Electrical Switchgear

06/23/2017 5:43 AM

I want to know about difference between AC1 and AC3 rating in contractors? Why we use AC3 rating of contractor in inductive load motor?

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #2
#1

Re: Electrical Switchgear

06/23/2017 5:50 AM

About 49,600 results (0.42 seconds), using Google...

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Electrical Switchgear

06/23/2017 6:43 AM

<...AC3 rating of contractor in inductive load motor?...> It stops the starting current blowing the contacts to smithereens, and thereby ensures a comfortable relationship with the facility's fire insurance company.

Define <...we...>, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Electrical Switchgear

06/23/2017 7:18 AM

..."AC-1 - This category applies to all AC loads where the power factor is more than 0.95. These are primarily non-inductive or slightly inductive loads, such as heating. Breaking the arc remains easy with minimal arcing and contact wear.

AC-3 - This category applies to squirrel cage motors with breaking during normal running of the motor.
On closing, the contactor makes the inrush current, which is about 5 to 7 times the rated full load current of the motor.
On opening, the contactor breaks the rated full load current of the motor."...

http://www.schneider-electric.us/en/faqs/FA120833/

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4
In reply to #3

Re: Electrical Switchgear

06/23/2017 1:35 PM

Inductors make life so interesting.......especially when it comes to shutting fully loaded ones down. That is when things become the most interesting!

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Reply to Forum Thread 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); NotUrOrdinaryJoe (1); PWSlack (1); SolarEagle (1)

Previous in Forum: Questions Asked of Job Applicants   Next in Forum: Ultra-thin Camera Creates Images Without Lenses

Advertisement