Fire Pump System Operation

08/10/2016 9:38 AM

sorry if this question has been ask many times, i already do search engine and didnt found it

i need to make an assignment regarding the operation of the fire pump. but i a bit confusing.

as i know, when the sprinkler is activate, the water would flow and the pressure in the pipe would decrease. so the jockey pump is active to maintain the pressure in the pipe so that water can be flow without interrupted. my question is, what the purpose of the duty pump and the standby pump?

i hope someone can clarify me about this. sorry for my bad english since it is not my native language. thanks.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: fire pump system operation

08/10/2016 10:23 AM

You should find a job that fits your knowledge base. You will surely kill many people with your lack of knowledge!

Fire pump - Wikipedia, the free encyclopedia

Register to Reply Off Topic (Score 3)
Participant

Join Date: Aug 2016
Posts: 3
#2
In reply to #1

Re: fire pump system operation

08/10/2016 10:44 AM

I have read that. But it didnt explain about the duty pump and also the standby pump.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #2

Re: fire pump system operation

08/10/2016 10:55 AM

My point is, if you don't know what you are doing, DON'T DO ANYTHING!

IT IS IRRESPONSIBLE OF OTHERS TO PUT WHAT IS ESSENTAILLY A LOADED GUN INTO THHE HANDS OF A BLIND MAN!

Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: fire pump system operation

08/10/2016 11:15 AM

I think he's just a student...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: fire pump system operation

08/10/2016 12:09 PM

Perhaps, but if this is the way he completes an assignment, what will he do in the real world?

Searching and finding correct, authoritative answers, with adequate supporting data is something that must be learned early on.

Internet searches are, as you demonstrate every day, are not a black art.

Register to Reply
Participant

Join Date: Aug 2016
Posts: 3
#11
In reply to #6

Re: fire pump system operation

08/10/2016 10:40 PM

Please dont mad at me..

My lecturer just tell me to find about fire pump, focus on Jockey, duty and standby pump. And I just doing my research based on that key point.

Maybe you can give me some idea regarding this

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12
In reply to #11

Re: fire pump system operation

08/10/2016 11:24 PM

Learn how to search!!!

Operational Sequence for Fire Pumps - ENGINEERING.com - AskForum

NEC Rules for Fire Pumps

Fire Pumps | Grundfos

I entered, "Jockey, duty and standby [fire] pump", words you used.

I got About 16,800 results.

Learn how to search!

Register to Reply
Member

Join Date: Sep 2009
Posts: 7
#14
In reply to #1

Re: fire pump system operation

08/11/2016 9:51 AM

" The supply of fools will always outstrip the demand ".....your words...

The same goes for negative critics.

We're all here to help each other. That's what the Forum is for.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#15
In reply to #14

Re: fire pump system operation

08/11/2016 10:13 AM

Well,

Get on with helping the OP, then.

Here is an example of how to help the OP.

Operational Sequence for Fire Pumps - ENGINEERING.com - AskForum

NEC Rules for Fire Pumps

Fire Pumps | Grundfos

Your total "contribution" of 6 posts means you have a way to go!

And in two of those posts, you are preaching to others about their lack of professionalism?

English Rose certainly didn't need an admonishment from the likes of you and neither do I.

Now, quit preaching and help the student do their homework!!!

Register to Reply
Member

Join Date: Sep 2009
Posts: 7
#16
In reply to #15

Re: fire pump system operation

08/11/2016 10:34 AM

"And in two of those posts, you are preaching to others about their lack of professionalism?" .......your words.

And now in 3 posts......

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#17
In reply to #16

Re: fire pump system operation

08/11/2016 11:24 AM

Pdm Engineer Member
Join Date: Sep 2009 Posts: 7

#

25
In reply to #9

Re: Siemens Motor

09/24/2009 7:18 AM
Are you an Engineer? If you are, you lack professionalism.....we should focus on helping this gentleman with the problem and keep negative criticism to ourselves.
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#20
In reply to #16

Re: fire pump system operation

08/15/2016 1:54 PM

Community

Acquired Engineering360

CR4 - The Engineer's Place for News and Discussion ®

Where does it state CR4® is the place to go for your Engineering degree? It doesn't.

Lyn said it best in post #4, "IT IS IRRESPONSIBLE OF OTHERS TO PUT WHAT IS ESSENTIALLY A LOADED GUN INTO THE HANDS OF A BLIND MAN!"

Fire suppression system is life critical, lives depends on the Engineer getting it right the first time. An anonymous forum is not the place to acquire your engineering degree or skills.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#21
In reply to #20

Re: fire pump system operation

08/16/2016 9:32 AM

I agree 100% with your and Lyn's intent here. Clueless, lazy people should not be allowed to design critical systems. I disagree that the design of a fire pump system is to save lives. A fire pump system attempts to prevent a bad situation from getting worse. Often lives will be saved in this process but life saving is not the primary goal. Respirators, defribulators, extraction harnesses and fire escapes saves lives. Putting out a fire protects property.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#24
In reply to #21

Re: fire pump system operation

08/16/2016 9:52 PM

You right in the fact the pumps are for fire suppression. But if your on the 13th floor and the fire is on the 7th floor, it becomes life critical that the pumps operate properly and suppress the fire/ heat otherwise ..... you crapped out of luck

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#23
In reply to #20

Re: fire pump system operation

08/16/2016 11:12 AM

I got at least 30% of my engineering skills while staying at a Holiday Inn, or was that Howard Johnson's...I forget, since they did not issue me a certificate.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#18
In reply to #14

Re: fire pump system operation

08/11/2016 2:50 PM

Please do elaborate your point: You mention negative critics. Is there another kind I am not aware of? Usually criticism is meant to point out flaws in a (1) design, (2) concept, (3) mathematical expression, or (4) constructed object.

If there were no negative (constructive) criticism, then no one would grow from their mistakes, receiving no feedback on weaknesses of what they are doing, they would progress from milding amusing to downright dangerous, to completely negligent contructions that result in injuries, maimings, and death.

I for one, thank God Almightly for engineers that can take criticism without taking it personally, and can dish it out as well as receive it. That, sir, is what the forum is for.

It is not the place for the little Johnnies of the world to come ask for the answer to their homework on a silver platter. We don't do that around here, we don't do floors, and we don't do windows, although we have criticized Windows (various versions) over and over again.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: fire pump system operation

08/10/2016 10:45 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
4
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#7

Re: Fire Pump System Operation

08/10/2016 12:50 PM

The jockey pump is much smaller than the duty pump, and is only there to maintain the pressure in the system without ever turning on the other pumps.

The jockey pump cannot maintain the flow necessary to feed an active sprinkler.

If there is a fire the duty pump runs, and, assuming that the demand is not too high it can deliver enough flow.

The standby pump will normally be a diesel pump, it will start if the main duty pump cannot meet the demand, or, there is a power failure to the duty pump.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #7

Re: Fire Pump System Operation

08/15/2016 9:40 AM

<...standby pump...will start if the main duty pump cannot meet the demand...> Ahem, actually, that would make it an assist pump, and not a standby pump.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#22
In reply to #19

Re: Fire Pump System Operation

08/16/2016 11:09 AM

Ok, then what is it when the main duty pump is handling the situation without any further assistance? The non-assisting pump? Really? I think this pump is offline more of the time than online, therefore when it is ready to operate, but not operating it is the stand-by pump, because you are (or are not) standing by it.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8

Re: Fire Pump System Operation

08/10/2016 1:14 PM

What assignment does any pump need? ON or OFF are the only assignments the pump needs. Its not like one can give a pump the assignment to squirt water in room 375 above the wastebasket. The pipes, hoses, sprinklers and steering valves select and steer where the fire protecting or extinguishing fluid goes. The pump provides only pressure for the fluid.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9
In reply to #8

Re: Fire Pump System Operation

08/10/2016 3:11 PM

The pump didn't get the assignment, the op did...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #9

Re: Fire Pump System Operation

08/10/2016 4:19 PM

ROFLMAO! Wow. not a clue about the duty (main) pump, or the standby (backup) pump, and wants to think the jockey pump is there to provide flow during an event. How dangerous is that?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#13

Re: Fire Pump System Operation

08/11/2016 5:19 AM

I worked on pressure tank system designed by my Australian boss Mr. Sam D Jovine. All electrical pumps. In this 1000 ltr pressure ventricle tank is used and small 1 HP pump keeps the pressure at 8 Bar against Air at top. When any sprinkler or jet opens, the pressure drop activates 30 HP pump.

Also please check this: http://www.sialco.ro/pdf/Documentatie-GRUNDFOS-pompe-4-7-2-Sisteme-pompare-in-instalatiile-stins-incendiu-EN-sialco-distribuitor-GRUNDFOS-romania.pdf

__________________
Subramanyam
Register to Reply
Register to Reply 24 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

dj95401 (2); James Stewart (4); kvsubramanyam (1); lyn (6); Pdm Engineer (2); PWSlack (1); Randall (1); redfred (2); renyyz (2); SolarEagle (3)