PT Connection

04/26/2017 2:18 PM

Consider PT connection below for a 400/110V ,V-V bus PT. in Fig.02, apparently the common wire of primary seems to be connected to the Bus through fuse disconnector with the other two phases just left open. it is beyond understanding. how can the PT function with two phases not even connected to Bus. can anyone explain please.

Cheers.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#1

Re: PT Connection

04/26/2017 6:50 PM

Clearly that's not a PT but an isolation transformer.

Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#2

Re: PT Connection

04/26/2017 7:14 PM

An AC/DC "Acca-Dacca" isolation transformer I might add. You can tell by carefully observing how it dresses on Saturday nights and noting if it attempts to woo other transformers of the same AND opposite polarity. When they all leave the party together you know something's up.

Register to Reply Off Topic (Score 6)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: PT Connection

04/27/2017 1:34 AM

A PT has a high impedance and the self capacity between windings and the tank and the parallel insulation resistance is lower. So since 400 V system is usually grounded the circuit is closed through the grounding.

__________________
Julius
Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#4
In reply to #3

Re: PT Connection

04/27/2017 8:17 AM

the winding is on phase A and C ,both of which are not connected at 400V(primary) side. so how is this a PT? in ur scheme , the PT primary is just bolted short circuit of the bus to ground.

Register to Reply
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: PT Connection

04/27/2017 8:46 AM

You are confusing the single-line diagram with the AC elementary or 3-line diagram. This is an "Open Delta" PT configuration, where 2 single-phase PTs are connected in a "V." See the diagram below. In the single-line, it looks like one fuse, because all 3 phases are represented by one line. However, in the 3-line, you will find that there are 3 fuses, one on each of the 3 phases (not shown in the picture I happened to have), but all 3 phases are connected to the main supply phases.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#6

Re: PT Connection

04/27/2017 9:44 AM

Coolyaar, your post is Reason #248 why you should go into horticulture or some other safe occupation that does not involve lethal quantities of energy. You're a danger to yourself and others, and your posts have shown this beyond all reasonable doubt.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#7
In reply to #6

Re: PT Connection

04/27/2017 2:14 PM

Yep, electricity is a field with no second chances, and guess work is fatal work, singular in its frequency of occurrence. In common terms - - if your concern for safety ceases, you become an endangered species.

If you are too broke to pay attention, you can't afford to work around electricity.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#8

Re: PT Connection

04/28/2017 4:20 AM

It seems to me I did not understand the o.p. I thought fig.no.2 as a part of the schematic when it was simply a wrong interpretation. I was sure it is about a derangement.

According to one line diagram-I hope it is actually- the PT is V-V-in Europe or Open_delta in USA, indeed.

I was myself a young engineer specialist in electrical machines and not in electric power and transmission domain. It is not the same profession. You have to collect another theory and experience in this field. This forum cannot help you to overcome this gap in your knowledge.

__________________
Julius
Register to Reply
Register to Reply 8 comments