Single Current Transformer on Parallel Loads - Effect of Low Power Factor?

06/01/2017 8:12 AM

Hi guys,

I'm trying to simplify a control and monitoring circuit for tandem pumps. These have one submerged pump, which pumps to another inline pump. I have previously controlled the two pumps individually, this requires software interlocks and timings. My device measures the pumping efficiency (energy used / volume pumped) - so I really need to consider the energy used by both pumps. In my mind, it will be much simpler and more accurate if I treat the whole pumpset (both pumps together) as one device. There has to be hard-wired interlocks and timers for manual and backup operation anyway, why duplicate it all?

My question is in regards to the measurement of current and power factor for the pumps. They are fed from the same supply, but I probably won't be able to find a single branch that feeds both pumps only. So I'll need one set of CTs at the top of each of the two starters, paralleled into a single input on my instrument. Using parallel CTs into a single instrument doesn't seem to be a problem (https://ctlsys.com/support/paralleling_current_transformers/), but what happens when one pump goes out of spec? e.g. The dry pump will be working fine, but when the wet pump draws air, it's power factor will drop off. I'm expecting a phase shift on the current for the wet pump only, is this going to manifest at the instrument as a power factor drop also (but only by half as much?)?

I'll also have to adjust my motor protection thresholds to suit - e.g. if one pump goes over current by 15% but the other is OK, that will only add 7.5% to the total current.

Has anyone configured a system like this before, any pointers?

Thanks for your help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 8:46 AM

You could use two CT’s and a summation transformer.

http://www.rayleigh.com/current-transformers/summation-current-transformers.html

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Commentator

Join Date: Apr 2008
Posts: 59
Good Answers: 2
#5
In reply to #1

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 9:28 AM

Yeah, looks good. The link I posted in the question indicates that CTs can just be paralleled with no transformer.

What's going to happen to the PF though when the PF of one load drops?

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#7
In reply to #5

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 10:03 AM

What's going to happen to the PF though when the PF of one load drops?

If the secondaries of the CT are paralleled, the resultant current will be the sum of the two, according to Mr. Kirchoff. Each pump current will be a vector sum of the current in phase with the voltage and 90 degrees out of phase with the voltage. So the paralleled CTs will output a current that will be the vector sum of the total current in phase with the voltage and 90 degrees out of phase with the voltage.

So, the bottom line is, you will see a partial phase shift if one pump starts sucking wind, and a further phase shift if both do.

Caveat: I am assuming that both pumps are on the same voltage phase. (If you have 2 phases, 180 degrees apart, you could reverse one CT.)

Register to Reply
Commentator

Join Date: Apr 2008
Posts: 59
Good Answers: 2
#8
In reply to #7

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 10:11 AM

Yup, all 3-phase pumps fed from the same feed.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 8:49 AM

So, what's wrong with a low-level switch to cut off the pumps? Why bother with power factor and all its complexity?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Apr 2008
Posts: 59
Good Answers: 2
#3
In reply to #2

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 9:20 AM

Power Factor isn't a complexity at all, it's part of the standard offering of our product (http://www.multitrode.com/products/multismart-and-probes/multismart-pump-station-manager-and-rtu/), you just need to tick a box and it's enabled with a default of 0.6, which can be adjusted.

My problem is what will happen when only one of the parallel loads goes low PF....

There might well be a Low Level Float which will disable all pumps as well - but drawing air is not the only time you can get a low PF. These are sewage pumps, so they can get ragged up, which will result in a low PF. (We automatically reverse the pumps to clear the blockage then restart.)

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #3

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/02/2017 1:05 PM

<...These are sewage pumps, so they can get ragged up...automatically reverse the pumps to clear the blockage then restart...> Well, that wasn't revealed at the initial posting.

Trying to pump rags is a Bad Thing.

Rate of drop of level in the wet well is another way of doing it.

Changing the pump for a Hidrostal "pre-rostal" type of pump (usual disclaimer) means the pump won't get damaged by either rags or air.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 9:21 AM
  • If the first pump starts pumping air, then won't the second as well?
  • If the current in the first pump goes to 115%, what is there to trip it off and prevent its being converted into a convector heater?
  • What has accuracy got to do with anything?

From here, this installation looks like the proverbial sledgehammer to crack the proverbial nut!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#9
In reply to #4

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/02/2017 10:59 AM

Summing the kW & kVAR for each pump will decrease the sensitivity of your Power Factor Low Flow Pumping Detection instrument, since you will be treating the two motors as a lump value, as asserted many times above. However, to the point PWSlack made where it is likely that eventually both pumps will be pumping air, eventually you will detect low flow.

You could also use a low kW setting instead of Power Factor, but then you'd need to know the pump & motor rating, and normal performance, to detect low flow. Think of Power Factor as the same thing, with the same reduced sensitivity due to lumping the values.

If the device is used for motor thermal protection, then summing the currents is a bad idea.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6

Re: Single Current Transformer on parallel loads - effect of low Power Factor?

06/01/2017 10:00 AM

You can parallel CTs to measure the total current to the two pumps. We do it all the time in substation applications where two breakers feed one line (such as ring bus or breaker-and-a-half schemes), in which CTs on each breaker are summed together for metering and protection relaying. However, I don't think it is that easy for your power factor measurement. You have to know what the vector sum of the two currents is for your abnormal condition to determine what PF you should trip at. It is not as easy as saying that 0.85 PF for one pump and 0.45 PF for the other will give a 0.65 PF at which you want to trip (or something like that). And if there are a variety of possible scenarios for each pump's PF, you may not be able to define a specific go - no go condition. You'd be better off if you could run each CT into its own input, and be able to adjust settings for each input to trip the pumps when PF on either one is out of whack.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11

Re: Single Current Transformer on Parallel Loads - Effect of Low Power Factor?

06/03/2017 12:19 PM

Seems to me you want to measure kWh to two pumps with one device having one current input per phase but also try and protect two motors at the same time with the same device.

This will give you heartache if one pump is sucking air and the other is dragging rag and combined power still looks normal. The customer will blame you if you give inferior protection to standard solutions which give separate monitoring and protection to each motor.

So far as summing accuracy is concerned, low power factor makes higher CT phase errors and hence kW errors on top of your metering double the current, so change due to only one motor is less definite.

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Critcho (3); PeterT (1); PWSlack (3); Rixter (1); rwilliams (1); TonyS (1)

Previous in Forum: Electrostatic Precipitator   Next in Forum: Phase Indication Lamp Flickering in HT Panel

Advertisement