Under Voltage Protection In Parallel Connected Switchgear

12/05/2016 1:47 AM

Dear all,

There are 2 incomers fed from 2 different remote substations to a 11kv panel, the switchboard consists of 2incomer and a bus-coupler, all 3 breakers are normally closed hence both incomers are parallel connected. Is it possible to provide an under voltage protection trip during under voltage in any one of the incomers since both are connected in parallel? the requirement is in case of an undervoltage in any one of the incomer, the respective breaker should trip.

thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster #1
#1

Re: Under voltage protection in parallel connected switchgear

12/05/2016 4:51 AM
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#2
In reply to #1

Re: Under voltage protection in parallel connected switchgear

12/05/2016 5:24 AM

The question is how to sense under voltage by an under voltage relay individually when both incomers are connected, because each under voltage relay will read the voltage if there is any one feeder is live, hence there will be a back feed during power outage in any one feeder. the undervoltage will act only when both incomer is in under voltage

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Under voltage protection in parallel connected switchgear

12/05/2016 5:33 AM

Er, so what's the problem?

If there is a two-out-of-three interlock between the bus coupler and the two incoming feeder isolators, as is normal on many twin-fed panels, a back-feed cannot occur.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#4
In reply to #3

Re: Under voltage protection in parallel connected switchgear

12/05/2016 8:24 AM

No, 2 incomers and 1 buscoupler in the panel is normally closed condition, ie it will act as a single system. the thing is the undervoltage relays provided in each incomer, but the relays will not loose its supply since it is connected parallel. the only option i think the reverse power relay, but its costly. please suggest if any idea.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Under voltage protection in parallel connected switchgear

12/05/2016 8:34 AM

<...please suggest if any idea...>

Er, how about a two-out-of-three interlock between the bus coupler and the two incoming feeder isolators?

<...reverse power relay, but its costly...>

Compare it to the cost of not doing it. Which one gives the better whole-life solution (rhetorical question - NNTR)?

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6

Re: Under Voltage Protection In Parallel Connected Switchgear

12/05/2016 11:51 AM

The simple answer is NO, you cannot do it with just undervoltage relays if you are operating with a dual source, closed tie configuration. The other source that is not sagging will try to maintain the voltage level. What will happen in that case is that current will flow from the other source to the sagging source to try to raise the voltage.

You will need to look at directional current or reverse power relays, or something like that. Hire yourself a good, competent consultant who deals with this, and get the job done right.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 3)
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#7
In reply to #6

Re: Under Voltage Protection In Parallel Connected Switchgear

12/06/2016 12:27 AM

agree, thanks

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#9
In reply to #7

Re: Under Voltage Protection In Parallel Connected Switchgear

12/08/2016 8:19 AM

Definitely directional relays.

Regarding the cost - look at the costs of not providing protection.

If you need both feeders, you have to decide which loads to cut - and how - when one feeder goes low.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#8
In reply to #6

Re: Under Voltage Protection In Parallel Connected Switchgear

12/06/2016 3:23 PM

A sudden unusual flow of reactive power out might be another indicator of an impending problem, where you could isolate based on that. These 3 solutions depend on your history and who owns the power passing through, if any.

Your utility will likely have some guidance on how to disconnect/sectionalize in an event.

Register to Reply
Register to Reply 9 comments