LV D.O.L Starter Thermal Overload Position

05/28/2017 11:25 PM

Normally in D.O.L motor starter the thermal or EOCL relay installed after magnetic contactor . why not it is installed before magnetic contactor b/c in this way , some how we even protect the magnetic contactor power contract against damage due to high current.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: LV D.O.L starter Thermal Overload position

05/28/2017 11:46 PM

It doesn't matter. No matter where in the circuit it is located, the overload relay causes the current to shut off through all components of the circuit.

Moreover, there are MCPs (motor circuit protectors), including overload protection, that are installed "upstream" of contactors.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #1

Re: LV D.O.L starter Thermal Overload position

05/29/2017 12:15 AM

Being a standard DOL starter I take these to be your industry-standard contactor and thermal relay combinations.

__________________
jack of all trades
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: LV D.O.L starter Thermal Overload position

05/29/2017 12:13 AM

Because that is how all the combination contactor and thermal relays are constructed.

The thermal relay is a control element only. It switches the contactor coil which in turn opens the contactor and electrically isolates the thermal relay. The thermal relay has no high current switching capability or electrical isolation capability itself, hence it is always down stream (after) the contactor.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#4

Re: LV D.O.L starter Thermal Overload position

05/29/2017 3:03 AM

In my 40+ years of experience I seen Thermal relay only before Magnetic contactor. First time I am hearing this. But it don't matter if it is fulfilling the intended function.

__________________
Subramanyam
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#8
In reply to #4

Re: LV D.O.L starter Thermal Overload position

05/30/2017 12:07 AM

This is the normal Arrangement. Can you send a picture of what you have seen for 40 years.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: LV D.O.L Starter Thermal Overload Position

05/29/2017 12:58 PM

Mounting it ahead of the contactor offers no more protection for the contacts than mounting it behind. Current in a circuit is the same in all parts of the circuit. Since the way a TOL relay functions is to act upon the coil of the contactor, where the sensing elements are is irrelevant.

As to why they are traditionally below the contactor, that is because of the earliest designs and the fact that in many of those early systems, the OL heater elements were replaceable, so if the TOL was ahead of the contactor and the heaters needed replacing, the terminals were live, whereas if down stream if the contactor, they were not. That predates more modern sensibilities about not working on live equipment at all, but the tradition continues. Now however, that would not be an issue.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#12
In reply to #5

Re: LV D.O.L Starter Thermal Overload Position

05/30/2017 12:13 PM

SHOULD not be an issue. Mistakes happen. Having the heaters down stream adds a layer of protection if, because of sloppy workmanship, bravado, laziness or defective disconnect the circuit is still live. Should never happen, but can. OP does not seem to understand that current is current no mater where in the circuit it is measured. - JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#13
In reply to #5

Re: LV D.O.L Starter Thermal Overload Position

05/31/2017 4:20 PM

There are some obscure faults where the overload relay could detect a contactor fault if it was mounted ahead of the contactor, a low level fault not detectable by the upstream fuse, (magnetic) circuit protector or (thermal-magnetic) circuit breaker.

Those obscure faults will eventually escalate so they are indirectly detected by downstream overload sensors, such as high resistance or open circuit on one or two phases. The reaction of the motor will cause the overload relay to trip. A fairly common incident is a loose connection between the contactor load side and the overload relay line side, which creates heat that conducts down to electro-mechanical overload relays, tripping them off, and confusing the techs who always look to the motor first.

Line side contactor loose connections escalate to a much higher level before clearing.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6

Re: LV D.O.L Starter Thermal Overload Position

05/29/2017 1:32 PM

Of perhaps more interest is... the N/C contact of the overload block should be in the feed to the coil and not after the coil connecting the coil to the neutral (return) conductor.

Why? If a coil burned out and managed to short to ground with just the right impedance, it could conceivably allow the coil to stay energized even if the N/C contact were to open. I have seen this happen twice in my career.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: LV D.O.L Starter Thermal Overload Position

05/29/2017 4:53 PM

I agree. However, in reversing and two-speed starters, it has been usual to place the NC contacts after the pair of coils, with red wire between.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#10
In reply to #7

Re: LV D.O.L Starter Thermal Overload Position

05/30/2017 9:15 AM

Yup... seen this arrangement many times.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#14
In reply to #6

Re: LV D.O.L Starter Thermal Overload Position

05/31/2017 4:32 PM

I think that practice arose to make it difficult for someone to inadvertently hot wire out the protection.

To get a motor going, a jumper wire from Hot to the Coil is the midnight fix to keep the process going (in the olden days), so having the O/L relay on the neutral side may have been deemed less risky than a grounded coil. I haven't been doing this long enough I guess to see a grounded coil bypass an overload relay, but certainly possible & plausible. On the other hand, I have seen lots of midnight hot wired motor starters (Who me?), especially when no one thought to publish the interlock list, or the button on the control panel is buried in a sea of 120V open terminals (old US style).

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: LV D.O.L Starter Thermal Overload Position

05/30/2017 4:33 AM

Because the motor overload isn't there to protect the contactor; it is there to protect the motor. It is the FUSES that are there to protect the other components in the circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #9

Re: LV D.O.L Starter Thermal Overload Position

05/30/2017 10:44 AM

...principally the cables...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Alanvaderi (1); Circuit Breaker (1); jack of all trades (2); JRaef (1); kvsubramanyam (1); North of 60 (2); PWSlack (2); rwilliams (2); Tornado (2)