Ex nA Motor in Hazardous Area

07/07/2016 5:48 AM

Ex nA by definition indicates that motor is non sparking in normal operating condition.

Normal condition is defined as full load condition.

However which condition for motor ( in zone 2) shall be considered as abnormal which shall cause a spark ( which in tern will be difficult to be installed in hazardous area)

Register to Reply
Pathfinder Tags: Exd ExnA hazardous area motor Zone 2
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Ex nA motor in Hazardous area

07/07/2016 5:53 AM

The question is nonsense.

  • Zone 2 is where a flammable gas/air mixture is unlikely to occur in normal operation, and if it does occur it will be present only a short time.
  • Ex nA is suitable for Zone 2.
  • Therefore provided the gas group and temperature rating are compatible, the motor and the zone are also compatible.

End of.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: May 2007
Posts: 4
#2
In reply to #1

Re: Ex nA motor in Hazardous area

07/07/2016 7:44 AM

u should not be called ur self as a guru,

question is not for asking definition or is motor compatible in zone 2 or not

please read properly , ur degree in electrical is in doubt ? u should retake electrical engineering.

what I am asking when they certify motor for ExnA, which abnormal condition they do not consider.

for u I am rephrasing ?

please forget this person and anser

Register to Reply Off Topic (Score 9)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #2

Re: Ex nA motor in Hazardous area

07/07/2016 8:45 AM

If you want free advice then you shouldn't insult those who answer you.

Obviously you should not criticize people on their schooling. Please review your grammar on spelling and punctuation before you rebuke others for misunderstanding your words.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: Ex nA motor in Hazardous area

07/07/2016 8:53 AM

Read this and this, then, for educational completeness, as normality in this area has nothing to do with the motor.

To confine oneself to the topic of Electrical Engineering would lead to a somewhat blinkered view of the subject, as evidenced by the quality of remarks made in #2 above and any response thereto.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Ex nA Motor in Hazardous Area

07/07/2016 9:20 AM

<...Normal condition is defined as full load condition....> Not in this context. Normal in ATEX terms is the normal containment of process materials. The Directive cannot deal with unforeseen circumstances such as a leaking, rusty pipe spilling flammables everywhere or, say, an aeroplane crashing onto the plant, for these things are abnormal in the context of equipment operation.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6

Re: Ex nA Motor in Hazardous Area

07/07/2016 11:04 AM

"...Ex nA by definition indicates that motor is non sparking in normal operating condition...", no it does not. What it does say in IS/IEC 60079-15, Section 4.2 Potential Ignition Sources:

"In Normal operation and in certain abnormal conditions specified by this standard, the apparatus shall not:

a) produce an operational arc or spark unless that arc or spark is prevented from causing ignition of of a surrounding explosive atmosphere by one of the methods described in Clauses 26 to 31..."

The key word is "prevented"; i.e., the equipment is designed to contain the arc/spark, not necessarily to prevent its occurrence, but to prevent its escape. In other words, the motor can spark under operational conditions, as long as those sparks do not reach the atmosphere outside the equipment, or vice-versa.

"...which abnormal condition they do not consider...", in other words you want to know if the standard covers all the unknown unknowns?! Thankfully the standard covers this by the use of the words "...certain abnormal conditions..." as stated in the preamble above.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: Ex nA Motor in Hazardous Area

07/07/2016 11:47 AM

One can only hope, for the sake of other CR4 readers who may well be in the vicinity of the installation when it is energised, that the original poster's reading skills are better than the writing skills displayed in #2 above, otherwise the help will be wasted....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: May 2007
Posts: 4
#8
In reply to #7

Re: Ex nA Motor in Hazardous Area

07/07/2016 12:18 PM

specifically u dont have knowledge so please dont come to this post.

You are totally waste.

You people are not from motor manufacturing industry so you should not answer.

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #8

Re: Ex nA Motor in Hazardous Area

07/07/2016 1:05 PM

What we have here is a failure to communicate.

As I expected, the reading skills are just as well refined as the writing skills. GIGO (That's a common acronym, son. You can look it up if you need to.)

Good Luck in your work. Try not to kill anyone. If your lucky you'll only embarrass yourself.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Participant

Join Date: May 2007
Posts: 4
#10
In reply to #9

Re: Ex nA Motor in Hazardous Area

07/07/2016 1:15 PM

i doubt ur skill, i found u are most useless person on earth , how many people have u killed in ur electrical carrier?

u dont know any thing and just coming here to show that ur forefather is tesla, why u are not still banned in this forum?

Register to Reply Off Topic (Score 8)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #10

Re: Ex nA Motor in Hazardous Area

07/07/2016 2:35 PM

Having claimed in a personal message via CR4's personal messaging system that username PWSlack is the <...useless person in world...>, the additional claim here that username Redfred is also the <...most useless person on earth...> simply invokes the response that the probability that both statements are abstruse has risen quite sharply.

[The full text of the personal message received in PWSlack's inbox was:

<...dont come to my post, u useless person in world?

if u cant discuss technical, which i highly doubt ?...>

It's writing that other readers might find quite amusing, and is shared for the sport that might arise therefrom.]

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #8

Re: Ex nA Motor in Hazardous Area

07/07/2016 3:12 PM

If the post were aimed solely at motor manufacturers then one might venture to suggest that an anonymous on-line Engineering forum is the wrong place to search for an answer to the technicalities involved in the original post. Motor manufacturers are listed in regional and national telephone directories and an interpersonal approach by telephone would yield more information from an original-poster-validated source far more quickly than a wait for information via CR4 ever could.

A highly recommended tool, is the telephone. There are now so many of them in the world, it is amazing that they are not used more frequently.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Power-User
CR4 Admins - CR4 Admin - CR4 Admin

Join Date: Jul 2008
Posts: 372
Good Answers: 33
#13
In reply to #12

Re: Ex nA Motor in Hazardous Area

07/07/2016 3:23 PM

Do you think someone should first give the "motor manufacturing industry" a heads-up about this incoming phone call?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14
In reply to #13

Re: Ex nA Motor in Hazardous Area

07/07/2016 3:35 PM

One might ring round looking for volunteers, perhaps. However, on account of <...useless person in world...> claims, enthusiasm for the task is somewhat lacking here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
CR4 Admins - CR4 Admin - CR4 Admin

Join Date: Jul 2008
Posts: 372
Good Answers: 33
#15
In reply to #14

Re: Ex nA Motor in Hazardous Area

07/07/2016 3:42 PM

You wouldn't be living up to your title, otherwise!

Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

PWSlack (7); RAMConsult (1); redfred (2); sumit4u13 (3); yamdankee (2)