Caterpillar Generator 0.9MW

05/09/2016 9:45 AM

I have got three 0.9MW generators powering up the plant thru 4 ATS. When main power goes off, the first generator starts automatically and the breaker get closed normally but the second and third generators shows under frequency fault and do not start unless i press the reset switch? Can you please help?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Caterpillar Generator 0.9MW

05/09/2016 10:56 AM

Standing by the reset switch doesn't sound like much of a career opportunity. Invitation declined.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: May 2016
Posts: 3
#2
In reply to #1

Re: Caterpillar Generator 0.9MW

05/09/2016 11:14 AM

Hello,

Thanx for the comment, But those books does not have an answer to what i have asked. I have called the dealer but they said that is not in their scope. It is something to do with the control

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Caterpillar Generator 0.9MW

05/09/2016 11:36 AM

The manuals for the control cannot be seen from here.

One could:

  • Go back to the commissioning records and double-check that every setting is in the "as commissioned" state, and try again.
  • Switch off the load and restart the first assist generator, and then the second, then putting the load back on line.
  • Call-in the individual that commissioned the sets, and get him/her to sort it out.
  • Etc.

Whatever is chosen, it will be a valuable learning exercise for both the individual and the organisation. Keep notes, and write it up after all is well.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Caterpillar Generator 0.9MW

05/09/2016 12:39 PM

The under frequency condition may be a transient situation occurring during startup....but first you need to determine if the control is at fault or the control timing sequence is the issue...I would try manual sequence start, while monitoring frequency...If there is no issue, then a stepped startup configuration...

http://www.tpub.com/celec/45.htm

http://ecmweb.com/ops-amp-maintenance/top-nine-reasons-generators-fail-start

https://forums.cat.com/t5/Cat-Products/Caterpillar-C9-Problem/td-p/6906

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Nov 2011
Posts: 56
Good Answers: 1
#5

Re: Caterpillar Generator 0.9MW

05/09/2016 11:54 PM

you already got a clue.find the under frequency sensors or detectors and the circuitry.for a start replace them and start working from there .

Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#6

Re: Caterpillar Generator 0.9MW

05/11/2016 7:17 AM

dear, you need to mention about;

1. type of governor in your generator

2. type of controller you are using to control the generator, for example if it is Caterpillar genuine controller or you are using some other brand like Deep Sea or ComAp or Datakom.

3. you are saying that the controller on generator shows under frequency alarm at idle position, am i right? or this alarm comes when they are running?

for control, if this alarm arises during startup, you need to check settings of Governor.

Register to Reply
Participant

Join Date: May 2016
Posts: 3
#7
In reply to #6

Re: Caterpillar Generator 0.9MW

05/11/2016 10:50 AM

Thank you very much for your reply.

Yes this Alarm arises up after 2 minutes from the time it starts up.

I will try that for sure.

Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#8
In reply to #7

Re: Caterpillar Generator 0.9MW

05/12/2016 12:55 AM

also you need to check the tolerance values for under and over frequency settings inside the generator controller.

if you have to adjust frequency from governor for this issue, you will also have to adjust/fine tune the voltage accordingly.

Register to Reply