Induction Motor Taking Full Load Current at No Load in Delta Connection

11/05/2016 10:41 AM

We have a 45 KW sq. cage motor having FLC 77 A, voltage 380-415V delta. During running on no load it is taking current of approximately 60 A. Motor connection is in delta . When running in star it is taking 10A.
We have checked the delta connection & polarity of winding is also correct.

please suggest any remedy if you have.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: induction motor taking full load current at no load in delta connection

11/05/2016 11:06 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: induction motor taking full load current at no load in delta connection

11/05/2016 12:47 PM

Why do you have it connected in delta? Is that what the motor information tells you to do? Because that would be unusual, most 400V class motors are designed to use the Star winding connection. Delta would be for a 230V supply, so if you connected in delta you are over saturating the motor windings.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4
In reply to #2

Re: induction motor taking full load current at no load in delta connection

11/06/2016 8:04 AM

He said 380-415V delta in original post

__________________
Give masochists a fair crack of the whip
Register to Reply
Member

Join Date: May 2009
Posts: 9
#12
In reply to #2

Re: induction motor taking full load current at no load in delta connection

11/09/2016 6:46 AM

Motor name plate reads 380-415V delta connection

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#13
In reply to #12

Re: induction motor taking full load current at no load in delta connection

11/09/2016 7:23 AM

Can you answer my #5? Is it OK driving the load? That's the acid test!

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: induction motor taking full load current at no load in delta connection

11/05/2016 11:02 PM

In most electrical motor (depend upon each country) as in my counrty, are offen design to run in delta connection at 415Vac/50hz. In delta connection, during running in NO Load condition, the running amp are usually lower than the FLC about 35% - 40% lower. This is condition is also depend upon the design of the electrical motor. By connection the Delta connection electrical motor in to the Star connection, the impendance of the motor winding will increase. The electrical motor still can be run but the motor torque are very much lower. Running the Delta connection electrical motor in to the Star connection with NO Load condition at 10 A is something not correct.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#5

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/06/2016 8:14 AM

Does the motor do its job OK, under load? If so there maybe isn't a problem.

On no load the power factor is much lower, so although the amps seem high the power drawn from supply is well below motor rating

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/06/2016 9:02 AM

Tell me what the motor manufacturer said during the phone calls, please?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/06/2016 3:45 PM

No-load 60 amp seems too much. Star 10 amp with constant impedance suggests about 30 amp delta connected, no-load, which is reasonable.

Are all phase currents the same?

Is the motor vibrating a lot or noisy on Delta?

Is it turning in the standard direction? Standard is clockwise looking on drive end, when the supply sequence is ABC at the motor terminals

Are you sure winding connections are correct - do you have the maker's connection diagram?

Register to Reply
Member

Join Date: May 2009
Posts: 9
#11
In reply to #7

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/09/2016 6:44 AM

Phase currents are Balanced.
There is no vibration
Direction is clockwise in ABC phase sequence
We have checked with makers connection diagram, Also tested the polarity of windings.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#14
In reply to #11

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/09/2016 1:22 PM

Thanks for reply. This is very odd...............

What is the motor speed nameplate value and measured speed at frequency? If available..

Register to Reply
Member

Join Date: May 2009
Posts: 9
#15
In reply to #14

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/10/2016 10:38 PM

This is a 4 pole 50 HZ motor & measured speed is 1492 RPM

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#18
In reply to #15

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/11/2016 8:36 AM

But what are the figures when it's driving the load?

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#20
In reply to #15

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/11/2016 4:34 PM

Thanks for further information. 1500 rev/min would mean more amps no-load compared to 3000 rev/min, roughly 40 amp. There is a tolerance, maybe +/- 20% on any winding impedances - that makes 48 amp. These figures for 45 kW Crompton motor at 400V. In proportion at 415V +10% = 456.5 V is 55 amp - plus there will be increased saturation.

To 55 amp can be added the probable meter error - maybe 5% or more if 60 amp is low compared to full scale. Maybe you have a CT error to add??

What meter ranges full-scale are you using, measuring 10 amp and 60 amp??

Considering the low current star connected there does not seem to be any mechanical fault.

What is actual supply voltage was there when you got 60 amp??

I think the suggestion posted that you should try the motor on-load is reasonable.

If you wish to be careful, I suggest backing-up the 60 amp reading with a different ammeter or a power factor or watts measurement.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#21
In reply to #20

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/12/2016 4:35 AM

Why do you say no-load amps would be higher on 4-pole than 2-pole? I don't get that, please explain.

My gut feeling is 1492 rpm no-load is a tad low, but I suppose could be right. My motor data says full load rpm 1475 - 1480 rpm (different makes). As you suggest, the actual supply voltage on the tests (presumably in range 380 - 415) would be of interest, as it affects slightly the rpm.

I'm not holding my breath for a reply about on-load operation ��

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#22
In reply to #15

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/12/2016 4:48 AM

Further to post #20 and to be sure this is not an unusual situation.....

Are you at a high altitude above sea level? This would need derating e.g. your 45 kW motor - normally a 225 frame could be a 55 kW motor frame 250. But no-load current would increase for larger motor. The 45 kW motor data I used was frame 225

For a normal horizontal, foot mounted, motor the size "225" is the vertical distance from shaft centre to bottom of feet in millimetres.

What does the rating plate of the motor have on it?

67model

Register to Reply
Member

Join Date: May 2009
Posts: 9
#23
In reply to #22

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/12/2016 6:12 AM

Motor is of 225 Frame.

At 30 KW input loading motor is taking 80 A which is not correct.

The measured current have no error. We have cross checked it with Clamp meter.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#24
In reply to #23

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/12/2016 5:57 PM

You have not told us the motor terminal voltage when you tested it - as noted in post #20, this has significant effect on no-load current.

Do you mean by post #23 that you have measured kW input?

If so, proper comparison with current - VA cannot be calculated without motor terminal voltage.

Since you gave 60 amp no-load current previously, may we take it 30 kW, 80 amps, ?? volts is with motor driving its intended mechanical shaft load?

Since the phase currents are the same, I am wondering if there is some odd error, like a rewind with too few turns.

Register to Reply
2
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#8

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/07/2016 4:11 AM

Check current in all three phases. may be one phase missing after going in to delta.

__________________
Subramanyam
Register to Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/07/2016 3:08 PM

I really have nothing to add, others here have not already pointed out. You have not done all your homework on this one yet. Check EVERYTHING, take nothing for granted, or nothing will turn around and bite you in the posterior.

Also check the motor bearings and couplings to make sure alignment is correct.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/08/2016 11:10 AM

Usually motors 4 kW and larger 380 – 415 Volt 50 Hz are DELTA connected.

If the no-load currents in all three phases are equal it could be a wrong connection-that means it is for star winding connection made nevertheless the rating plate says other.

Since the gap is very small a small difference could change the no-load current.

It could be an air gap problem-as ball bearing damaged. In this case the currents will be unbalanced.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#16

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/11/2016 5:50 AM

At a second glance the airgap is not the source of the problem.

What is confusing is the huge fraction between delta no-load current and star.

It has to be 2 about and here is 6. I think something wrong with the measurement has to be.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#17

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/11/2016 6:39 AM

huge fraction =huge ration [I meant]

__________________
Julius
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#19
In reply to #17

Re: Induction Motor Taking Full Load Current at No Load in Delta Connection

11/11/2016 8:55 AM

If you overfeed a cat for a long time, do not be surprised when it exhibits a paunch.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 24 comments