Anonymous Poster #1

Motor Tripping and Abnormal Noise

04/25/2016 4:12 AM

We observed abnormal noise from subject motor body. Following were observations:

Motor tripped on O/L while running. O/L relay was reset and motor trial taken in coupled condition. This time Main breaker tripped immediately upon starting.

Motor IR Value and resistance readings found ok.

IR Value: 4.5GOhms with 500Volts

Resistance: 0.2Ohms balance

Motor de-coupled and started for NLT again this time breaker tripped. Starting current found 830Amps.

Both Motor and power cable IR value taken separately and found ok.

After taking IR value for both Motor and power cable, again motor NLT was taken and this time motor ran for 4-5Seconds before tripping on O/L.

Also abnormal noise observed from motor. Motor running current had come down below 100Amps before tripping.

Motor was rotating freely and no noise observed in bearings.

What could probably cause for tripping of breaker and abnormal noise from motor body.

Motor Make: Reliance Electric

415V 100HP

FLC: 120Amps

2970 RPM, 50HZ

Mounting : V1 Duty: S1

Frame: 405LP TEFC

In. CL.: F

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Motor tripping and abnormal noise

04/25/2016 4:21 AM

Mechanical obstruction? Fish out the rag or stick or whatever it is?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Active Contributor

Join Date: Dec 2010
Posts: 13
#3
In reply to #1

Re: Motor tripping and abnormal noise

04/25/2016 4:29 AM

Thankx for the reply.

Rgds,

-SV

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Motor tripping and abnormal noise

04/25/2016 4:35 AM

Good luck. I was just guessing, so it might be something else.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#2

Re: Motor tripping and abnormal noise

04/25/2016 4:25 AM

How old is the motor?

2950 RPM for such a big motor can make a lot go wrong.

Bearings may look and roll normal at low speed, but may act different under full load. You should describe the noise better and do a vibration check to know the bearing status.

Sometimes the shaft to the rotor connection is troublesome, or windings may be loose.

Does the motor have collector rings?

What is the nature of the load on this motor, intermittent, constant, e.g

__________________
Plenty of room here
Reply
Active Contributor

Join Date: Dec 2010
Posts: 13
#5
In reply to #2

Re: Motor tripping and abnormal noise

04/25/2016 4:36 AM

Hi, thankx for the reply:

1. Motor is more than 10yrs old.

2. No. Motor has no collector rings.

3. Load is constant - for typical heat medium circulating pump.

Rgds,

-SV

Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#6
In reply to #5

Re: Motor tripping and abnormal noise

04/25/2016 4:51 AM

Is it a reliance USA motor?

Made for 50 Hz? Did it run too hot?

__________________
Plenty of room here
Reply
Active Contributor

Join Date: Dec 2010
Posts: 13
#7
In reply to #6

Re: Motor tripping and abnormal noise

04/25/2016 5:16 AM

Yes.. Its Reliance motor... 415Vac/50Hz..

No. Not run too hot..

abnormal noise and tripping problems observed whilst running.. as explained and few trial runs taken on no-load conditions too.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Motor tripping and abnormal noise

04/25/2016 6:25 AM
  • From experience, the last time a motor tripped on overload was on a sewage sludge centrifugal pump. The cause of the trip was found to be a 4m length of blue polypropylene rope that had become wrapped inadvertently around the impeller and shaft within the pump casing. Once the rope had been removed, the pump no longer tripped; performance close to the original design intent resumed thereafter.

Do bear in mind that the only people who can see the posted pump, and are in a position to investigate, are the Original Poster and immediate colleagues; the pump cannot be seen from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Dec 2010
Posts: 13
#9
In reply to #8

Re: Motor tripping and abnormal noise

04/25/2016 6:28 AM

Thankx indeed for your valuable reply.

Rgds,

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: Motor tripping and abnormal noise

04/25/2016 6:33 AM

The forum does not know to what the motor is coupled. An "Electrical Engineering problem" approach may be too limiting. Take the blinkers off!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Dec 2010
Posts: 13
#11
In reply to #10

Re: Motor tripping and abnormal noise

04/25/2016 6:38 AM

Oopps...! The motor is coupled to Heat Medium Circulating pump (continuous operation ) on offshore process platform.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #11

Re: Motor tripping and abnormal noise

04/25/2016 6:52 AM

Consider the possibility of something being inside the pump other than what would be expected.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#15
In reply to #11

Re: Motor tripping and abnormal noise

04/25/2016 10:41 AM

Sounds like you sucked up some seaweed, or perhaps a grouper....

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#20
In reply to #8

Re: Motor tripping and abnormal noise

04/27/2016 9:54 AM
  • Case 2: the problem of poor performance on 2 out of 3 sludge pumps connected to the same inlet manifold and the same outlet manifold was eventually traced to the presence of a 6in square offcut of glass-reinforced polyester roofing material that had inadvertently found its way into the upstream tank and had become lodged part of the way along the inlet manifold.

All good fun. :-)

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#13

Re: Motor tripping and abnormal noise

04/25/2016 7:24 AM

Strip the pump and motor, you'll have to do it eventually so why wait?

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#14

Re: Motor Tripping and Abnormal Noise

04/25/2016 10:41 AM

You still haven't isolated the problem, disconnect the leads at the motor then close the breaker, then you'll know if it's in the supply or the cable. If it trips again then disconnect the leads at the breaker and test again. Now you can concentrate on the motor and load, though I suspect it's mechanical.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16

Re: Motor Tripping and Abnormal Noise

04/25/2016 11:44 AM

Troubling in your descriptions is that breakers were tripping after the OL tripped, including a MAIN breaker tripping When the motor was unclupled! That points to an electrical problem for sure.

I would continue focussing on insulation failures somewhere. Often times when people perform an insulation check, they only check the phase to ground reference. If there is a phase to phase short, that will not show up.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#17
In reply to #16

Re: Motor Tripping and Abnormal Noise

04/25/2016 2:11 PM

Electrical problem is certainly the first place to look in a marine setting....the salt air is unbelievably corrosive...

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Member

Join Date: Mar 2016
Posts: 6
#18

Re: Motor Tripping and Abnormal Noise

04/26/2016 11:07 AM

What you've decribed remind me of a motor being provided inadequate utility power. If you monitor the line to line voltage of the motor starter before and after energizing, you might find that there is inadequate utility power available ... and probably due to power line loss (too long, inadequate ampacity, temperature rating, etc.). The motor will start at a lower voltage than will allow it to run continuously. If you have an inadequate utility power supply, the line current will slowly increase in response to the line to line voltage decreasing, and because of increasing load as it comes up to speed. I've seen this effect many times ... usually an A/C unit at the end of a utility line that is only inadequate on really hot days. If the neighbor wouldn't also use their A/C units .. it would be a non-problem.

Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19
In reply to #18

Re: Motor Tripping and Abnormal Noise

04/26/2016 3:42 PM

I disagree. Low line voltage would not explain all of his symptoms, ie the Main breaker tripping when the motor was UNCOUPLED.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Member

Join Date: Mar 2016
Posts: 6
#21
In reply to #19

Re: Motor Tripping and Abnormal Noise

04/27/2016 12:57 PM

Perhaps you misunderstood.

Un coupling doesn't necessarily adress the problem.

Not low line voltage at startup. Gradual low line voltage during start up and what should be steady state operation. The condition I describe is not necessarily a constant ... and is a function of other's also using the utility source, the weather (A/C required), etc.

Reply
Reply to Forum Thread 21 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dvmdsc (2); JRaef (2); Mel Presswood (2); PWSlack (4); RAMConsult (1); Sadashiv Vaidya (5); SolarEagle (2); TonyS (1); Tornado (2)