Automatic Power Factor Correction Panel

04/25/2016 2:02 AM

Hello All,

Please tell me what are the parameter to segregate capacitors bank in Capacitor panel?

To be more precise suppose we do have separate 30KVAR, 20KVAR, 15 KVAR, 10KVAR capacitors bank in Capacitor Panel. What are the parameter that we have segregated 30KVAR, 20KVAR, 15 KVAR, 10KVAR capacitors bank in capacitor panel.

Thanks

Vikash

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Automatic power factor correction Panel

04/25/2016 2:32 AM

Fuses or circuit breaker, and contactor, for each capacitor, with some logic to "decide" how many KVAR are needed at any given time.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#2

Re: Automatic power factor correction Panel

04/25/2016 3:10 AM

to be more precise for solution please tell which automatic power factor correction controller you are using?

Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 20
#6
In reply to #2

Re: Automatic power factor correction Panel

04/25/2016 4:06 AM

Senitron, Accuvar relay

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #6

Re: Automatic power factor correction Panel

04/25/2016 8:14 AM

Please describe to the forum the outcome of the telephone call that has taken place to the original equipment manufacturer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Automatic power factor correction Panel

04/25/2016 3:16 AM

"Automatic capacitor banks consist of stages controlled by a power factor controller which ensures that the required capacitor power is always connected to the system, it means that always would be optimal correction "

"The relevant Standards on this device recommend a continuous overload capacity of 30%. A capacitor can have a tolerance of up to +15% in its capacitance value. All current-carrying components such as breakers, contactors, switches, fuses, cables and busbar systems associated with a capacitor unit or its banks, must therefore be rated for at least 1.5 times the rated current."

http://electrical-engineering-portal.com/capacitor-banks-in-power-system-part-one

http://electrical-engineering-portal.com/capacitor-banks-in-power-system-part-two

http://electrical-engineering-portal.com/capacitor-banks-in-power-system-part-three

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 20
#7
In reply to #3

Re: Automatic power factor correction Panel

04/25/2016 4:10 AM

My question is The total 75 KVAR is required. We are dividing it as 30,20,15,10KVAR, so what parameter we are following to segregated it to 30,20,15,10KVAR

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #7

Re: Automatic power factor correction Panel

04/25/2016 8:28 AM

It is described as <...automatic...>, which means that the expressed concern is superfluous, as the equipment sorts itself out.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#17
In reply to #7

Re: Automatic power factor correction Panel

04/25/2016 10:11 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#22
In reply to #7

Re: Automatic power factor correction Panel

04/28/2016 12:24 AM

By combining these in various ways, you can get many increments of 5kvar, and thus cater to most motor combinations. An even better combination here could be 40, 20, 10, 5. Then you could get every 5kvar step from 5 to 75.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Automatic power factor correction Panel

04/25/2016 3:36 AM

<...we...> could always use the telephone to speak directly to capacitor bank panel suppliers. Given that <...we...> indicates there is more person at the facility, several phone calls to different suppliers could take place simultaneously. As telephone calls are 2-way, they enable both parties to the call to ask questions and doing so means that understanding is reached quickly during the call. This technique is by far the fastest way to determine the missing information.

CR4 does not offer training in the use of the telephone.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Automatic power factor correction Panel

04/25/2016 3:41 AM

One could always get entrepreneurial and fix that for a small sum.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #5

Re: Automatic power factor correction Panel

04/25/2016 8:25 AM

Modesty forbids.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 20
#8
In reply to #4

Re: Automatic power factor correction Panel

04/25/2016 4:16 AM

My question is The total 75 KVAR is required. We are dividing it as 30,20,15,10KVAR, so what parameter we are following to segregated it to 30,20,15,10KVAR

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#9
In reply to #8

Re: Automatic power factor correction Panel

04/25/2016 4:42 AM

Your question should be:

Is the 75 kVAR required?

A parameter is your power factor.

This you can only know by monitoring the power factor and change the values to your best approach. Your bank gives you possibilities to switch to to the following values:

10, 15, 20, 25, 30, 35 (20+15), 40 (30+10), 45 (20+15+10), 50 (30+20), 50 (20+30), 55 (30+15+10), 60 (30+20+10), 65 (30+20+15), NO 70 () , 75 (30+20+10+15)

Someone has been thinking this together to get a selection (segregation as you call it) to chose from.

Maybe we both have a "English language" problem?

__________________
Plenty of room here
Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 20
#10
In reply to #9

Re: Automatic power factor correction Panel

04/25/2016 5:28 AM

Answer is

segregation depend upon based upon load. Suppose we are having four motor total requirement of KVAR is 75KVAR. segregation is required because four motor do not run at a time. Thus we have segregated capacitors bank into 30KVAR for 1st motor,20KVAR for 2nd motor, 15KVAR for 3rd motor and 10KVAR for 4th motor.

Suppose if we are starting 1st motor then capacitor bank of 30KVAR we will be switch on and like on so..

If for 1st motor we are switching on 75KVAR of capacitor bank then over voltage will cause and will damage the motor. Thus segregation is required.

Register to Reply
Participant

Join Date: Apr 2016
Posts: 2
#19
In reply to #10

Re: Automatic power factor correction Panel

04/27/2016 1:35 AM

Not getting you, your motor will not decide which capacitor to switch on but the controller. Combination of KVAR may vary designer to designer and depending upon start-stop sequence of load, PF controller will decide how much KVAR to switch on/off.

Register to Reply
Active Contributor

Join Date: Sep 2015
Posts: 20
#20
In reply to #19

Re: Automatic power factor correction Panel

04/27/2016 11:44 AM

Hello Do not considered pf controller . Suppose you are operating capacitor bank manually ie manually capacitor banks is to be start and stop with motor.under that condition we are estimating how much kvar is needed for a motor.For example for 100hp motor how much kvar Is required. So we follow thumb rule talking 33% of hp ie 33 kvar is required for that motor or kvar=Kw(tan@1-tan@2) Where @1 is the pf of motor written on nameplate @2 Is the. Pf required. Suppose there are other motors also then we are estimating there kvar .then all motor required kvar assemble in panel. This is know segregation methodology. Hope now all will understand

Register to Reply
Participant

Join Date: Apr 2016
Posts: 2
#21
In reply to #20

Re: Automatic power factor correction Panel

04/27/2016 11:46 PM

OK, somebody may operate it manually, but there is a problem. At design stage you may not know the percentage of loading on motor. PF of motor are different at different percentage of loading. That's why PF controller play a major role to fulfill the very purpose of capacitor.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #8

Re: Automatic power factor correction Panel

04/25/2016 8:22 AM

It is pointless asking the forum what <...we...> are following without defining <...we...>.

Please also define <..parameter...>; give the forum some context, please.

With the listed combination, 10, 15, 20, 25, 30, 35, 40, 45, 50, 55, 60, 65 and 75kVAr are possible by switching various combinations in and out of circuit. The original equipment manufacturer can explain how this is done if it isn't in the Operation Manual, or said manual is not to hand. And if it is not to hand, a simple telephone call to the manufacturer will precipitate a replacement.

Please explain what has been done to obtain this information and why the answer to the question is not in the information obtained.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#11

Re: Automatic power factor correction Panel

04/25/2016 6:38 AM

as of my knowledge, capacitor bank relay works by monitoring the current power factor of system. we just feed the values of individual capacitors i.e 30KVAR or 20 KVAR etc for different step outputs of relay. relay then decides which bank to take into operation according to actual power factor.

you can find digital outputs on relay. these outputs energize magnetic contactor that is connecting the respective KVAR with bus.

Register to Reply
Anonymous Poster #1
#12
In reply to #11

Re: Automatic power factor correction Panel

04/25/2016 7:17 AM

Who's homework are we being asked to do here, yours or the OP?

Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#18

Re: Automatic Power Factor Correction Panel

04/25/2016 11:15 PM

your SENITRON ACCUVAR RELAY will take care of it.you only need to have your capacitors wired as per your local wiring requirements .

Register to Reply
Register to Reply 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dvmdsc (1); MI76 (2); mrmuneb (2); pillay (1); PWSlack (5); SolarEagle (2); Tornado (3); vikashkumar (5)

Previous in Forum: Transformer Inrush Current   Next in Forum: Motor Tripping and Abnormal Noise

Advertisement