Three Phase Ungrounded Fault - Symmetrical Components

09/12/2016 12:05 PM

I have a low resistor grounded system. How do you compute the three phase ungrounded fault through symmetrical components at a distance of the source? Can you please advise of a textbook that lists exactly the three phase ungrounded fault calculations? I see only three phase grounded fault calculation which is only the positive sequence circuit and the fault impedance in series and a single line to ground fault which is the three positive, negative, and zero sequence circuits and a fault resistance in series. Could not find a book about three phase ungrounded fault calculations!!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Three Phase Ungrounded Fault - Symmetrical Components

09/12/2016 4:43 PM

There cannot be a significant ground fault current in an ungrounded system, unsurprisingly. The only faults that can occur are circuit overcurrent, for which the usual suspects of circuit breaker or fuse are applicable, and ground fault, which is expressed by the phase voltage with respect to earth/ground dropping.

  • In hospitals, which is where ungrounded systems can be found, a pesky ground fault can be tolerated without disconnecting the supply, on the basis that it is better to sustain a ground fault and report it rather than disconnect a piece of equipment that is supplying precious life-support!
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Three Phase Ungrounded Fault - Symmetrical Components

09/12/2016 5:34 PM

Any classic textbook on Symmetrical Components will answer your question, you will even find out that a three phase fault has exactly the same current as a three phase to ground fault, even more magically you will find that only positive sequence currents flow making it the easiest fault to calculate.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Three Phase Ungrounded Fault - Symmetrical Components

09/19/2016 10:54 AM

In my opinion, in ungrounded-or High Resistance Grounded-system a phase-to-ground-to-phase will be the highest level current. It is difficult to imagine a three phase-to-ground in the same time. However, only a very small part –negligible- of

this current will return to neutral through grounding resistor.

Through the neutral grounding resistor the highest level current will flow only in

one phase-to-ground fault case.

See[for information]:

GE Application Information Short-Circuit Current Calculations
http://apps.geindustrial.com/publibrary/checkout/GET-3550F?TNR=White%20Papers|GET-3550F|generic
Post Glover NEUTRAL GROUNDING RESISTORS TECHNICAL INFORMATION

http://www.postglover.com/download/neutral-grounding-resistors-technical-information/

__________________
Julius
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5
In reply to #3

Re: Three Phase Ungrounded Fault - Symmetrical Components

09/19/2016 5:39 PM

Fortunately this is engineering science, not political science, where facts are more important than opinions. From your GE reference, page 12, Three-phase Bolted Short Circuit: "A three-phase bolted short-circuit...generally results in the maximum short-circuit values and for this reason is the basic short-circuit calculation in commercial and industrial power systems."

Granted this is the least likely fault (less than 5% occurrence vs. all other types), but it yields a conservative value; i.e., no other type of fault will exceed this value. (There are certain exceptions to this, but only those engineers that deal with switchgear directly connected to utility-sized generators that are also grid-connected, will ever encounter these specialized situations. That's why segregated phase bus is used between the generator and the step-up transformer, specifically to prevent such faults.)

To continue from the reference (and to address OP's question), "In most three-phase power systems, the levels of line-to-line bolted short circuits currents are approximately 87% of three-phase bolted short circuits currents, but this calculation is seldom required because it is not the maximum value."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#6
In reply to #5

Re: Three Phase Ungrounded Fault - Symmetrical Components

09/20/2016 12:06 AM

Thank you. I agree with you about the difference between politics and science, of course. However, in the actual conditions when no "scientific" data is provided one could only to express his opinions.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#4

Re: Three Phase Ungrounded Fault - Symmetrical Components

09/19/2016 10:58 AM

That is the disadvantage copying from my Excel Workbook:

See[for information]:

GE Application Information Short-Circuit Current Calculations

http://apps.geindustrial.com/publibrary/checkout/GET-3550F?TNR=White%20Papers|GET-3550F|generic

Post Glover NEUTRAL GROUNDING RESISTORS TECHNICAL

http://www.postglover.com/download/neutral-grounding-resistors-technical-information/

I think it could be better

__________________
Julius
Register to Reply
Register to Reply 6 comments