VFD Motors...

10/31/2016 12:21 AM

What I understand from my experience so far is that the VFD driven motor are different from standard motors by 2 ways. 1) They undergo VPI(vacuum pressure impregnation 2)They will have insulated bearing in NDE side.

Is there any other difference between standard & VFD motor such as size?.

Kindly share your knowledge.

Thanks.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#2

Re: VFD motors...

10/31/2016 9:51 AM

In addition to that, you need to be aware that a motor connected to a VFD has the potential to emit more heat, and therefore operate at a higher temperature. In zone 1 and zone 2 hazardous areas, this characteristic has implications on Eex d systems in that the motor and VSD need to be selected as a combination as opposed to individual items. In most cases the implication is to go up one size on the motor to keep its casing within the T rating. In all cases, seek advice from both the VFD's and the motor's manufacturers.

__________________
Good moaning!
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: VFD motors...

10/31/2016 10:31 AM

There is no enforceable 3rd party standard defining a "VFD motor" or "Inverter Duty" motor, so it still boils down to "let the buyer beware". There are voluntary design standards, but they are performance based, meaning how a manufacturer gets there is their own business. So some may use vacuum impregnating, others don't. Some include isolating bearings (both ends by the way), others include shaft grounding, some ignore the bearings altogether. Some use 1600V winding insulation, others use 2000V, some use 2200V. Some use fish paper in the slots, others don't. Some do nothing more than de-rate one size and call it good!

In general, you get what you pay for. The advice I always give is to read the specifications on what you are buying and study up to understand what they mean to you.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: VFD Motors...

10/31/2016 5:09 PM

An example of a manufacturers' standard would be NEMA MG-1, which may give you some guidance.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: VFD Motors...

10/31/2016 10:42 PM

Dear Mr. Giri,

The following are also differenc for VFD motors.

1. A seperate air blower with filter to cool the motor - irrespective of speed which may vary from 10% to 90% during operations. The normal motor for small or medium size - which run near to synchronous speed will have a shaft mounted fan.

2. Bearing Insulation is also followed which is economical as the Insulated Bearing is costly/expensive.

3. The earthing - flat AREA should be 2.5 times more than the conventional motor earth flat area of same capacity motor.

4. The earthing should be dedicated one - that is independent and other motr/equipment earthing should not be clubbed.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#6

Re: VFD Motors...

11/01/2016 8:22 AM

In practice, (my continuous experience in industrial equipment for past 25 years now), any energy efficient motor will work fine down to a 10 to 1 turn down, 6 Hertz, and pretty much any rag-tag collection of NEMA Design B and metric integral hp motors will work down to a 6 to 1 turn down, with normal expected life.

There will be outliers, where the mechanical load is consistently equal to the motor rating, it will get hot at the lower speeds, for constant torque loads. In practice, for ratings at least through 150hp, it is unnecessary to purchase special designs for a motor, unless it gives you peace of mind. (modern IGBT PWM drives are very kind to motors these days)

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Crabtree (1); dhayanandhan (1); JRaef (1); lyn (1); rwilliams (1); Tornado (1)

Previous in Forum: Selection of Transformer and Cable Rating for A/C Units   Next in Forum: KV Meter

Advertisement