero, only that the machines keep on running 247, 365.

Secondly, there is no way I can just call any manufacturer and ask for help, thus I came to this forum.

The problem is clear, yet the solution is not.

7 identical machines are running with practically identical AVR settings, and are all drawing similar load since they are synchronized on a Woodward system to a cummon 11KV bus in a substation, in a similar bandwidth . . . . except for the one machine, which is drawing much more current, before releasing and the current would decrease over a very short time to way below the others, as explained below. So its up and down, up and down, and not controlling like the others.

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: Leroy Somer R450M AVR Problems

03/18/2016 8:01 AM

If the real output power (KW) is changing, it's not a voltage regulator problem but likely a problem with the engine driving the alternator. It could be a throttle problem or a problem with the fuel supply.

Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#3
In reply to #2

Re: Leroy Somer R450M AVR Problems

03/18/2016 9:24 AM

Interesting, I would have suggested it is a regulator issue...

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#7
In reply to #2

Re: Leroy Somer R450M AVR Problems

03/18/2016 1:04 PM

This is what I was thinking too. There are fine gas settings and our mechanical team will check this tomorrow morning.

Register to Reply
4
Member

Join Date: Mar 2016
Posts: 7
Good Answers: 2
#4

Re: Leroy Somer R450M AVR Problems

03/18/2016 11:16 AM

Hello,

First I am trying to explain a little bit and second I would like to give you contact

The problem you are facing is related to "droop setting", meaning that when several units are running in parallel together, it is important to set up the droop which is automatically balancing the load between the different units running together.

On top of that, regarding generating sets, we must point out that both engine and alternator are operating and each one is controlling different parameter

To make it short, the engine is controlling the speed and the active power (kW), while the alternator is controlling the voltage and the reactive power (kVAR)

So it meanss that depending on the type of unbalanced experienced, we should act on the engine governor or on the alternator regulator.

  • if the unbalance is related to kW, then we should adjust the speed droop
  • if the unbalance id related to kVAR, then we should adjust the voltage droop

Both droop system are working with the same principle; we need to adjust the initial value setting (initial speed or initial voltage) and to adjust the droop slope, to tune how much the parameter (respectively speed or voltage)is forced to decrease when the load is increasing (respectively kW or kVAR)

regarding the R450M AVR (and same for all Leroy-Somer AVR), please refer to the manual inwhich you will find some information, regarding parallel operation as well as the different voltage and droop setting.

at first step, it should be important to identify whether the problem is related to speed droop or to voltage droop

  • if speed droop, then refer to the governor instruction
  • if votlage droop, then refer to the AVR instruction and alternatively you can contact us.

contact by email at contact.epg@leroy-somer.com

or call +33(0)238609908 for assistance

hoping this could be of some help

Register to Reply Good Answer (Score 4)
Associate

Join Date: Mar 2016
Posts: 26
#6
In reply to #4

Re: Leroy Somer R450M AVR Problems

03/18/2016 1:02 PM

Hi and thank you for the excellent info. I have read your post a few times and have picked up good information about the KVAR and KW and will dig more into that perhaps in another post, but I was wondering whether you could assist with a few questions I have specifically relating to the setting up of the R450M AVR:

  1. Where do I start once the machine is ON LOAD? (I monitor with my Fluke multi meter and I can confirm that voltage is stable at 400VAC / 50HZ)
  2. Should I put the generator on load with a fully ant-clockwise setting of the Droop potentiometer and then start tuning, or do I leave it in the middle position.
  3. Take note I only have settings for a) Voltage b) Voltage Stability c) Excitation ceiling and d) Droop
  4. So my main question now is: In what sequence should I set the AVR up? I usually start with Voltage first (since this pot is always fully anti-clockwise for minimum voltage) and work my way from there.
  5. In this particular case my method is not producing the required results.

Your assistance would be much appreciated.

John

Register to Reply
3
Member

Join Date: Mar 2016
Posts: 7
Good Answers: 2
#8
In reply to #6

Re: Leroy Somer R450M AVR Problems

03/18/2016 1:46 PM
  1. assuming the problem is related to reactive load only (meaning kVAR) so that we can react on the AVR of the alternator directly,
  2. and assuming that the genset which is causing problem of unstability and eratic load is having same configuration as the others...

let's focus on particular aspects.

  • when all machines are running in parallel, the voltage is the same on all units, whatever the internal voltage setting. SO basically, as soon as a unit is running in parallel, we should not tune the voltage pot.
  • by default, we recommand to let the droop pot in middle position. initially, the droop potentiometer is presetted for 3% voltage droop (note that it should vay from 0 to 5% approx.)
  • do not put the droop at 0, because without droop, the units cannot share the load, so we need a certain droop.
  • 3% voltage droop is very good as it is reasonably low voltage drop, allowing automatic synchronisation anyway and sufficient to have a good sensitivy for the load sharing

AVR adjustments :

a) Voltage : to adjust the initial voltage of the alternator (very important!)

b) Voltage Stability : a kind of simple PID to adjust the response time of the AVR

c) Excitation ceiling : only to set up the maximum current, possibly for inrush or sudden load impact, short circuit, etc (no need in that subject)

d) Droop : adjustment of the voltage decrease in respect with the load. default setting at 3%, meaning that for 100% reactive load produced by the alternator unit, the output voltage will be -3% below the initial or no load voltage. the voltage decrease is proportional to the reactive lod (linear)

Most Important : is the no load voltage or initial voltage !

just consider that the droop pot is in middle position or presetted at 3%. Beside this consideration, the initial voltage is even more important, and possibly more difficult to adjust depending on the starting on site conditions.

It is far more important to adjust the initial voltage at the same value on all units running in parallel

Register to Reply Good Answer (Score 3)
Member

Join Date: Mar 2016
Posts: 7
Good Answers: 2
#9
In reply to #6

Why Initial voltage is more important

03/18/2016 2:02 PM

let's consider 2 gensets running in parallel, for example and explanation.

if the initial voltage is not the same on the 2 units,

as far as each unit is running isolated or disconnected from the other unit, then we can measure on each unit its own output voltage.

V1 and V2 for example.

if V1<>V2 then when we connect the 2 units in parallel, the resulting voltage on the bus bar, U, will be different and the U value with be in between min and max value (V1, V2)

in fact, as soon as the 2 units are interconnected, the output voltage become the same on the 2 units; meaning that one unit is decreasing its initial voltage and the next unit is increasing its initial voltage.

the problem resulting from this situation is that one unit is going to feed the other with reactive power, and the next one is consuming reactive power; even if there is no load connected to them.

as a conclusion, the most important is first to adjust the lo load voltage or initial voltage at the same value on all units, and this adjustment must be done before the unit is connected to the others. And then this voltage potentiometer should not be moved anymore !

Register to Reply Score 1 for Good Answer
Associate

Join Date: Mar 2016
Posts: 26
#12
In reply to #9

Re: Why Initial voltage is more important

03/22/2016 3:46 AM

Hi,

And thank you once again for the excellent info.

Let me just say that for the past three days I have been heavily involved in another commissioning effort and have not had a chance to get back to our main Gas Yard Power Generation Plant and continue to try and solve this problem. I will continue there later this afternoon or tomorrow and will get back here at the first opportunity.

Register to Reply
Member

Join Date: Mar 2016
Posts: 7
Good Answers: 2
#17
In reply to #12

Re: Why Initial voltage is more important

03/25/2016 6:19 AM

do not hesitate to make direct contact...

call +33(0)238609908 for assistance

someone will asl you further questions and guide you more in deep or offer you technical assistance.

Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#18
In reply to #17

Re: Why Initial voltage is more important

03/27/2016 5:51 AM

Thank you, however I cannot call out from where I am without incurring exorbitant pay-as-you-go cost. Chevron is in the process of installing fixed lines and this may be possible in months to come.

We are situated deep in the Niger Delta region and there are no roads or fixed lines to where we are. Everything is brought in via ship up the river or via fixed wing or helicopter. The nearest "town" is 350km away.

So you get the idea.

Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#13
In reply to #9

Re: Why Initial voltage is more important

03/24/2016 10:33 AM

OK, finally had time to give attention to the machines.

  1. I have checked every machine personally, adjusted no-load voltage here and there (very small adjustments) and can confirm that they are all running at a stable 400VAC/50HZ at NO LOAD.
  2. All machines also have similar excitation ceiling, stability (50%), and Droop settings. All CT's are reading correct resistance so there is current flow in all the AVR's for droop setting
  3. With all of the machines running ON LOAD I can see NO.2 machine (of 8) still has a problem, even with a brand new R450M AVR.
  4. I can monitor each machine's Woodward Controller in the substation and it is clear that power factor goes up and down on machine NO.2, fluctuating from i0.82 to i0.96 (over a 30 second period), with a resulting fluctuating 220KW to 380KW. So it's constantly going up and down, up and down.
  5. The other 7 machines synchronized on the grid are running very stable with power factor of i0.95 and KW from 290KW to 310KW, so no problem with the others
  6. It is only this one machine No.2 that has a problem that I am unable to solve.

PS: I have another question - What does C mean in front of the power factor on the Woodward controller. This is something unrelated but I see one of the other machines, instead o0f showing a power factor rating of i0.98 it is showing C0.98. What do I make of this and how do I rectify this, if it is a problem indeed?

Thanks in advance

John Meyer

Register to Reply
Member

Join Date: Mar 2016
Posts: 7
Good Answers: 2
#14
In reply to #13

Inductive or capacitive power factor

03/25/2016 5:55 AM

when considering a load on a power plant, or more generally considering any electric power including active and reactive values, then regarding the reactive power it can be inductive or capacitive in respect with the main property of the load we are considering.

so the Power Factor measurement is a mean to illustrate this load property. this means that we can have both value for inductive , when a 'i' is presented before the value itself or for capacitive when a 'c' is presented before the value also

now applying this to a genset, which is providing power to the load.

when the load is inductive, the genset is providing reactive power (kVAR)

when the load is capacitive, the genset is consuming reactive power (still kVAR)

when this happens on a site, it is an illustration of unproper setting of the 'droop' system.

unfortunately, this is not really related to the load variation.

to be more precise, any load variation will lead to sudden change of hte running condition, and consequently will lead to reactive power fluctuation between gensets

why is that visible on unit n°2 ?

let's say that if unit n°2 is having different setting than the others, any running condition change will the balanced unit n°2 and the set of 7 other gensets.

so the impact of load change will be very much visible on unit n°2, but less on the other units as same value's impacr will be divided by 7.

Register to Reply
Member

Join Date: Mar 2016
Posts: 7
Good Answers: 2
#16
In reply to #13

Re: Why Initial voltage is more important

03/25/2016 6:16 AM

Hi John,

Taking much consideratin to your problem, I am trying to explain as much as possible droop system, parallel operation and so on...

but I am still confused regarding the real site situation...

is kW value changing ?

in your point 4, you indicate a load fluctuation in kW...

this is important, in order to take apropriate action...

if the fluctuation on unit n°2 is regarding kW, then you should act on the speed governor (linked to speed droop!), the power factor value change could only be a consequence of the active power value change...

(same reactive power but with different activ power leads to power factor change!)

only if the active power is stable but the reactive power unstable, then you can consider it is an AVR concern.

if there is active power (kW) fluctuation, there is no chance to resolve this with the voltage regulator.

So it is very much important to identify the root cause to resolve your problem.

So far, it does not look to me that it is AVR issue

Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#10

Re: Leroy Somer R450M AVR Problems

03/20/2016 7:17 PM

HI John,

Firstly I am no expert and am wanting to understand your problem more clearly.You have had far more knowledgeable input than mine which 'hopefully' has solved your problems, but your description sounds to me like 7 of your alternators are handling the majority of the (stable) load while most of the load variation is being supplied by your eighth alternator rather than it being shared across all of them. Is my understanding correct?

Bill

Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#11
In reply to #10

Re: Leroy Somer R450M AVR Problems

03/22/2016 3:39 AM

Your understanding is correct.

Register to Reply
Member

Join Date: Mar 2016
Posts: 7
Good Answers: 2
#15
In reply to #11

paralleling

03/25/2016 6:04 AM

trying to illustrate this situation with another image...

just consider that the grid is one line... not a line, but physically a rope !

and to maintain this rope, you a team of 8 guy, each representing one of the 8 gensets...

in your situation, it looked like you have more or less 2 teams,

one team with 7 guys and one team with 1 guy only... both pulling on the rope...

even so there is no load... no action from grid side...

a small action or the "7guys" team will have bigger impact on the next team, to maintain the rope stable or static...

Register to Reply
Associate

Join Date: Mar 2016
Posts: 26
#19
In reply to #15

Re: paralleling

03/27/2016 6:30 AM

Hi there,

And thank you for your enlightening info.

After thorough investigation and testing I think I may have found the cause of the problem.

Background: We have 8 generators on an 11KV grid producing around 6.5MW of electricity at 400VAC/50HZ. Two alternators have been replaced over the past few years. The original alternators were Leroy Somer LSA50.1 type with PMG primary excitation and R449 AVR's, however the 2 replacement alternators were a different type in design, still LSA50.1type, but with AREP excitation and R450M AVR's. And it is these new alternators that have been producing fluctuating KILOWATT outputs, with the one I have been referring to the more problematic of the two.

Now here's the thing. I have found, in the case of both of these troublesome alternators, that the CT that is mounted around the neutral conductors within the alternator itself and connected to the AVR for droop setting, does not have all of the alternator neutral conductors passing through it, and only 1 of four conductors able to pass through the CT. The problem was, when technicians retrofitted the new alternators a few years ago they realized that the existing CT's (that were removed from the faulty PMG alternators for re-use) had an inner diameter much too small for all of the neutral conductors of the AREP alternator to pass through it. They obviously did not have the correct CT's on hand at the time and just reinstalled the old ones, resulting in the current configuration.

As an experiment I have disconnected these CTs from the AVRs in the two AREP alternators and shorted them out to prevent burnout, kept the droop settings on the AVR on default, and then started the machines and put them on load.

The result is that both alternators are running a lot more in sync with the others on the synchronized grid and Kilowatt (and power factor) is a lot more stable.

I guess my question now is: If I procure the correct CT's (400:1 Ratio) with a larger internal diameter to enable all of the neutral conductors within the alternator to pass through it, and I were to connect these back onto the AVR, should this solve my problem. Do you think that the incorrect CTs and the way in which they were mounted could have made the alternators behave the way they did?

John.

Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

John365 (8); Leroy-Somer (7); phoenix911 (1); PWSlack (1); Rixter (1); WAWAUS (1)