Anonymous Poster

Selection of CT, PT?

08/14/2007 5:11 AM

how to select Current tranaformer and potential transformer for 11kv/415v , 200kva capacity transformer. How to calculate the CT Ratio at 11kv side and 415v side and same for PT pl tell me how to select CT, PT for various Voltage like 415v, 11kv

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#1

Re: Selection of CT, PT?

08/14/2007 1:09 PM

Is it for metering or protection ?

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Selection of CT, PT?

08/14/2007 1:20 PM

Ummmm... "ratio" means you divide one side by the other. So if you have an 11kV line, and you want to transform that down to a safe level to work with in your metering by using a PT, say, 110V, then you divide the primary (11,000) by the desired secondary (110) and come up with a 100:1 ratio. But fiorst you have to decide what your secondary potential needs to be. Here in the US we use 120V for secondaries of PTs, but with you having 11kV I know you are not in the US.

The same basic principal hold true for CTs as well, only with current. The one difference is however, you want your normal full load operating current to fall as close to the middle of a metering range as possible. That's because at the top end of a CTs operating ratio, the accuracy drops off rapidly, therefore you want to be operating in the 'sweet spot: of the middle of the range. So for instance if you are metering the primary side of that transformer, the full load current will be 200,000/11,000= 18A So you would want your CT ratio to be roughly for double that so that at full load, the 18A is in the middle of the range. So a 36:1 ratio would be right, except that CTs are usually based on a 5A secondary, so you would express it as a 180:5 ratio. Now again, CTs usually come in standard sizes, so the closest standard size will be 150:5 or 200:5, I would go with the 200:5 ratio.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#3
In reply to #2

Re: Selection of CT, PT?

08/15/2007 8:37 AM

Additionally, you want to make sure your CT is designed for 11 kV or higher. Some CT's, even though the hole will fit over the wire, do not have the insulation resistance to handle high voltages (or higher medium voltages).

__________________
We have met the enemy and he is us . . . Walt Kelly
Reply
Anonymous Poster
#5
In reply to #2

Re: Selection of CT, PT?

03/01/2009 5:46 AM

dear please give me the available ratio of CT in market

Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#6
In reply to #2

Re: Selection of CT, PT?

10/28/2011 6:04 AM

Dear Sir,

In India, generally PT ratio is specified by 11000/sqrt.3 : 110/sqrt.3, could you please through some light on why primary and secondary voltage level are divided by sqrt. 3?

are we making both primary and secondary winding of PT for Phase-Neutral measurement, if so, how we are using same PT with help of 7 position selector switch to measure P-P and P-N voltage?

__________________
manirul
Reply
Participant

Join Date: Aug 2007
Posts: 2
#4

Re: Selection of CT, PT?

08/27/2007 12:44 PM

the ct shall have a ratio of 10/5 A.its very simple divide the the capacity/demand by sq.root of 3 and system voltage.

to select a ct u need more information:-

1)class of accuracy

2)type of meter

3)burden to be connected to the ct.

4)fault level etc.,

Reply