06/28/2016 6:55 PM

I have alighting controller that outputs a sourcing 0-10 volts.The LEDs I'm trying to dim require a sinking 0-10 volt controller.Are there any sourcing to sinking converters out there that would solve this problem?

66 Lighting fixtures,so it would have to be a fairly big converter.

Thanks for any suggestions.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7955
Good Answers: 459
#1

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/28/2016 7:50 PM

Manufacturer, model number of the lighting controller?

Manufacturer, model number of the lighting fixtures?

Is the voltage/current AC or DC?

How much current are you sourcing or sinking?

Is the 0-10 volts strictly a control voltage and there is another bus that provides the power?

Do you have a schematic diagram of the lighting circuit that you can share with us?

I've been in the electrical engineering field for 31 years now and I've never seen a sourcing to sinking converter. The best I can come up with is a voltage to current converter which is basically a transconductance amplifier. But most of these are designed for relatively low currents in instrumentation circuits. You could certainly scale up the output for larger currents. Or you could find a DC electronic load with analog input.

http://www.chromausa.com/product/modular-dc-electronic-load-63600/

Register to Reply
Associate

Join Date: Jun 2016
Posts: 34
#3
In reply to #1

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/28/2016 9:28 PM

Just to clarify a bit.The lighting controller i'm using outputs a 0-10 vdc "control signal". The controller supplies the 0-10vdc from its own internal power supply,therefore it is a "sourcing output".

The LED fixtures we're using have 0-10vdc dimming incorperated into each driver. The driver supplies 24vdc across the control leads,which then has to be broken down to 0-10vdc by the dimmer controller,ie. the voltage has to be "sunk' down to 0-10v.This is done by varying the resistance across the control leads.(Most new LED fixtures use such a sinking type control). The control leads are all wired in parralel back to the dimming controller.

Fixtures are 120-277 vac.

Is there any way to use such a lighting controller to control these fixtures?

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7955
Good Answers: 459
#7
In reply to #3

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/29/2016 2:16 PM

It will all depend on the design of your lighting controller. Since the fixtures will impose a 24 VDC voltage across the control lines, as long as your lighting controller can regulate voltage while sinking current, the answer would be yes. Without a schematic of the lighting controller, I have no way of saying for sure. A shunt type of regulator will typically sink or source currents while a series or pass regulator can (generally) only source current. If the lighting controller uses a switching topology, then it is only likely able to source current. There are some four quadrant switching topologies, but they are generally only used at higher power levels.

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7955
Good Answers: 459
#9
In reply to #3

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/29/2016 8:58 PM

Here is a simple circuit that will do basically that. This is basically a shunt voltage follower. The input goes into the inverting input of the operational amplifier because Q1 acts as an inverter. A few cautions here:
1. You can't take it completely to zero volts. You are limited at the lower limit by the saturation voltage of the NPN transistor. Roughly about 0.2 volts but it depends upon the base and collector currents.
2. You may need a higher current transistor than a classic 2N2222 depending on how much current each driver is going to output as you pull the 24 VDC down to the 10 to 0 VDC range. Only you know what the 'sinking' current will be. Short the fixture driver control line to ground and measure with an ammeter. If you have sixty-six fixtures, that may be a lot of current.
3. You may need to change the value of R5 depending on the beta of the transistor and the supply voltage to your op amp. Make sure that the base to emitter current doesn't exceed the specified value in the transistor data sheet for the given resistance and op amp supply voltage. For a 2N2222, I would keep the base current at or below 15 mA.

Good luck with your quest.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Apr 2015
Posts: 13
Good Answers: 2
#10
In reply to #9

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/30/2016 10:14 AM

This is how I would do it:

Use one transistor per lamp so you don't have to worry about current draw from the total circuit.

The emitter follower will convert the 0-10 volts drive into 0-10 volt sink.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#11
In reply to #10

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/30/2016 11:05 AM

You must like the smell of roasted BJT in the morning.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#12
In reply to #9

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/30/2016 11:14 AM

I like this.

My only criticism is that this assumes a common return between all three circuits. This is a reasonable assumption most of the time but we've all been burned by an unstated assumption.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7955
Good Answers: 459
#13
In reply to #12

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/30/2016 11:57 AM

So very true (common returns). The circuit was really just meant to illustrate the concept. We have so precious little information about the application, that it is impossible to provide a complete solution. There are no protections of any kind built into this, we don't know if a true zero volts is required (and hence a more complicated circuit to pull it all the way down to zero), we don't know the source impedance of the fixture drivers or the lighting control output, and . . . , and . . . ., and . . ..

Register to Reply
Associate

Join Date: Jun 2016
Posts: 34
#14
In reply to #13

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/30/2016 4:17 PM

Lighting controller 0-10volt output min. impedance=1200 ohms

One led driver control leads shorted together. current=20 milliamps

66 led drivers 0-10v control leads all shorted together: max control current=20 milliamps. Sounds crazy that control current doesn't increase from 1-66 fixtures, but I Flukemetered it.

This won't require true zero volts;1.0 volts would be low enough.

Returns could all be made common.

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7955
Good Answers: 459
#15
In reply to #14

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/30/2016 5:36 PM

Sounds like you've got it made in the shade then. Sounds like you could do this with one PNP transistor in that case. You might need some series resistance in the base to limit base current. Or you could go with the op amp approach which provides a bit more isolation between the lighting controller and lighting fixtures.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2016
Posts: 34
#16
In reply to #9

Re: Convert Sourcing 0-10v to 0-10v Sinking

03/23/2018 12:22 AM

What is device U1? Never seen that symbol before.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#17
In reply to #16

Re: Convert Sourcing 0-10v to 0-10v Sinking

03/23/2018 7:50 AM

U1 is an unspecified operational amplifier.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9940
Good Answers: 1148
#2

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/28/2016 7:56 PM

I am assuming this is 66 circuits that you want to invert. What is the current draw on the LEDs? You might be able to use some NPN Darlington Transistor Array ICs (8 circuits each). They will sink 500 ma. on each circuit. If your load is greater than that, you can connect more than one circuit in parallel to increase current.

http://www.ti.com/lit/ds/symlink/uln2803a.pdf

Register to Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#4

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/29/2016 2:36 AM

This post is left intentionally blank
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15620
Good Answers: 986
#5

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/29/2016 9:16 AM

I think Professor Norton and Professor Thevenin should be able to answer your question. They will also need to know the driver and receiver circuits that you have. Careful use of these two guiding principles in testing and analysis can tell you the equivalent circuits you actually have if the manufacturer of the circuits does not give you any support. After doing this work you might find that you only need to add one external load resistor to get this to work.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#6

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/29/2016 11:06 AM

its been pretty common and has been discussed in a number of degrees here.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#8

Re: Convert Sourcing 0-10v to 0-10v Sinking

06/29/2016 7:11 PM

Something like this http://www.automationdirect.com/adc/Shopping/Catalog/Process_Control_-a-_Measurement/Signal_Conditioners/DC_Voltage,_Current_or_Potentiometer_Input/FC-33 ? You'd have to make sure it can sink the current you need. If that doesn't work out, Google something like 'voltage converter', 'power conditioner', or similar combinations.

Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bigg (1); Brave Sir Robin (5); KB0RAE (1); phoenix911 (1); redfred (4); REH (3); Rixter (1); user-deleted-1105 (1)

Previous in Forum: What Would You Use and Why   Next in Forum: Loss of Excitation

Advertisement