instrument for potentio meters

08/11/2007 1:18 AM

I want to have a correlation (instrument) between linear (5ohms) and rotary (5ohms) potentio meters; Rotary is a 0-320 deg turn and linear is 0-100mm stroke

The question is when I set a rotary at 100 deg, that should be the cut off point for the linear scale and it should send signal to solenoid valve. Basically this application is for hydraulic cylinder to control up and down movement of crimping machine.

Thanking u

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#1

Re: instrument for potentio meters

08/11/2007 5:13 AM

Hello guest,

Sounds interesting but I'm not getting what you mean by "cut-off point for the linear scale".

If I may hazard a guess, you want to control the position of the hydraulic cylinder using the rotary potentiometer. The linear potentiometer is mounted on the cylinder which gives you feedback of the actual position of the cylinder. Is this correct?

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#2
In reply to #1

Re: instrument for potentio meters

08/11/2007 7:02 AM

I'll bet a pound to a penny they are not 5 ohm.... 5k, 50k ? maybe.

__________________
health warning: These posts may contain traces of nut.
Reply Score 1 for Good Answer
Anonymous Poster
#7
In reply to #1

Re: instrument for potentio meters

08/13/2007 7:24 AM

Thanking U Sir,

Exactly, when set point (Equally divided say 1-10position,and rotary is at 3 set position) of rotary pot reaches of linear pot 3set point. It should send the signal to solenoid valve.

Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#3

Re: instrument for potentio meters

08/12/2007 10:52 AM

If I understand correctly, you want to use a rotary pot to control where the hydraulic cylinder stops, and the linear pot to determine where the cylinder is located. You simply need a comparator chip like the LM311 (or 111 or 211 depending or precision and reliability required). You connect the slider of the rotary pot to one input and the slider of the linear pot to the other input. The output flips high or low depending on which pot is at a higher fraction of its scale. Better use a multi-turn rotary pot to get the required precision.

If you don't want to build a circuit, you can use two analog in puts to a PLC etc...

I'm not at all sure that a linear pot has sufficient precision to continue stopping the crimping action at the correct position over the long term - depends on the linkages between the cylinder and the actual crimping mechanism.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Anonymous Poster
#5
In reply to #3

Re: instrument for potentio meters

08/13/2007 12:49 AM

Thank u sir,

i have connected potention meters by PLC ALLEN-Bradly with PCB and transformer to convert ohms into Volts. but here the problem is converting the Ohms into Volts had became a big circuit. can i have simple one....

Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#6
In reply to #5

Re: instrument for potentio meters

08/13/2007 4:43 AM

Why build?

You can buy resistance-to-current converters for no hassles at all. All you need to do is connect the potentiometers to the resistance inputs and then connect the 4-20mA output to the analog input of the PLC. After connecting power to your converter, your programming does the rest.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#9
In reply to #5

Re: instrument for potentio meters

08/13/2007 11:16 AM

First, let me say that Vulcan's solution is more robust than what I am about to say, but the following is probably cheaper:

If you don't need isolation of the sensors from the PLC, and assuming that your potentiometers (single word) are 5k Ohm, not 5 Ohm, you simply connect a 7 kOhm resistor, or a 10 kOhm trim pot adjusted to 7 kOhm, in series with each of your 5k pots, and connect those to the 24VDC supply. This drops the maximum voltage of the two pots to 10VDC, so the sliders can be directly connected to the 0-10V analog inputs of the PLC.

Of course it would be preferable to use a voltage regulator to prevent variations in the 24V supply from reaching the pots. In this case the series resistors would have a lower value, or be eliminated entirely if the regulator output is 10V.

If you need a circuit I could draw one...

Dick

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#11
In reply to #9

Re: instrument for potentio meters

08/13/2007 8:46 PM

Oh, my myopia!

Dick, thanks. I didn't see the 0-10V requirement. Well, I read it but it didn't register.

Your solution is fine and takes into the account the problem of distance between the potentiometer and the PLC input. The problem with using voltage inputs is that as the distance to the analog input increases, the voltage drop may seriously affect the level that reaches the input module. Having the 7k ohm trim-pot allows him to compensate for the drop.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#12
In reply to #11

Re: instrument for potentio meters

08/14/2007 12:53 AM

Hi Vulcan!

Actually the post says "(Equally divided say 1-10position". It does NOT say 0-10V. Its just that that's what I've used on all my machines, because my motion controllers have 0-10V inputs built in, and my control pots are in the same metal enclosure as the controller, so the distances are short and everything is shielded.

Dick

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#13
In reply to #12

Re: instrument for potentio meters

08/14/2007 4:50 AM

Yes, but in post #5 he mentioned that he was converting resistance to voltage.

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#14
In reply to #13

Re: instrument for potentio meters

08/14/2007 10:15 AM

Right you are!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Reply
Power-User

Join Date: Jul 2007
Location: Orlando
Posts: 242
Good Answers: 3
#4

Re: instrument for potentio meters

08/12/2007 11:09 AM

It sounds like this is probably for an industrial application. If so, then perhaps a digital encoder along with a uP interface (can be simple) // or even more simply a D/A interface and a comparator (LM311 suggested earlier) to establish the desired end points. This would be much more reliable.

Potentiometers can with time suffer from being erratic and resulting in failure for the task.

Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#8

Re: instrument for potentio meters

08/13/2007 8:40 AM

Law, Law, Law. Ohm's Law, that is. Use a different voltage on the potentiometers. If you don't get the concept, find someone who does.

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Power-User

Join Date: Apr 2007
Location: Kingman, AZ
Posts: 110
Good Answers: 3
#10

Re: instrument for potentio meters

08/13/2007 11:24 AM

This sounds like a lot of effort without any real advantage gained. Whats the point in measuring displacement when performing a crimping operation? Unless your also measuring the force applied, displacement gives you no added value. The two combined can give you the most accurate crimp for any individual part by zeroing out variations in hardness & stackups(dimensions), but without force being measured, it is much simplier just to make a hard stop with a down position switch & focus on keeping the stroke length consistant(If operated manually).

I say this as someone who has spent many years delevoping & improving crimping stations used in crimping pressure sensor housings while also setting the compression of the main seal rings within a tolerance of 2-3thousandths.

Reply
Reply to Forum Thread 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Bill (1); Bill ML (1); dkwarner (4); Sonave Sunsets (1); user-deleted-1105 (1); Vulcan (4)

Previous in Forum: sharing mutual knowlwdge about electronic repairs   Next in Forum: Optics and Light

Advertisement