In one of my project I need to retrofit old generator protection relay with MiCOM P343. In old setup there are two relays in rotor earth fault circuit one is voltage balance relay (the generator is contra-rotating turbine having two field windings in series) used for interturn faults in rotor windings and another is conventional relay based on rotor circuit impedance.
Now my query:
providing P391 unit will be sufficient to take care of all kind of rotor earth faults? I mean can I use it as a replacement of two separate relays?
Please help.
Pathfinder Tags: MiCOM P343 P391 rotor earth fault
Good Answers: 181
Re: Rotor Earth Fault through MiCom p391
07/30/2016 12:06 PM
I’ve looked at your previous posts, do you ever feel guilty cashing your pay cheque?
Register to Reply Off Topic (Score 15)
07/30/2016 1:57 PM
07/31/2016 5:40 PM
Please advise the outcome of the telephone calls that have taken place on this topic with the equipment manufacturer and why an answer has not been forthcoming from that source?
08/01/2016 10:01 AM
It looks like neither of your protective relays detect earthing faults, despite your statement that they are in the rotor earth fault circuit. It may be if you do get an earth fault, the excitation protection may take itself off line, or perhaps float until the next ground fault.
Do both of the existing relays trip off the machine?
Not sure of the value of voltage balance relays, but it could be a good diagnostic tool if your excitation current increased unexpectedly to hold terminal voltage. The relay could indicate turn to turn short circuit in one of the two windings.
From Solar Eagle contribution, thank you....
The voltage balance detection between field windings is not covered in the Micom.
You need a special version of your Micom, and another device to couple to the rotor circuit.