We had Short Circuit Generator for Short circuit testing of Power system equipment. It is initially running as a motor up to reaching the 3000rpm, after reaching the 3000rpm we cut off the supply and it can be used as a generator. After completion of the test again it was reconnected to the power supply and speed is decreasing form above 2000rpm to 0rpm during this period motor is in the regenerative braking mode. During this mode, it is pumping power to the grid. Now present problem is during regenerative braking mode rotor earth fault is coming, but it was not there in motor mode. What is the reason?. Please explain
Re: Rotor Earth fault in Synchronous Motor during regenerative braking mode
01/06/2017 5:11 AM
Timing or synchronous phasing perhaps. Are you sure you have the right circuit?
01/06/2017 5:23 AM
The possibility of winding over-voltage and conductor insulation breakdown because of it during regenerative breaking needs to be investigated.
01/06/2017 8:05 AM
When you checked everything out before running the motor was there an earth fault then? You did check everything out first, yes?
Re: Rotor Earth Fault in Synchronous Motor During Regenerative Braking Mode
01/06/2017 11:12 AM
Shifting from power on rotor to off and generation causes a shift of force in the opposite direction, this may be changing the attitude of the shaft in such a way that it is thrusting and making contact with a ground source....I would check for any movement during shift...the bearings may be worn...
01/07/2017 4:41 AM
Is the "Grid" AC or DC?
If AC, I really don't understand how this could work, using the extremely limited information that you have supplied!!!
For the best help from CR4, you always need to give FULL information!! Err on the side of too much, rather than too little, is a great tip!!
Good Answers: 42
01/07/2017 5:41 AM
In my opinion, the excitation[rotor winding] short-circuited behaves as an induction motor rotor windings.
At start from s=1[rpm=0] frequency 50 Hz and the induced voltage [emf] is approximate E*s=E. At close to synchronous speed s=~0 and emf=0.
In braking operation case the slip is more than 1.For -2000 rpm s=133.33%.Then the induced voltage will be 1.33 times the induced start voltage. In this case a weak insulation could be entirely damaged.
Julius
Good Answers: 445
01/07/2017 7:40 PM
There are many details missing before any diagnosis is possible; things like the rating of the machine, synchronous or induction, AC or DC, how it is brought up to speed, is there a flywheel, if synchronous how is the field controlled, is it randomly reconnected to the grid, why is the speed falling as it reconnected to the grid, how does it pump power to the grid if its speed is below synchronous speed, etc., etc. If it's DC then some of these questions are irrelevant.