High Voltage Isolators

01/17/2017 6:23 AM

Generally High voltage (say 220KV ) switch yards have off load isolators on incoming/supply side. what is the need for it in the switch yard or why even it is used? As for as i know there will be a high voltage circuit breaker which provides the job of isolation once tripped.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: High voltage isolators

01/17/2017 6:53 AM

Would these be the ones making connections between the isolated high voltage conductors and electrical earth? If so, the answer is "for the safety of those working on those particular conductors".

Get it wrong with HV, and it's half a day out with the Undertaker, assuming there is enough left to bury or cremate...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: High voltage isolators

01/17/2017 7:46 AM

Cremation is automatic at 220 kV.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
7
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: High Voltage Isolators

01/17/2017 8:16 AM

Most switching sequence instructions require that there be a "visible open" in the circuit for personnel safety reasons. The utility that I do work for has this in its procedures. Thus, when we want to work on a line circuit breaker, we require the breaker to be opened, then the line switch to be opened so that we can visibly see the breaker is disconnected from the line (since you cannot see the open contacts within the breaker directly). Similarly on the bus side.

Also, since the line may need to remain in service while the breaker is being maintained, repaired, tested (whatever) due to other taps off it ahead of this connection, the switch allows the breaker to be out of service while the line is still energized.

This is not just a function of the higher transmission voltages - it is also often, if not usually, done at lower voltages as well.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 7)
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#6
In reply to #3

Re: High Voltage Isolators

01/18/2017 7:38 AM

" This is not just a function of the higher transmission voltages - it is also often, if not done at lower voltages as well ".

Very true. Good answer.

A common example is the typical home circuit breaker panel, a single or multiple branch circuits can be placed in the open or off position, while the main is in the closed or on position.

A switch yard is just a larger circuit breaker panel.

You don't really think they are gonna shut the juice off at the power plant just because someone down stream wants to work on the wiring.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: High Voltage Isolators

01/17/2017 2:38 PM

Visual break.

Ask someone who actually works in a switch yard if they would trust an indicator on a circuit breaker as their only means of isolation. Look into the appropriate codes and standards for switch yards which state that visual break is required and you cannot rely on an indicator alone for proving isolation.

Dear God your questions and lack of basic knowledge regarding high voltage transmission and distribution concern me, especially since you previous questions indicate you actually work in the field!

In your apparent position of responsibility you should not be asking these sort of questions of an online forum to cover up your apparent lack of knowledge in a field you are being paid to work in with very little margin for error. It is very unethical.

How's that 25MW 132kV grid-connected coal power station you were asking for help with last year going.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#8
In reply to #4

Re: High Voltage Isolators

01/20/2017 3:46 AM

Haha.That 25MW plant is under evaluation

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9
In reply to #8

Re: High Voltage Isolators

01/22/2017 1:52 PM

Yes, on CR4 it appears, based on your latest posted questions.

We are here to discuss matters of Engineering and such, not act as your free consultancy service or help you do your job, which I get a sense that you are doing.

I feel in my opinion you have crossed an ethical line and are taking advantage and abusing the point of this forum to make up for your Engineering short comings in a job position you are getting paid for.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: High Voltage Isolators

01/17/2017 3:06 PM

Because the safety codes demand it...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Off Topic
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#7

Re: High Voltage Isolators

01/18/2017 8:20 AM

There is more than one good reason to have line isolators on the busbar sections.

1. It disconnects the live line from the switchyard equipment on that circuit.

2. It provides a visual 'open isolation point' to anyone working on a circuit(s)

3. It allows for a earthing point to ensure the non line side equipment is safe to work on from backfeeds or feeds.

4. It allows for secure lockouts of that circuit, that it cannot be energised by an unothorisied person(s).

5. Anyone with experience in this field will know that CB's do not always operate and may not be in a safely maintained condition to operate properly, and be fully disconnected when tripped. So an isolator is a back and you will know if the CB did not trip fully, as you will draw and arc on the isolator when one opens it.

It is also a handy back up safety switch.

Register to Reply
Register to Reply 9 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: