Rotor Earth Fault through MiCom p391

07/30/2016 7:32 AM

In one of my project I need to retrofit old generator protection relay with MiCOM P343. In old setup there are two relays in rotor earth fault circuit one is voltage balance relay (the generator is contra-rotating turbine having two field windings in series) used for interturn faults in rotor windings and another is conventional relay based on rotor circuit impedance.

Now my query:

providing P391 unit will be sufficient to take care of all kind of rotor earth faults? I mean can I use it as a replacement of two separate relays?

Please help.

Register to Reply
Pathfinder Tags: MiCOM P343 P391 rotor earth fault
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Rotor Earth Fault through MiCom p391

07/30/2016 12:06 PM

I’ve looked at your previous posts, do you ever feel guilty cashing your pay cheque?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Off Topic (Score 15)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Rotor Earth Fault through MiCom p391

07/30/2016 1:57 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Rotor Earth Fault through MiCom p391

07/31/2016 5:40 PM

Please advise the outcome of the telephone calls that have taken place on this topic with the equipment manufacturer and why an answer has not been forthcoming from that source?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1369
Good Answers: 105
#4

Re: Rotor Earth Fault through MiCom p391

08/01/2016 10:01 AM

It looks like neither of your protective relays detect earthing faults, despite your statement that they are in the rotor earth fault circuit. It may be if you do get an earth fault, the excitation protection may take itself off line, or perhaps float until the next ground fault.

Do both of the existing relays trip off the machine?

Not sure of the value of voltage balance relays, but it could be a good diagnostic tool if your excitation current increased unexpectedly to hold terminal voltage. The relay could indicate turn to turn short circuit in one of the two windings.

From Solar Eagle contribution, thank you....

The voltage balance detection between field windings is not covered in the Micom.

You need a special version of your Micom, and another device to couple to the rotor circuit.

You do get an output from the Micom that can measure some degree of turn to turn faults, not sure if it is connected to an automatic protective function, they pass it to a current loop which then most likely is connected to an alarm, rather than trip.

Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (1); rwilliams (1); SolarEagle (1); TonyS (1)

Previous in Forum: Two Cores of Power Cable are Shorted with Ground and Still Motor is Running   Next in Forum: Dielectric Properties of Water Emulsions

Advertisement