Feeder Calculation Help

11/16/2016 6:04 AM

hi all,

i am working on protection calculations of a feeder, having following details;

1. total power 7 MW

2. System Voltage 13.8 KV

3. CT Ratio 600/1

4. Feeder Max current 366 Amp.

i have Calculated the following to feed to IDMT relay,

1. Ip> 70%

2. Ip TMS: (Need Help)

3. Ip curve: Normal Inverse

4. Ip>> 200% ( need recommendation)

5. Ip>> Delay: need help

6. IE> 10 % ( need recommendation)

7. IE curve: Normal inverse

8. IE>> 150%( need recommendation)

9. IE>> Delay (need help)

10. 3 Phase O.L. 105%

11. 3 Phase O.L Delay. 600 Sec ( need recommendation)

please guide if i am wrong on calculated values and advise for the help i have requested.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Feeder Calculation Help

11/16/2016 6:21 PM

No! No! No! No! No!

You are not capable of this work!

You are also irresponsible!

You are not qualified! You will surely fail and in the process may even kill people!

Quit! Go away!

HIRE A PROFESSIONAL ELECTRICIAN/TECH/ENGINEER!

This forum does not give advice to the unknowing so that they can injure others or burn buildings.

Reply Score 2 for Off Topic
Associate

Join Date: Oct 2012
Posts: 44
#3
In reply to #1

Re: Feeder Calculation Help

11/17/2016 2:54 AM

if you read my question carefully, i have done calculations, what i have asked is just verification.

what is this forum then for?

i have done some calculations, some are missing,

this behavior of yours shows you are also not capable about this calculation, so why bothering to reply?

your previous posts that i have gone through depicts your replies based totally on discrimination.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #3

Re: Feeder Calculation Help

11/17/2016 5:49 PM

OK, that's fine with me.

I went through your previous posts and discovered that your posts all ask for help with rudimentary concepts of electricity. So, neither you, nor I, can do the calculations. I don't need to, you do.

Did you ever get that free copy of NFPA 70 2014 Electrical Standards you needed?

That might help you discover some of the questions you have previously asked the forum.

Good luck.

Reply Score 1 for Good Answer
Associate

Join Date: Oct 2012
Posts: 44
#7
In reply to #6

Re: Feeder Calculation Help

11/18/2016 12:46 AM

yes,

i bought it from local market.

i am just confused regarding setting of tripping time, what i know is that the tripping times are adjusted according to short circuit (KA) withstand time of cable and for the coordination of upstream and down stream circuit breakers. anything else to consider?

thanks for your humble reply by the way.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8
In reply to #7

Re: Feeder Calculation Help

11/18/2016 7:49 AM
Reply Score 1 for Good Answer
Associate

Join Date: Oct 2012
Posts: 44
#5
In reply to #1

Re: Feeder Calculation Help

11/17/2016 10:23 AM

nice drawing by the way....

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Feeder Calculation Help

11/16/2016 7:13 PM

Get some electrical consultants to do the calculation before you kill someone with your calculation. if you don't know how to do the calculation then don't do it.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Associate

Join Date: Oct 2012
Posts: 44
#4
In reply to #2

Re: Feeder Calculation Help

11/17/2016 2:56 AM

you were born qualified??????

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #4

Re: Feeder Calculation Help

11/19/2016 6:30 AM

The Anonymouse roars.

Seriously, this 13.8 kV system is fed from a higher voltage system by a transformer. Supposing that voltage at HV of transfo is unchanged by any short on 13.8 kV side, I guess you have worked out the fault currents.

Any setting curves you decide need to be inside the operating curves of the transformer protection relays (or upstream protection if there are no relays for transfo) by a margin to cover relay and CT errors i.e. the tolerance bands of upstream and feeder protection must not overlap on the time versus current graph.

Your setting curves must also be inside the withstand curve of the feeder, so you need the feeder overcurrent withstand capacity. You did not define insulated cable type or open wire feeder. Saruman (in the "Lord of the Rings" used a "crystal ball" - and you know what it did for him!

You have not given us a system diagram with impedances, CT numbers, locations etc.

The meaning of Ip and Ie is not clear, maybe phase and earth fault - here the diagrams help.

You cannot expect folk to verify settings on an unknown system.

Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); lyn (3); mrmuneb (4); Simon Wan (1)

Previous in Forum: 1/3 in Symmetrical Components   Next in Forum: Select One of Different Sized Matrices Simulink (PLC Compatible)

Advertisement