Active Contributor

Join Date: Aug 2016
Posts: 14

Bus Tie Duct Noise

08/22/2016 6:41 AM

Dear Sir,

We have installed BTD for 5000A,bus bar 120X10X4 for each phase, when load cross 2400A , than there is lot of noise , can you explain how we can decrease noise, and tell how minimum clearance need between phase to phase bus bar and phase to earth bus bar

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Bus Tie Duct Noise

08/22/2016 8:04 AM

I would start with safely measuring and recording the acoustic (?) noise in both amplitude and frequency. This should do two things for you. It will give you a baseline to compare your later attempts to reduce this noise and you will now have information that one can analyze.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Bus Tie Duct Noise

08/22/2016 8:21 AM

It comes as a surprise to learn that the installation is claimed to be complete, and that the assessment of minimum clearance necessary for correct installation has not been completed! The organisation's procedures would warrant a careful reassessment in that case.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Bus Tie Duct Noise

08/22/2016 10:02 AM

The magnetic forces increase as the square of the current; i.e., the forces at 4,800 Amps is four times greater than at 2,400Amps. Any loose or improperly torqued connectors, insulators, fasteners, supports, panels, covers, etc. will be effected by these forces. Your only solution is to do a complete inspection and retorqueing of every connection and fastener in the entire bus duct assembly, and (Darwin Award spoiler) don't forget to deenergize the equipment.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Bus Tie Duct Noise

08/22/2016 3:23 PM

Define "noise".

Can you give the amplitude and frequency of the noise?

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5

Re: Bus Tie Duct Noise

08/23/2016 4:21 AM

Copper or aluminium bars, the separation, the support/bracing spacing, nothing other than the bars would appear to be undersized.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#6

Re: Bus Tie Duct Noise

08/23/2016 7:16 AM

Is the loud noise a "HUM"?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#7
In reply to #6

Re: Bus Tie Duct Noise

08/23/2016 9:54 AM

Why do the bus bars hum - because they don't know the words? JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#8
In reply to #7

Re: Bus Tie Duct Noise

08/23/2016 10:21 AM

DANG IT! Steal a man's thunder will ya?!

That was gonna be my reply if he answered yes!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#10
In reply to #8

Re: Bus Tie Duct Noise

08/23/2016 12:06 PM

Never ceases to amaze me the questions posted about projects in the multi mega watt and multi mega $ range and it seems the poster has no comprehension of what will, can or may happen. I had to take my shoes and socks off and still couldn't count the power (s)he is talking about - even at fairly low voltage. I have never worked with that kind of power and so I can't imagine how loud the "bang" will be. Even the Mythbusters should be impressed. And that's not even thinking about the death and destruction that is sure to follow. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: Bus Tie Duct Noise

08/23/2016 1:28 PM

It helps to thin the gene pool.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #7

Re: Bus Tie Duct Noise

08/23/2016 10:58 AM

Hum a few bars and maybe I'll pick it up.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#12

Re: Bus Tie Duct Noise

08/23/2016 2:08 PM

The voltage of the installation will determine some of the clearance requirements, and the BIL of the other attached equipment will also determine clearance, to coordinate the insulation. Also, what is the insulation system, and whether the system is solidly or effectively grounded could also be a factor.

Heat dissipation may also be a factor in the conductor spacing, if you plan to alter the original design and clearances of the original equipment.

Register to Reply
Register to Reply 12 comments