VCB Closing and Opening Coil Inrush

08/07/2016 12:22 PM

Dear All,

The control circuit breaker to the VCB closing and tripping coil is tripping. The Closing coils are of 110V DC rating. The Control circuit breaker gives 220V AC supply to the bridge rectifier and then rectifier converts the 220V AC to 220V DC
What happens when 110V Dc rated coil is energized with 220V DC?

Is it because of higher inrush when applied with 220V DC?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: VCB Closing and Opening Coil Inrush

08/07/2016 12:30 PM

What do YOU think?

Surely you have an opinion about running a coil rated at 110 VDC at TWICE that voltage.

If you are a student, do your own homework!

If you are applying for a job, don't bother.

If this is a work related question, quit your job now, before they fire you.

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: VCB Closing and Opening Coil Inrush

08/07/2016 3:48 PM

"...What happens when 110V Dc rated coil is energized with 220V DC?

"...The control circuit breaker to the VCB closing and tripping coil is tripping..."

See, you know the answer!!!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: VCB Closing and Opening Coil Inrush

08/07/2016 3:56 PM

Call the manufacturer, buy the right coil, and have a qualified electrician install it.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: VCB Closing and Opening Coil Inrush

08/07/2016 4:15 PM

You need to control the inrush current ...this will cause control failure....

http://electronicdesign.com/power/limit-inrush-current-ac-dc-power-supplies-and-rectifiers

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#5

Re: VCB Closing and Opening Coil Inrush

08/07/2016 5:14 PM

Applying ohms law, a 110V DC coil energised at 220V will draw twice its rated current and dissipate 4 times the watts.

The coil will burn-out if connected continuously.

So the designer did a good job if the control circuit breaker operates before the coil fails.

It may be that 110V DC continuous coil is energised at 220V to give greater speed and pull. But it would be necessary that the coil was disconnected by an auxiliary contact after the breaker closed, else it will overheat and fail. It might be that the auxiliary contact operation inserts a resistor in the circuit which limits the current to less than the coil continuous rated current and holds the breaker closed.

So if the auxiliary contact is not working or the resistor is shorted you will get an excessive current and the control circuit overcurrent breaker operates.

Did the VCB close??

At this point my "magician's crystal ball" is a lot less reliable than your eyes and tools at the circuit/wiring diagrams and the breaker.

Read the Maintenance Manual. Please ensure all safety precautions like isolating, grounding and "checking dead" the HV supply are observed before working on the breaker.

A DC coil may have an "inrush" current which is that taken with only its own resistance limiting current and a "holding" current which is got by a ballast resistor once it is operated [switched into circuit by the auxiliary contact mentioned].

"Control circuit breakers" often have a thermal overload element and a magnetic instant trip which operates at about 5 times their rated current for short-circuit protection. I think it is likely to be the thermal element trip you have tripping - there would be a noticeable delay after pressing "VCB close" before thermal trip.

Please tell us what else you you find out, information like the measured resistance of the Closing coil and the type and rating of the "control circuit breaker" and circuit diagram would help.

67model

Reply Score 1 for Good Answer
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#6

Re: VCB Closing and Opening Coil Inrush

08/08/2016 10:46 AM

Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7

Re: VCB Closing and Opening Coil Inrush

08/08/2016 3:17 PM

It sounds like the contactor was designed to operate with this equipment. It's not likely someone changed parts with some random voltage rating. Normally it is a full wave bridge (as you note), and the applied voltage is reduced with a resistor or electronic circuit once the contactor is proven closed. You may have missed this part, as the controls are often in a potted assembly with just wires coming out. A half wave rectifier would give you about the right voltage for the coil.

Once the dc coil has moved the load, it only requires about 20% of the voltage to hold in the mechanical load, where an ac coil requires over 60% of the normal voltage to hold in position. Your equipment then can more easily ride through power dips.

One of the reasons your control circuit breaker could be tripping is the armature of your contactor is not closing all the way. A small amount of contamination/rust paperclip or junk on the laminations, preventing full closure of the magnetic circuit, can cause large amounts of current to flow in the coil, tripping your breaker. Also not so good for your breaker, as the overtravel for the power contacts typically designed in may not happen, leading to local heating in the bottles.

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Jpfalt (1); lyn (1); RAMConsult (1); rwilliams (1); SolarEagle (1); Tornado (1)

Previous in Forum: Proper Location of OHL to Install Line Voltage   Next in Forum: API Bubbles

Advertisement