I had a problem in one my Electrical panel,The DLM meter is showing different current reading (R & B will be same & Y will be double the R & B).
We have check the CT connection ,Meter connections & measure the Input current no where else we could not able to trace the Problem.
Regards
Murali
Re: Current Reading is Uniform in All the Phases
09/06/2016 10:06 AM
So, what do you want? Another reader to drive the equipment?
There's a charge for that, you know.
Good moaning!
09/06/2016 11:34 AM
Hire a knowledgeable electrician, and have him hire an electrical engineer with some experience, and you find another job not involving electricity?
09/06/2016 12:33 PM
Have you considered looking at the loads on the system since that is what determines the current draw in the system?
09/06/2016 3:05 PM
Quite. Imbalance is a norm.
Good moaning!
09/06/2016 4:11 PM
Especially here on CR4.
09/06/2016 4:55 PM
NO, that is unbalance. Some of us here lean to the right, some to the left. All of us wobble after Lyn blows bullshine up our skirts. It does make for a lively day, though.
09/06/2016 6:49 PM
The truth, the whole truth, and nothing but the truth.
09/06/2016 6:42 PM
One of the loads might consist of a ground fault on phase Y....
Good Answers: 804
09/06/2016 8:04 PM
The CT on Y phase may be mounted backward.
09/07/2016 12:41 AM
You may not have these wired properly...can you provide a diagram?
http://cr4.globalspec.com/thread/58018/why-Current-transformer-Star-point-is-grounded
Good Answers: 42
10/04/2016 1:27 PM
DLM=Digital Light Meter. How you use it? See for instance:
http://www.jameco.com/Jameco/Products/ProdDS/2140251UsersManual.pdf
or:
file:///C:/Users/user/Downloads/DLM-Power-Monitoring-Provides-Unique-Snapshots-of-Power-Use-Technical-Bulletin.pdf