Anonymous Poster #1

Power Factor For The Electric Motor

05/19/2016 3:36 AM

dear experts,

pls advise if there is minimum power factor for the electric motor based on IEC, ANSI or other international standard. as we know, lower power factor will draw higher current. i found only the minimum of the efficiency for the electric motor based on IEC 60034-30-1.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: power factor for the electric motor

05/19/2016 3:39 AM

Why?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: power factor for the electric motor

05/19/2016 3:49 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: power factor for the electric motor

05/19/2016 4:02 AM
  • Systems have power factors. Power factor correction equipment is used to approach unity. Investment is based upon the return to be gained from lower heat losses and smaller cables on the basis of the tariff charged.
  • The minimum power factor of anything is zero. An energised, unloaded cable could be said to have a power factor approaching zero.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5
In reply to #3

Re: power factor for the electric motor

05/19/2016 4:33 AM

But OP was asking about motors, and whether a minimum power factor is required by various standards. I don't know, but it seems a reasonable question.

__________________
Give masochists a fair crack of the whip
Reply
Anonymous Poster #1
#4

Re: power factor for the electric motor

05/19/2016 4:30 AM

my concern is on the power factor for the electric motor, if there are minimum requirement based on international standard (IEC, ANSI and etc..)..I just received an electric motor which mentioned in the datasheet that the power factor for this electric motor is 0.74 which is quite low for me, it cause the electric motor has high rated current.

For efficiency, there are min efficiency that the manufacturer have to follow as mentioned in IEC 60034-30-1. Whichever electric motor has the efficiency below the standard, it may say that its not comply with the international standard.

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #4

Re: power factor for the electric motor

05/19/2016 7:51 AM

....and the reason for the concern is what, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #4

Re: power factor for the electric motor

05/19/2016 9:02 AM

I'm not familiar with the standard, but if a minimum efficiency is specified it would have to be related to motor rating, as efficiency varies quite a bit with size - bigger ones have higher efficiency. Same goes for power factor.

__________________
Give masochists a fair crack of the whip
Reply Score 1 for Off Topic
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#12
In reply to #4

Re: power factor for the electric motor

05/21/2016 4:31 AM

Typically, motors with rated speed 1500 rpm or above have higher power factor such as 0.8/0.85 for LV and 0.85/0.9 for HV. Low rpm motors have low power factor and this is due to limitation in the principle of induction motors.

It may be good idea to go for Synchronous motor if the requirement is for low speed motor and high power factor is required.

This applies even if the kW rating happens to be a couple of thousands. in return for the additional expenditure, the benefits would be high power factor and efficiency.

__________________
Raghunath
Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#8

Re: Power Factor For The Electric Motor

05/20/2016 8:02 AM

It's like this. The power factor for an ideal inductor (or capacitor) is zero.

Since motors are made from loops of wire, it means by definition that they are in fact a version of the ideal inductor with the exception that the interaction between inductor fields causes motion, thereby making them useful for converting electrical energy into mechanical energy.

So, power factor really is an indicator of how much deviation there is between the perfect inductor and something that effectively converts electricity into mechanical energy. If you are concerned about the current, you can try to optimize the power factor (to 1.0000000000000000000000000000) or you can do something useful with your time.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9

Re: Power Factor For The Electric Motor

05/20/2016 11:07 AM

If your motor is not stamped "Conforms to XYZ Standard #123..." then there is no need for it to conform to any particular standard, it just has to perform to the information listed on the nameplate. You bought a motor on price alone, it was inexpensive because it has less iron and less copper than a high efficiency, better rated one of identical physical size that clearly states which standards it conforms to.

You got what you paid for, and as a bonus you will continue paying extra for it every hour that the motor is in service.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10

Re: Power Factor For The Electric Motor

05/20/2016 6:57 PM

It would be difficult to formulate a meaningful minimum standard for power factor. Partly loaded motors tend to have low power factor, so that a standard would have to allow for that, or maybe prohibit partly loaded motors, which would be ridiculous.

Power factor and efficiency are often confused, though quite distinct.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Power Factor For The Electric Motor

05/20/2016 8:22 PM

The "minimum" is going to be dictated by the utility servicing you, because they are the only ones who will really care. The reactive current represented by the low PF value has to be supplied by the utility, but is not registered on a WH meter, because by definition, Watts are a measurement INCLUSIVE of the PF; A x V x PF. But the utility is going to need to supply the kVA, ie A x V, so their distribution transformers and other lines and equipment must be over sized to accommodate that reactive current, even though they don't get paid for it.

That's why utilities will PENALIZE a user (not usually residential) for having a low PF, and most of then will base that on the PF being lower than .95. You will not find an AC induction motor that has a .95 PF however, it is up to the USER to correct the poor power factor if necessary.

Also, PF is a cumulative effect so if your total load has a lot of high PF loads, like resistive heating, such as 750kW, and only one inductive load like a 3kW motor with a .74PF, then the ratio of that total load represented by that one motor is really small and the fact that is it, stand-alone, at a .74PF, might be completely irrelevant. But if you are the other way around, with 3 x 250kW motors and 3kW of heating, you are going to need to correct the PF of those motors to avoid penalties.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Codemaster (2); JRaef (1); NotUrOrdinaryJoe (1); PWSlack (3); raghun (1); RAMConsult (1); SolarEagle (1); Tornado (1)