Overhead Line Testing

05/28/2017 2:05 PM

Hi

We have just constructed a New transmission line having Rail conductor 132kv double vertical circuits line, and now we performing HI-POT 80kv test which is the common practice in my country before line energize , when I perform the test in the small section of the line (Hi-Pot phase to ground) the maximum voltage reach and stand 60kv and in next portion its goes in 8kv only, what is the reason, is this device fault ? or line have some fault but why its even goes 8kv ? if line have some fault ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: overhead Line Testing

05/28/2017 2:39 PM

My guess would be broken or dirty insulators. Maybe if you run the test at night, you might be able to see the fault.

Reply Good Answer (Score 2)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4
In reply to #1

Re: overhead Line Testing

05/28/2017 4:17 PM

Words fail me sometimes, what the heck are people being taught now days that simple analysis and fault finding techniques are beyond some people and have to be outsourced.

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #4

Re: overhead Line Testing

05/30/2017 6:06 AM

...to anonymous strangers who cannot see the installation, have no financial interest in it, and, at the time of writing, have no idea where on the planet the problem is located.

It is absolutely astonishing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#2

Re: overhead Line Testing

05/28/2017 3:37 PM

Your electric utility company may benefit from using a DayCor camera. If you've any arcing, excessive corona in your system this camera will find it. (I am not connected with DayCor's mfr in any way)

Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1366
Good Answers: 105
#25
In reply to #2

Re: overhead Line Testing

05/31/2017 5:22 PM

I like the Rail system they have, but may not be sensitive enough to detect hipot discharge, with generally limited current available. I tend towards IQ Post 24, where you just put the boots to it, and back-check with your DayCor, if the insulator string doesn't flash over. The Preventive Maintenance possible with that, combined with thermographic data, would make you both efficient and reliable.

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: overhead Line Testing

05/28/2017 4:13 PM

What else could it be but your insulators?

Check your insulators.

__________________
jack of all trades
Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#19
In reply to #3

Re: overhead Line Testing

05/30/2017 10:52 PM

There is a LOT of air to be checked.

Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#20
In reply to #19

Re: overhead Line Testing

05/30/2017 11:28 PM

I think I found his problem

He said overhead line testing, right?

Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#5

Re: overhead Line Testing

05/28/2017 7:36 PM

I too would post this question as an "AP"! Common sense would tell you are not qualified to work with HV, but stupidity tells you to continue on and go to an anonymous forum and seek answers!

Hopefully, you live to tell about it!

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #5

Re: overhead Line Testing

05/28/2017 8:10 PM

I am starting to wonder if this is partially a cultural thing where some people are just too afraid to lose face (or something similar) by asking a more senior engineer on site a question and so resort to asking on online forum instead.

We are not talking toys and games here. The MW level power generation and high kV transmission-level power line selection and fault finding questions like these asked on CR4 recently should NOT be this common.

What's going on out in the industry that could be causing this? Is this common and CR4 is just becoming more popular and attracting more of these questions.

__________________
jack of all trades
Reply Score 1 for Good Answer
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#7
In reply to #6

Re: overhead Line Testing

05/28/2017 8:30 PM

This is becoming too common here on CR4. But if you think about how some countries string their lines, it's amazing that the magic smoke hasn't appeared sooner, taking the continent's power grid out of service

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#8
In reply to #6

Re: overhead Line Testing

05/28/2017 10:09 PM

I tend to agree - it may be a cultural thing. Could also be they work for a harsh superior who's unapproachable and so feel safer asking elsewhere anonymously.

There are also areas in the world where professional training isn't accessible for any number of reasons, and so people are trained by being thrown to the wolves. I suspect this is the case more often than not.

I don't think it'll hurt us too much to help these folks out. There was a time when I knew diddly squat about my field (and about many, many subjects I still do), and so being able to ask someone was a huge help. Sometimes all I needed was just one tiny little key piece of information and the rest of it all fell into place.

The way I look at it, I give them credit for asking. The ones who don't ask, who think they know what they're doing (but don't really, and don't know that they don't know), are the really dangerous ones. Those and the ones who come here repeatedly with questions but don't learn anything. We've a few of those, yes.

Reply
Anonymous Poster #2
#14
In reply to #8

Re: overhead Line Testing

05/29/2017 3:51 PM

You didn't belittle the original poster nor actively insult him or her nor try to degrade their environment. A breath of fresh air. Thanks.

Reply Off Topic (Score 5)
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#9

Re: overhead Line Testing

05/29/2017 12:38 AM
__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#10

Re: overhead Line Testing

05/29/2017 8:30 AM

Do you have any power factor compensation capacitor on the line?

You didn't specify if your test was conducted with AC or DC.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Reply Score 1 for Good Answer
Anonymous Poster #1
#12
In reply to #10

Re: overhead Line Testing

05/29/2017 2:03 PM

it is DC

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#13
In reply to #10

Re: overhead Line Testing

05/29/2017 3:41 PM

On a (test isolated) section of 132kV overhead transmission line? Are you sure? Can you provide a link of an example.

__________________
jack of all trades
Reply
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#11

Re: Overhead Line Testing

05/29/2017 9:54 AM

AC or DC Hi-Pot? There may be more than "the next section" in the test circuit unless it is isolated or sectionalized in some manner. You are likely seeing the effect of charging current over a much longer section of the transmission line than you realize.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15

Re: Overhead Line Testing

05/30/2017 4:39 AM

The answer to the three questions is "It doesn't matter". The test failed. End Of.

So the only thing to do is to investigate why the test failed, carry out an appropriate remedy, and repeat, until the installation passes the test. It could be anything.

As the installation and the test equipment cannot be seen from here, the investigation, and the remedy/ies, are all in the domain of Anonymous Poster #1.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#17
In reply to #15

Re: Overhead Line Testing

05/30/2017 3:04 PM

Test is not failed, its just not upto the mark ., as leakage current in 40mA at 80kv or some times leqkage current is more then 40mA but voltage only 1 or 2kv and equipment get tripped, and this is also happening specially in night .

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#18
In reply to #17

Re: Overhead Line Testing

05/30/2017 3:15 PM

Then what's different at night do you think? Increased moisture in the air perhaps causing a path to ground through a faulty insulator? <hint> <hint>

__________________
jack of all trades
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#23
In reply to #17

Re: Overhead Line Testing

05/31/2017 4:40 AM

Why bother testing at all? Why not just energise and be done with it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#26
In reply to #17

Re: Overhead Line Testing

06/01/2017 9:12 AM

<...its just not upto the mark...> So which side of the pass/fail boundary is it, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#21

Re: Overhead Line Testing

05/31/2017 12:23 AM

Too bad "they" (he/she) posted as an "AP", we have no clue about where in this world they reside in and what climate they're dealing with, moisture, dust, bird droppings- the list goes on ...... Sounds like a homework question to me

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#22
In reply to #21

Re: Overhead Line Testing

05/31/2017 2:34 AM

Hmm...I dunno. Homework questions are usually a bit too 'tidy' and clear-cut. I tend to suspect this is a real, in-the-field situation.

Reply
3
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#24

Re: Overhead Line Testing

05/31/2017 9:31 AM

Rail conductor? Can you elaborate? AAAC ACSR, HTLS, but rail conductor?

1. 80KV is not the right pressure test voltage for 132Kv by any means. Try 198Kv minimum for 1 hour per line section and all you might do is test some insulators.

2. The 8KV (52kV drop), is due to the line length.

3. Do not take the results as serious tests, as the test you are trying to perform is totally pointless.

Just connect the line to the busbar supplying 132kV and leave it to soak for 24hrs. You do not have a sufficiently large pressure test unit (Hi Pot Tester), for the line length you have. If the line holds on 132kV for 24 hrs with no tripping, you can then energise the line for load.

Seriously, you are testing nothing, proving nothing at 80kV, on a long line, double circuit. Your 80Kv is only good for pressure testing 33kV cables up to 6km long.

Reply Good Answer (Score 3)
Anonymous Poster #1
#28
In reply to #24

Re: Overhead Line Testing

06/05/2017 1:30 PM

thanks for the reply

Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#27

Re: Overhead Line Testing

06/02/2017 9:38 AM

Is it in all phases?In both circuits?Try Isolating the sections,I mean disconnect the jumpers at angle towers and take only a section at a time.Weather makes a difference but values are very low even otherwise

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply Score 1 for Good Answer
Anonymous Poster #1
#29
In reply to #27

Re: Overhead Line Testing

06/05/2017 1:32 PM

i did this , now line only 2km in length and insulators also cleaned but leakage current is too much and at night no voltage applied ? not more the 1kv

Reply
Guru

Join Date: Jul 2016
Posts: 1366
Good Answers: 105
#30
In reply to #29

Re: Overhead Line Testing

06/05/2017 1:55 PM

So above 1kV DC power, you exceed the current output rating of your hipot set (?).

As asked before, do all 3 phases show the same behavior?

I've never hipot tested an open line. Insulated HV cable, yes, to prevent excessive and perhaps un-repairable damage to insulation/stress cone, or prevent a fire in the middle of a cable tray, in the case of pulling/install or manufacture defect.

Risk of excessive or consequential damage beyond blowing apart or flashing an insulator string you should be able to confirm & evaluate, and decide whether to energize at full voltage,

Isolate to smaller section, one that you know you can charge successfully,

Or get a bigger hipot.

Reply
Anonymous Poster #3
#31
In reply to #29

Re: Overhead Line Testing

06/06/2017 2:35 AM

Just try charging the line with rated voltage.See whether it stands.At best Breaker will trip and may be the bad insulator show up.By the way Is it a Tee Off Line?

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#32

Re: Overhead Line Testing

06/09/2017 1:42 PM

Seems elementary but...

Your 80 kV tester may have enough current to test one insulator or transformer but not miles of line - the first line section you tested may be short and the next long.

Tell us the line length and test set current capacity @ 80 kV and maybe a line guru will appear.

Reply
Reply to Forum Thread 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Andrew Westman (4); Anonymous Poster (6); Bluestone (1); Brave Sir Robin (1); dj95401 (4); IQ (1); jack of all trades (5); marcot (1); nesubra (1); PWSlack (4); Rixter (1); rwilliams (2)

Previous in Forum: Vector Parallel to the Line   Next in Forum: Grounding for NGR of Transformer

Advertisement