Effect of Saturated Current Transformers On Distance Relays

07/06/2016 10:26 AM

hello,

I have come across literature where it is stated that saturating current transformers could lead to distance relay 'under reaching.' I thought the opposite is true I.e saturation of current transformers would lead to 'over reaching' as a saturated CT supplies less current to the relay.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: Effect of Saturated Current Transformers On Distance Relays

07/06/2016 7:47 PM

A distance relay detects a fault by measuring the impedance of a transmission line. Impedance is the ratio of voltage to current. The distance relay is set up so the cable voltage holds the relay in place and the current causes it to energize.

http://www.electrical4u.com/distance-relay-or-impedance-relay-working-principle-types/

The farther the fault the higher the voltage and lower the current. For example, a very near fault would result in high current and low voltage. The relay is designed to detect a fault out to a specific distance which would have a defined ratio of voltage and current. If the actual distance that the relay detects faults is less than the design distance, this is termed under reach. Likewise, if the actual distance is greater than the design distance, it is over reach.

https://www.quora.com/What-is-over-reach-and-under-reach-of-a-protecting-relay

Since the current to voltage ratio decreases with distance to the fault, if the current is reduced due to saturation of the CT, the farthest fault distance that can be detected is reduced from the design distance, the definition of under reach.

Register to Reply Good Answer (Score 3)