Amount of Starting Current of a Rotary Compressor

04/21/2016 10:00 AM

I want to know what could be the value(amount in amperes)of starting current of rotary compressor of a 1.5 Ton air conditioner(carrier make) whose rated running current is 6.7 Amps. Also whether locked rotor current and starting current is same in such types of machines ?

Will anybody help please ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Amount of Starting Current of a Rotary Compressor

04/21/2016 10:04 AM

A1) Between 5 and 7 times the FLC.

A2) They are the same.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Amount of Starting Current of a Rotary Compressor

04/21/2016 11:13 AM

The peak starting current is always the same (unless a reduced voltage starting method is used) per what PWSlack said. The only thing that changes with different loads is the acceleration time.

So was this just to satisfy curiosity, or do you have some sort of problem to solve related to that?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Amount of Starting Current of a Rotary Compressor

04/21/2016 12:18 PM

First of all translate 1.5 ton A.C. in kW. Second, translate it in HP.

For instance see:

http://www.rapidtables.com/convert/power/ton-to-kw.htm

Now see also at the motor shield what locked rotor code letter is written.

Check in a book-NEC Table 430.7(B) Locked-Rotor Indicating Code Letters for instance

instance- what it does means k=kilovolt_amper/hp.

Multiply 1000 with HP and with this k and divide it by sqrt(3)-for three phases

and by voltage.

Let's say the code is J then k=7.99.

1.5 ton AC=5.27 kW [ 7 HP].Voltage 480 V.

Ilocked=1000*7*7.99/sqrt(3)/480=67.27 A.

__________________
Julius
Reply Score 2 for Off Topic
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13
In reply to #3

Re: Amount of Starting Current of a Rotary Compressor

04/27/2016 5:05 AM

Sorry, I forgot Thermodynamics and EER!

I read the shield plate of my air conditioner and I found 4 KW.

In Europe some time "kW" does not mean output power as usually in USA, but

the input power.

That means my air conditioner of 4 kW produces about 4.30*4=17.2 kW

or 58700 BTUH about 5 ton AC. Amazing!

__________________
Julius
Reply
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Amount of Starting Current of a Rotary Compressor

04/21/2016 12:26 PM

I suspect the locked rotor would be around 55 amps, but it should say on the compressor.....A rotary compressor starting unloaded will have a starting spike, but I would be surprised if it was hitting LRA....and if it was, I'd be testing the start/run cap...

http://www.ebay.com/itm/Copeland-1-5-Ton-Scroll-HP-A-C-Condenser-Compressor-18-000-BTU-ZR18K5-PFV-800-/351144244298?hash=item51c1d3f44a:g:eO4AAOxytL9SIVCd

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Good Answer (Score 2)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#5
In reply to #4

Re: Amount of Starting Current of a Rotary Compressor

04/21/2016 1:20 PM

It is better than all my calculation, indeed!

__________________
Julius
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #5

Re: Amount of Starting Current of a Rotary Compressor

04/21/2016 3:21 PM

Well we don't know the voltage....but the question was whether a compressor should be drawing LRA on start-up....I've never seen a 3Ø compressor under 5 tons...So I'm assuming single phase 230v with start/run capacitor...therefore if you are hitting LRA on start-up, you have a problem....now you can short cycle a unit in any phase or voltage and cause the unit to draw LRA trying to start against pressure built up in the system, in which case the compressor should go off on overload within something like 5 seconds...but allowing the pressures to equalize and the compressor to cool down should remedy that situation....most systems have a time delay short cycling protection on them...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#7

Re: Amount of Starting Current of a Rotary Compressor

04/22/2016 9:28 AM

Please call or go to your local refrigeration supply house, or, look up the information on the website for the manufacturer. They both have the exact info. you are looking for.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #7

Re: Amount of Starting Current of a Rotary Compressor

04/22/2016 12:49 PM

The're part sellers, not technicians...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#9
In reply to #8

Re: Amount of Starting Current of a Rotary Compressor

04/22/2016 1:50 PM

I have worked at 2 parts houses between jobs. Don't sell them short, they have the information on hand. Some are better than others, just ask for the sharpest on the subject.

Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #9

Re: Amount of Starting Current of a Rotary Compressor

04/23/2016 12:40 AM

So why didn't you answer the question?

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Associate
United States - Member - Old Member

Join Date: Jun 2008
Location: Topeka, Ks.
Posts: 49
Good Answers: 3
#12
In reply to #10

Re: Amount of Starting Current of a Rotary Compressor

04/25/2016 9:42 AM

http://www.northamericahvac.com/carrier-bryant-payne-1-5-ton-scroll-condenser-compressor-p021-18211p-p021-18211/

I found this in about 2 minutes, more than enough info. for the info. needed. This is for R-22, if R-410 it's probably a Copeland.

Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Amount of Starting Current of a Rotary Compressor

04/23/2016 12:49 AM

I am not specialist in refrigeration indeed. However, something does not fit here.

18000 Btu/h it is 5.27 kW but the rated current it is not for 1 phase of 230 V .

[In my opinion has to be 25-30 A or it has to be 3 phases.]

See -for instance:

http://www.ebay.com.au/itm/AIR-COMPRESSOR-MOTOR-ELECTRIC-INDUCTION-7-5HP-5-5KW-THREE-PHASE-2880RPM-/111575009990

__________________
Julius
Reply
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (4); JRaef (1); PWSlack (1); Sasnak (3); SolarEagle (4)

Previous in Forum: Rating of Induction Motor   Next in Forum: Motor Current Discrepancy

Advertisement