Transformer Inrush Current

04/25/2016 1:09 AM

Dear Fellows,

i have to give power to a step up transformer having following details;

Voltage= 13.8/132 Kv

Power= 100 MVA

Vector Group= YNd11

IEC 60076

But...the power feeder system is 26 diesel engines each of 1000 KW coupled together to form a 20 MVA supply system.

what i am worrying about is in rush current of transformer and duration of that inrush current.

as of my knowledge, rule of thumb is, it is 10% of nominal current i.e. in my case:

primary current= 100 MVA/ (13.8 Kv X 1.732 X 0.8)

= 5229 Amps

10% of this current is 5751 Amps.

please guide me if this is correct and also is this possible to fed power to 100 MVA transformer with 20 MVA supplying source(diesel gensets). ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Transformer Inrush Current

04/25/2016 1:17 AM

For one thing, it might be 110% instead of 10%, and even that may be too low of an estimate.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Transformer Inrush Current

04/25/2016 7:11 AM

The obvious question is "why do you want to do this?"

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Transformer Inrush Current

04/25/2016 3:42 PM

Why is transformer inrush a problem?

With your system are you not powering up and synchronising the diesel engines and transformer with the 132kV side switch open (if it is capable of load switching) or downstream loads disconnected so you are not trying to switch into full load. I am assuming you are switching the transformer with a load capable 13.8kV switch.

The consultant that designed the system should have taken transformer inrush into account.

Wait, based on previous threads on CR4 are YOU the consultant?

__________________
jack of all trades
Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#4
In reply to #3

Re: Transformer Inrush Current

04/26/2016 1:45 AM

this is an emergency requirement by a client for 2 months only, as the client needs to test his load.

i am just trying to support the client.

secondly, i have to supply power to 13.8 Kv side.

diesel power system the client requested is of 20 MW. i will have to provide 29 generators each of 1 MW @ 70% running load.

these generators will all be synced together and will supply to step up transformers which will step up 460v into 13.8 Kv.

that 13.8 Kv will be feed to 100 MVA transformer. i have to give a black start to system that is why considering inrush current for my system safety.

client have to test the load with our generators until unless he gets power from national grid.

i think i have made the picture clear.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5
In reply to #4

Re: Transformer Inrush Current

04/26/2016 3:27 PM

As long as the generators are all synched properly and your only loading the generators to 70% full load AND the electrical system can handle the additional transformer inrush current then the generators should be adequate to supply the additional momentary transformer inrush current.

What's the customers load as black starting a large capacitive or inductive load could be a bigger inrush current problem than transformer inrush?

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Transformer Inrush Current

04/27/2016 12:50 AM

I suggest that you do much more research to find out where that thumb-rule was pulled out of. When you do you will find that what you list as 10% is actually 10X, that energizing via the low-side can be raise this to nearly 20X, that the type of transformer core affects the magnitude, as does the source reactance, and all this assumes that your transformer has no high-side load.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#7
In reply to #6

Re: Transformer Inrush Current

04/27/2016 1:36 AM

yes, regarding energizing current, its 10X, not 10%, typographical error you can say.

and no, at the moment of closing our main VCB, the load side of transformer will not be connect to any load. they will switch the load on after every thing gets normal in case any abnormality occurs.

load in this case is the induction motors, mostly driven by VFD.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8
In reply to #7

Re: Transformer Inrush Current

04/27/2016 1:47 AM

Nice try on shifting blame to the typo, but no cigar, you used the 10% in your calculation of the inrush current. Do you honestly believe that your generation can really supply 50,000 to 100,000 amps of mostly reactive current, even if it's only until the transients die out?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2012
Posts: 44
#9
In reply to #8

Re: Transformer Inrush Current

04/27/2016 2:55 AM

ahan, i see, ok, my bad, my fault, i get the calculation wrong, now you feel good.??

i have checked with some engineers over here also working in other organizations. they said it is fine and you will face no problems, will let you know after i run the project

:-)

Register to Reply Off Topic (Score 6)
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jack of all trades (2); mrmuneb (3); RAMConsult (2); TonyS (1); Tornado (1)

Previous in Forum: Capacitor Panel   Next in Forum: Automatic Power Factor Correction Panel

Advertisement