Electrostatic Precipitator

05/31/2017 5:13 AM

Recently we have renovated two chambers of our ESP with new collecting and emitting electrodes and also changing to 3 phase transformers.This is for our clinker cooler ESP in our cement plant.Supplier assured the performance at less than 300 Deg Centigrade temperature at the inlet of ESP .Ours is a 3 field ESP and we renovated only two fields and 3rd field is left untouched.When we charged the ESP,we observed that 1st field is getting charged and working well upto 300 Deg,Centigrade. 2nd field is working well upto 270 Deg Centigrade Temp. Beyond 270 Deg.C Temperature,the 2nd field transformer is not developing any KV. The supplier wants us to change the old support and shaft insulators for the 2nd field to work upto 300 Deg Centigrade.These insulators developed very small cracks ,but with these cracks also,the ESP is working well before renovation.Request your help for clarification and guidance..Thanks.NVRSrinivas

Register to Reply
Pathfinder Tags: ELECTROSTATIC PRECIPITATOR
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Electrostatic precipitator

05/31/2017 5:25 AM

What's wrong with following the guidance already received, then?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Sep 2013
Posts: 59
#6
In reply to #1

Re: Electrostatic precipitator

06/01/2017 8:59 AM

Why we are hesitant to change insulators is even the supplier is not very confident and also it is a job which can be done in kiln stoppage.We have to procure new insulators also.But the same insulators with this type of small cracks worked well before ESP renovation.Hence,I thought whether any body help me with some different solution.Thanks.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Electrostatic Precipitator

05/31/2017 2:18 PM

If you have a short circuit when power is applied primary current will rise but the voltage won’t, you don’t mention current.

The insulators would have to be badly damaged to cause a fault before the voltage has a chance to ramp up.

More information needed.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Electrostatic Precipitator

05/31/2017 3:37 PM

Judgement call....what's the risk vs reward...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Electrostatic Precipitator

05/31/2017 5:05 PM

To replace the insulators isn’t a quick job and can’t be done with the kiln running. That is unless the OP totally ignores any emission limits and vents the cooler direct to atmosphere. Most of the recovered cooler exhaust material can be returned to the kiln as usable feed stock, a costly exercise if it’s vented, even worse if you get nailed for pollution.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Jun 2016
Location: Chagrin Falls, OH
Posts: 26
Good Answers: 6
#5

Re: Electrostatic Precipitator

06/01/2017 8:56 AM

Change the old support and shaft insulators, especially if they have developed very small cracks. Even without cracks, the insulators can form carbon traces on their surface that will leak off current to ground. Good maintenance practices should be observed to clean the insulator surfaces on a regular basis. With cracks in the insulators, it is much more likely that carbon traces will form and leak off current to ground.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2016
Location: Chagrin Falls, OH
Posts: 26
Good Answers: 6
#7

Re: Electrostatic Precipitator

06/01/2017 10:36 AM

Although I am not an electrician, I have another thought. Perhaps your three-phase service is old or rural like mine having only three incoming conductors. I believe this may be referred to as an ungrounded "delta" service. A consequence of having such a service is a "floating" neutral. A floating neutral means the neutral point is not earthed and is determined by the load on each phase, so it may virtually float around in potential. If the loads on each phase are perfectly balanced, the neutral point will be at zero or ground potential and will behave no differently than three-phase service having four incoming conductors, one of which is a neutral point to earth ("star" service?). However, in an ungrounded delta three-phase service, if the load is not balanced, or there is a short or "leak" to ground in one or more of the phases (such as a carbon trace on an insulator), the floating neutral point will not be at zero or ground potential. It will rise to a potential greater than zero volts. This will cause the voltage in the remaining phases to become much higher in value and, as a consequence, cause insulators to break down and possibly arc, creating new ground traces and a vicious circle of chasing such problems. How to "fix" such a system? I'll leave that to the electricians. I think I read somewhere that a corner of the delta can be grounded or a delta-delta transformer can be used and have a point between two legs taken to earth, but again, I am not an electrician, so don't go by what I say, let an electrician weigh in.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#8
In reply to #7

Re: Electrostatic Precipitator

06/01/2017 11:37 AM

I was thinking the same thing, your new 3 phase service for the TR Sets probably has a power system ground reference your old single phase system did not have.

If the new TR Sets are auto-transformers, but the old TR Sets were fully galvanically isolated transformers, then your supplier cut a corner perhaps inadvertently, not realizing that your previously leaky insulators had only capacitive coupling to ground (ungrounded system).

With your new power system, a ground in the insulators systems is easily detected, thereby shutting down the supply when the leakage current gets high.

Going back to ungrounded operation may be possible, or you might add a transformer to isolate the TR sets from power system ground, or fix the insulators. The collection efficiency grounded/ungrounded should be the same, maybe a little better ungrounded, as you won't be charging the grounded precip casing, very small amount, depending on your ripple.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#9

Re: Electrostatic Precipitator

06/02/2017 1:55 AM

In my opinion gas temperature decrease the particle resistance.

If the new installation it is rated for less electrode number the reactor cannot limit the current at this elevated temperature and the voltage controller shuts-down the supply.

On the other hand the insulator cracks could increase the current -as if there are more electrodes than it was designed.

I think the manufacturer has to double check if the new installation corresponds the existing number of electrodes and the customer has to replace the insulators.

It may be also an equipment failure and the dissolved gas in oil has to be checked.

__________________
Julius
Register to Reply
Member

Join Date: Sep 2009
Posts: 7
Good Answers: 1
#10

Re: Electrostatic Precipitator

06/05/2017 9:17 PM

Do you progressively loose KV as the temperature increases or is all well until reaching 270° C and then a complete loss of KV (dead short)? With the field having been rebuilt I'm wondering if there is a thermal expansion problem within the chamber which brings emitting and collecting systems close enough to short at that temperature. For example a single collector plate with a minor variation in mounting location (or an un-slottted bolt hole) may be restrained relative to its neighbours causing it to bow out across towards the emitters. There are many close approach locations between the two where minor variations can lead to contact - and can be very frustrating to locate and correct.

270° C is well below fusion temperature of any carbon/carbonate dust in the insulators so not sure why insulator failure (tracking) would be affected by that temperature - would more expect to see an inability to reach full KV at any temperature. Unfortunately to find an expansion problem means not just shutting kiln but cooling sufficiently for internal entry to the chamber. If you do need to do this and know you already have some insulator cracking, then it would be prudent to at least be prepared to change them at the same outage.

You may also want to consider using airborne ultrasonic to "listen" for sounds of arcing / corona at the insulators while on line as one means to determine whether that may be the problem.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2013
Posts: 59
#11

Re: Electrostatic Precipitator

07/19/2017 6:55 AM

Further to continuance to my earlier topic Electrostatic precipitator,we have purchased new support insulators and we are going ahead with the replacement of old insulators job. Simultaneously,we have done open circuit test of the transformer and we have observed that the ESP controller panel is feeding 3 phase voltages with large variation to the transformer.

RY phase 389 volts

RB phase 369 volts

YB phase 461 volts

So,When we are increasing the voltage on primary side,when the primary voltage of transformer is attaining 380 volts and further,we are seeing voltage hunting and small typical noise from the transformer.The supplier says the voltage variation is alright for the transformer.But I am worrying it will have implications on losses,harmonics and transformer life.Kindly guide me with your advise.Supplier's point is when ESP field is connected to transformer,voltages are not full and that time,voltage difference between phase to phase will be around 30 volts only approximately.How much voltage imbalance is tolerable for power transformer.

Best Regards,

NVRSrinivas

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#12
In reply to #11

Re: Electrostatic Precipitator

07/19/2017 1:11 PM

As long as you're not running rotating machinery (induction motors) from that unbalanced source voltage, that is what will suffer due to unbalanced voltage. It is important to watch your supply system voltages in that case.

The harmonic content of your rectifiers and fields was already factored into the sizing of your transformer, assuming that the load hasn't really changed from design.

The heat load in your transformer is the sum of the 3 phases, but that 3 phase TR Set was designed for precipitator service, so the engineers who applied the equipment already understand the possibility of unbalanced field loading.

They may have a specification for what the maximum unbalanced load on the transformer is, which should allow some overload on a particular phase, providing the other two phases are lower than rated. There is some limit to the heat removal from one set of windings in the group, so would be limited that way.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers: