Installing Capacitor Banks in LT Diesel Generator Circuit

08/20/2007 2:31 AM

We r running low tention DG of 250 kva capacity . Can we insatall the capacitor banks to reduce the kva loading ?? The load is of varying nature i.e. crane , welding transformers , lighting , batching plants etc. During operation of DG , the PF varies from 0.6 to 0.98 within few seconds . The load on generator as observed is less than 50 % of the rated capacity . So, pl suggest in this regards .

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: installation of capacitor banks in LT Diesel Generator circuit

08/20/2007 5:10 AM

No.

If you have automatic voltage regulation on the gen set any attempt at pf correction will upset working of voltage regulator.

Reply
Commentator
India - Member - Electrical Energy

Join Date: May 2007
Location: Tamilnadu
Posts: 57
#2

Re: Installing Capacitor Banks in LT Diesel Generator Circuit

08/20/2007 1:01 PM

The DG set is operating at 0.8 power factor lag.The Capacitor is required for Voltge improvement for the line losses.The capacitor addition will derate the capacity of DG Set.So you should not connect the DG Set with capacitor bank.More over sine wave of genaration will be distorted which results equipments get damaged.

Reply
Commentator

Join Date: Aug 2007
Location: INDIA
Posts: 58
#3

Re: Installing Capacitor Banks in LT Diesel Generator Circuit

08/20/2007 4:27 PM

Hello,

At first i suggest u dont use capacitor for D.G. Alternator of Diesel Generators systems are rated for 0.8pf Lag. We can not add uncontrolled reactive ( Capacitive ) compensation for DG. If in case of power factor of system goes to leading, then there is every chance failure of windings

__________________
TARGET - Where many stop thinking, some start from there. Tenacity to get target helps to WIN.
Reply
Guru

Join Date: Jan 2007
Location: Sitting directly behind my keyboard in Albuquerque - USA
Posts: 592
Good Answers: 19
#4

Re: Installing Capacitor Banks in LT Diesel Generator Circuit

08/20/2007 11:36 PM

You can purchase power factor controllers commercially (reactors). We use them all the time on drilling rigs which run at 0.2 PF. 7-8 MW at 0.2 PF is a ton of amps and heat. We have swings from 0.2 to 0.95 with the average at 0.6. Low power factor numbers like 0.2 heat up the rotor more than the stater. At 0.8 PF the generator people wind and cool the stater and rotor to be at the same temperature rise. Anything off of the 0.8 standard rating will heat the rotor as the regulator field forces the poor girl to keep voltage dip in control due to recirculating magnetism throwing some harmonics on the sensing lines. You can even buy reactive load banks to match your resistive load banks when you test generator sets. The engine only sees watts, so controlling power factor will not save you any fuel. It will keep the generator cooler. 1000 kW at 0.9 PF will burn as much fuel as 1000 kW at 0.2, but, the amps will toast your alternator at 0.2 if it is not rated for it. For low power factors I specify a 20% sub-transient reactance generator (high impedance windings) to limit current draw at these excursions. You can also look into a permanent magnet generator on the back of your rotating rectifier (your alternator may be designed to add this) and this roatating magnetic field produces AC voltage to power your regulator so the regulator line power voltage is free from harmonics and will not shut off the regulator during a short circuit.

I hope this helps.

__________________
If it eats, it's going to be trouble!
Reply
Anonymous Poster
#6
In reply to #4

Re: Installing Capacitor Banks in LT Diesel Generator Circuit

08/22/2007 8:22 AM

Hi Petropower,

Recently, a 500 kW - 480 V 3 ph new DG plant, shut-off 3 minuts after start by inverse power when start a 180 HP ESP. The HV side of SUT has one capacitor Y bank 5 kV - 3x2x5 microfarads.

Can we discuss this question please?

Please answer to Serca_2@hotmail.com

Thanks.

Reply
Associate
India - Member - New Member

Join Date: Mar 2007
Location: India Bangalore
Posts: 40
#5

Re: Installing Capacitor Banks in LT Diesel Generator Circuit

08/21/2007 11:58 PM

All the Alternators are rated for .8pf. The true power limit is KVAX.8. In order to limit the reactive power,We may have to adopt real time compensation rather than fixed compensation. As you increase the power factor the de-ration of DG starts to increase.

Hence we may have to check & balance KVA gained and de-ration.

I have seen some real time dynamic reactive compensator, which will provide reactive compensation for both lag and lead depending on the input signal it gets from output. It is PWM IGBT based compensator with capacitors.

__________________
Nothing is impossible, Impossible is nothing
Reply
Anonymous Poster
#7

Re: Installing Capacitor Banks in LT Diesel Generator Circuit

09/22/2010 11:48 AM

I recently bought new diesel generators, and was pleasantly surprised by the speed and reliability of service I received from http://www.gopower.com/
Their diesel generators are built with the highest quality diesel engines in the world. The safety aspect of a diesel generator is also substantial. The diesel used in a diesel generator set is not flammable as it must be compressed in order to ignite.

Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: Installing Capacitor Banks in LT Diesel Generator Circuit

01/16/2014 9:48 AM

Instal AUTO POWER FACTOR CONTROLLER, with a set point as 0.92 Lag

DHAYANANDHAN.S

Reply