pl tell me the copper busbar size calculation for current rating of 3000A for temp rise of 85°C
Good Answers: 19
Re: busbar size
08/05/2007 11:08 PM
Please check ,generally the final temperature of busbar would be 85 deg C, not the temperature rise.Please inform ambient temperature.
I have answered to such a question earlier reply.
Ramesh,Freelance Electrical/automation Consultant
Re: busbar size
08/06/2007 7:14 AM
Go to
http://www.copper.org
There are tables for quick sizing copper busbar and the equation for determining bus bar size based on several considerations.
Re: busbar size
08/06/2007 7:03 AM
When you supply enough information to solve the problem, you will probably be able to come up with your own answer. You need to consider the power dissipated in the bus bar (current, resistance, and power factor), and the rate power is dissipated from it (type of cooling). You can then design for delta T. Not rocket science.
Re: busbar size
08/06/2007 9:25 AM
The industry standard rating for a 4"x1/4" cross section of copper bus is 400 amps.
Good Answers: 21
Re: busbar size
08/06/2007 1:23 PM
Old rule of thumb in the switchgear industry has been 1000 amp per 1 sq. in. of buss. 3ka ought to be at least 3x 1/4x 4 Newer tables will show 1200ish but ... 1/4 by 4 is 1000amp.
http://www.stormcopper.com/design/Ampacity-Quick-Chart.htm
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.