there r problem in motor star delta strarter . starter not get change over from star to delta.
Re: question
08/13/2007 6:26 AM
Let's assume that post to contain the question word "why?". To answer such a question requires more questions to be asked.
  • Is the star timer expiring correctly and closing the delta solenoid?
  • Is there a loose wire in the control circuit? Or a blown fuse?
  • Is the mechanical interlock between the star and the delta contactors working correctly?
  • Is the cabling to the motor corrected correctly at both ends?
  • Is the MCC cubicle slide-out chassis correctly connected to the backplane?
Re: Motor Star Delta Starter
08/16/2007 7:22 PM
Sir
Actually We are maked interlocking Bent star-delta contactor so interlocking fail or u r timer /timer contact fail
which contactor, timer u r use ?
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
08/21/2007 3:49 AM
....Bent....interlocking fail....
Un-jamming the mechanical interlock will solve the problem. Do not remove it, as its purpose is to prevent, absolutely, the star and delta contactors making contact at the same time; were they to do so then the supply fuses will be presented with a short-circuit, and will rupture, protecting the cabling.
...timer contact fail...
Replace the timer like-for-like, with a spare. Make sure the delay time setting is identical to the faulty one.