Anonymous Poster

Motor Star Delta Starter

08/13/2007 5:35 AM

there r problem in motor star delta strarter . starter not get change over from star to delta.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: question

08/13/2007 6:26 AM

Let's assume that post to contain the question word "why?". To answer such a question requires more questions to be asked.

  • Is the star timer expiring correctly and closing the delta solenoid?
  • Is there a loose wire in the control circuit? Or a blown fuse?
  • Is the mechanical interlock between the star and the delta contactors working correctly?
  • Is the cabling to the motor corrected correctly at both ends?
  • Is the MCC cubicle slide-out chassis correctly connected to the backplane?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Commentator

Join Date: Aug 2007
Location: INDIA
Posts: 58
#2

Re: Motor Star Delta Starter

08/16/2007 7:22 PM

Sir

Actually We are maked interlocking Bent star-delta contactor so interlocking fail or u r timer /timer contact fail

which contactor, timer u r use ?

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Motor Star Delta Starter

08/21/2007 3:49 AM

....Bent....interlocking fail....

Un-jamming the mechanical interlock will solve the problem. Do not remove it, as its purpose is to prevent, absolutely, the star and delta contactors making contact at the same time; were they to do so then the supply fuses will be presented with a short-circuit, and will rupture, protecting the cabling.

...timer contact fail...

Replace the timer like-for-like, with a spare. Make sure the delay time setting is identical to the faulty one.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply