Anonymous Poster #1

Electronic Earthing System

05/17/2016 3:57 PM

Dear Sirs,

I am facing a problem in Earthing system at our project site.We prepare some Electronic earthing pits in furnace slag filled area with the help of Copper Plate, Strip and bentonite Powder.But in the time of testing we are not getting good result.

So kindly advise me how to get the earthing value in slag filled area.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Electronic earthing system

05/17/2016 4:08 PM

This sort of question has come up before on CR4 a number of times. You may need to alter the backfill composition to retain more moisture, add an additional moisture holding filler compound or change the pit design.

Try a search on CR4 for earth pit for more detailed answers such as the following thread. More detailed answers can be found in your local standards and codes or online.

http://cr4.globalspec.com/thread/67973#comment718807

Have you taken into account the ambient and ground temperature may be higher than expected in this application which may be increasing the water evaporation in the pit and hence possibly reducing the pit resistance?

__________________
jack of all trades
Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#2

Re: Electronic earthing system

05/17/2016 4:47 PM

Plumb all the urinals in the plant to empty into your earthing pits.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Electronic earthing system

05/17/2016 5:10 PM

It is assumed that the location is difficult to plumb piping to for any liquids.

__________________
jack of all trades
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #3

Re: Electronic earthing system

05/17/2016 5:20 PM

Perhaps it is assumed that they just don't want to spend money on properly grounding their equipment nor paying someone who know how to do it property.

Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#10
In reply to #5

Re: Electronic earthing system

05/18/2016 9:44 AM

Well, in that case, let's hope the safety inspectors (if any) are cheap to bribe.

I hate to sound prejudiced, but an Anon OP is someone who KNOWS that they're asking for something they should already know, or want free advice on when the only REAL advice of worth is "Hire an Engineer locally and pay him/her to solve the problem."

It's bad enough when we get people asking how to set up dangerous equipment when we can SEE that they're from The Land that Occupational Safety and Health Forgot. When the OP is AP#1, we have no clue where he is, or what regional safety commission he's trying to do an end-run around.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: Electronic earthing system

05/18/2016 10:51 AM

Please confirm that the male includes the female and vice versa.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#12
In reply to #11

Re: Electronic earthing system

05/18/2016 12:00 PM

Yes, unless I am referring to a specific person of known gender, any uses of 'he,' 'she' '(s)he,' etc. can be assumed to be the genderless "He, she, or it.(1)" When being sarcastic, I'm an equal-opportunity offender.

Notes

  1. "He, she, or it" has been popularly abbreviated by writers and satirists as h/sh/it, pronounced as "Horsesh-(2)"
  2. I may be an equal-opportunity offender, but I prefer not to use foul language in semi-public forums. Too much 'splatter' landing on innocent bystanders.
__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#16
In reply to #12

Re: Electronic earthing system

05/18/2016 2:31 PM

ROFLMFAO!

Sorry if That offends anyone equally!

Maybe they should equally invite the male AND female employees to piss on the earthing pits!

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#18
In reply to #16

Re: Electronic earthing system

05/18/2016 2:38 PM

See, we can get along, as long as things don't get political.

I will be SO glad when this election cycle is over. Canada wrapped up theres in 11 weeks, and that was a record for long elections for them, the US election cycle is feeling like it's been going on for 11 YEARS.

I want to quit thinking about idiots ruining my life for money and power.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#19
In reply to #18

Re: Electronic earthing system

05/18/2016 4:59 PM

We most definitely concur on that point. I hate it. It is time for some serious term limits, and putting all the old dinosaurs in the Senate out to pasture, or a Petri dish

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Power-User

Join Date: Nov 2015
Posts: 133
#6
In reply to #2

Re: Electronic earthing system

05/17/2016 9:47 PM

you really had some sense of humor sir, good suggestion though.

__________________
formerly Legolaz
Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#14
In reply to #6

Re: Electronic earthing system

05/18/2016 1:47 PM

Ask any Signal Corps soldier about that . . . . . very effective.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Electronic earthing system

05/17/2016 5:17 PM

Hover cursor over picture and left click mouse.

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#17
In reply to #4

Re: Electronic earthing system

05/18/2016 2:32 PM

Any way out will do in a pinch.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Electronic Earthing System

05/18/2016 3:13 AM

Tip a tanker-load of seawater into the pit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Electronic Earthing System

05/18/2016 4:05 AM

Have the system designed properly by an Electrical Engineer instead of an Anonymous Poster. Electrical Engineers will know of the regulations prevailing in that locality and will design to suit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#9

Re: Electronic Earthing System

05/18/2016 6:04 AM

Have you used crushed or granulated slag, crushed slag doesn't hold moisture very well.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#13

Re: Electronic Earthing System

05/18/2016 1:35 PM

Maybe the problem is the test! More times than I care to think about, I've tested the "test" only to find out that the test equipment or the operator was the problem.

Take a look at another finished site to see if you get a different result. Better yet, call the metering equipment manufacturer for a proper description of how to use the equipment or how to perform the test.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#15

Re: Electronic Earthing System

05/18/2016 2:29 PM

I forget, is bentonite always recommended for earthing pits? I think that may be your problem, as it may have sealed the pits from conduction to moist soil around that area.

If the earthing pits have become dry (for one of a number or reasons), apply water injection and start over.

I do not recall any requirement for the use of copper plating in earthing pits at our power plants, but there again, if this is some giant electric arc furnace, you might have a real problem until you put some really large earth grounding in place, and you may have to get rid of the clay part of the pits.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Reply to Forum Thread 19 comments
Copy to Clipboard

Users who posted comments:

adreasler (3); Brave Sir Robin (2); jack of all trades (2); James Stewart (4); lyn (2); NotUrOrdinaryJoe (1); Peterpipper (1); PWSlack (3); TonyS (1)

Previous in Forum: Power Factor vs Fuel Consumption   Next in Forum: Power Plant Parallel Operation

Advertisement