Grounding for NGR of Transformer

05/28/2017 7:41 PM

Dear Sir and Friends, good morning

I wanna ask about grounding for NGR.

Is there any standard that stated for grounding of NGR must be directly connect with ground rod?

What if grounding of NGR just connected to grounding grid system? As we know that the philosophy of grounding, wether connect to ground rod or connect to grounding grid is same.

I hope we can discuss further about this.

Thanks for your help.

Register to Reply
Pathfinder Tags: grounding Neutral NGR transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Grounding for NGR of Transformer

05/28/2017 7:56 PM

What local codes and standards are you working to?

I have built and sold a few of these but never installed them myself, I was under the impression that the earthing just needed to be suitable to handle the expected current at a suitably low ground resistance, but again the local codes and standards should dictate if direct connection to additional ground rods along with the earthing grid is required, along with the required maximum ground resistance.

__________________
jack of all trades
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#2

Re: Grounding for NGR of Transformer

06/07/2017 1:29 PM

In my opinion, according to NEC Art.36 (A) and Art. 30(A)(6) you may connect the high-impedance [resistor] to the "common grounding electrode" that means "to the grounding grid".

__________________
Julius
Register to Reply