06/27/2017 2:18 AM

what is the reasons of vfd getting tripped by over temperature.We noticed the setting of current rating of motor and power rating is lower than actual. And during running it is taking more than actual current.

motor rated current entered in vfd is 169 A ,actual is 269 A

motor running current is 196 A

motor rated power entered in vfd is 110 KW, actual is 150KW.

If the parameter entered in vfd wrongly, Is it lead to over temperature of vfd?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: vfd

06/27/2017 2:52 AM

What does the evidence suggest?

What did the equipment manufacturer suggest during the telephone discussions?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: vfd

06/27/2017 3:17 AM

Is this the <...vfd...> that is powering those mechanically-jammed stern thrusters?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jun 2017
Posts: 10
#3
In reply to #2

Re: vfd

06/27/2017 3:39 AM

No, this ia for engine room fan

J

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: vfd

06/27/2017 3:50 AM

So, what is preventing the fan from turning to the extent that the motor is turning without obstruction, thereby causing its motor to draw too much current and the <...vfd...> to trip out on over-temperature? Whatever it is, it cannot be seen from here!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: vfd

06/27/2017 3:54 AM

Could be any number of problems....

http://www.eng-tips.com/viewthread.cfm?qid=205931

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: vfd

06/27/2017 4:31 AM

When the cause has been discovered and corrected, please do let the forum know what it was.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jun 2017
Posts: 10
#7

Re: vfd

06/27/2017 4:43 AM

while tripping vfd showing error code, as per manual it is high of ambient temperature.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #7

Re: vfd

06/27/2017 5:03 AM

There is no need to repeat the statement in the original post.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#22
In reply to #7

Re: vfd

06/27/2017 12:15 PM

So then, this vfd is located in the engine room that the fan is to cool off? Wow.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#8

Re: vfd

06/27/2017 4:49 AM

What is the difference between actual current and running current?

You said "during running it is taking more than actual current."

then you said actual current is 269A and running current is 196A.

In addition you said that the rated power is 110KW, and rated current is 169A: this indicates a rated Voltage of 651V; is that correct?

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Active Contributor

Join Date: Jun 2017
Posts: 10
#9
In reply to #8

Re: vfd

06/27/2017 4:59 AM

motor is 150 kw ,269 amps.

In Vfd entering data is 110 kw, 169 amps (previously somebody entered).

running time current is 196 amps.,

vessel voltage is 440 v, 60 hz .But running time we checked the parameter in vfd that time voltage is 359 and frequency 50 hz

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10
In reply to #9

Re: vfd

06/27/2017 5:02 AM

So, take the plunge and re-program the inverter correctly!

Sheesh.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12
In reply to #9

Re: vfd

06/27/2017 5:22 AM

The parameters may have been lowered to restrict demand in an attempt to make the VFD/motor combination work.....It's also possible the VFD is not properly ventilated....Is the VFD in an enclosure, is there a forced air ventilation system at work here? Is it possible the ambient temperature is exceeding the rating? What is the temperature rating for the VFD, and what is the ambient reading?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #12

Re: vfd

06/27/2017 5:24 AM

...none of which can be seen from here.

Neither can the commissioning records be seen from here..

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jun 2017
Posts: 10
#14
In reply to #12

Re: vfd

06/27/2017 5:49 AM

ventilation is here big problem , now they operating the vfd panel fully opened and they give two blower support.

we installed a panel ac in the panel and try to run vfd by close the panel , but the panel inside temperature gradually increasing and the panel ac giving alaram when reaching 40 degree and after getting 41 - 42 degree celsius the vfd tripping with high temperature alarm.

panel ac temperature set point is 35 degree, and we tried out at 30 degree, but same tripping, because vfd producing more temperature

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16
In reply to #14

Re: vfd

06/27/2017 6:08 AM

So your trip temperature is set too low...raise it to 50

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #14

Re: vfd

06/27/2017 6:12 AM

Go back to the original design concept and the original commissioning records:

  • Find out why the temperature set point is set to this low value and consider raising it to the original setting.
  • Find out why the inverter current setting is set too low and consider changing it back to the original setting.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#24
In reply to #14

Re: vfd

06/27/2017 12:19 PM

Some of our VFD controls are in a thermostated room (with its own dedicated air conditioner. If you have your controls in the engine room, you are fooling yourselves into thinking that is OK.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#15
In reply to #9

Re: vfd

06/27/2017 5:51 AM

Brother, Why dont you change the parameter values as per the Motor name plate?..is there any problem for that?

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#18

Re: vfd

06/27/2017 8:10 AM

Wait a minute! If I absorbed this correctly you are running a big motor with a little VFD. And you wonder why it overheats?

It is not recommended for that very reason. You should be using a larger VFD and the term is "rated" which means that it is capable. Do not mistake the term actual for rated.

It seems to me that you are saying that the motor is "rated" for 269 A. If you are limiting the VFD to a smaller current, but it is drawing 196 A, then you have a bad mis-match between VFD and motor. It will attempt to create a voltage necessary to accomplish your set frequency and "pull" more current than you want.

You might find a sweet spot at a slower frequency, but I doubt it for this much of a difference between motor power rating and your attempt to limit the power by a setting (or capacity issue) in your VFD.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#19

Re: vfd

06/27/2017 9:27 AM

It appears, old boy, that someone may need to pull up his shorts.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#20

Re: vfd

06/27/2017 10:24 AM

You need an electrical engineer familiar with shipboard systems to thoroughly inspect your electrical system and its ability to handle the load. I suspect that this is an older vessel that has had many additional loads added to it without any regard for the alternator's ability to handle them. Your statement that the voltage is 359VAC, coupled with breakers tripping on overcurrent due to inductive motor loads, indicates severe overloading.

Shipboard systems are isolated systems and usually have specialized excitation systems to provide the extra boost required to start large inductive loads like motors. Unfortunately, the older systems often have difficulty handling the harmonics generated by newer electronics like VFDs, resulting in overheating of other harmonic sensitive equipment such as motors, transformers, and excitation systems; all of which contributes to saturation of the iron leading to excessive heating.

I also suspect that equipment was added without regard to balancing the loads across the phases, leading to large phase current and voltage imbalances which in turn cause massive zero sequence currents (aka Triplens) to flow throughout the electrical system.

Shipboard systems also tend to be ungrounded delta, but as the insulation ages, ground faults start to develop, and add up to wasted current which flows through the ships metal leading to electrolytic corrosion.

Get proper technical help from qualified onsite personnel, not anonymous internet gurus.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#21

Re: vfd

06/27/2017 10:36 AM

Any decent VFD is not going to allow you to run a motor at higher amps than the VFD is rated for, and wait for the VFD to trip on Over Temperature, it would trip on over current long before that can happen. I suspect measurement error here, as in someone is using a cheap meter to attempt to read the complex waveforms coming out of the VFD, and the meter is incapable of properly interpreting the real current.

An OT trip on a VFD will be based on thermal sensors attached to the heat sinks themselves. Usually on something that large, there will be several sensors looking for a hot spot value that is just below the junction breakdown temperature of the transistors, typically 185 degrees F (85C). The drive itself is likely rated for 40C ambient operation. If you have an AC unit set to 30C, it is either way too small for the task, or there is another problem. Hard to say anything about the AC unit size because you provided no info. But if we assume someone sized it correctly, then the other possibility is that an internal "stirring fan" on the VFD chassis itself has failed. These are small fans that just move air around inside of the electronics and across the heat sinks to aid in convection cooling to avoid hot spots. If one fails, the cold air of the AC unit may not be enough to compensate. These little fans have a finite life, usually around 80,000 hours for high quality fans, as low as 40,000 for cheap ones, which is under 5 years if running continuously. You get what you pay for and when people buy VFDs based on price alone, this is one of the consequences. If your VFD is 5 years old or more, that might explain the failure, but they can also fail early if clogged up with dust and debris, mold, moisture etc.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#23
In reply to #21

Re: vfd

06/27/2017 12:16 PM

Didn't OP state it tripped on ambient temperature?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#25
In reply to #23

Re: vfd

06/27/2017 4:46 PM

Didn't OP state it tripped on ambient temperature?

I don't know of any VFDs that have a separate ambient temperature sensor, because really, the design is based on an ambient, but the actual problem is really the junction temperature of the transistors. So the only temperature sensors they have is on the heat sinks near the transistors.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#26
In reply to #23

Re: vfd

06/28/2017 12:23 AM

Almost any compartment below deck on a ship has a "high ambient" due to a distinct lack of circulating/cooling air. Unless the VFD is rated for shipboard use, the ΔT between the heatsink and the surrounding air can be quite low, resulting in very poor heat rejection. The problem is exacerbated if the VFD is in an enclosed/poorly ventilated panel with other heat producing equipment in it.

The whole situation is common on older ships where new equipment was added without regard for the impact of internal heat generation/rejection. "Hey Chief, is ok to mount it here? It's the only place I can find any room for it."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#27
In reply to #26

Re: vfd

06/28/2017 3:36 PM

Almost any compartment below deck on a ship has a "high ambient" due to a distinct lack of circulating/cooling air. Unless the VFD is rated for shipboard use, the ΔT between the heatsink and the surrounding air can be quite low, resulting in very poor heat rejection. The problem is exacerbated if the VFD is in an enclosed/poorly ventilated panel with other heat producing equipment in it.

The whole situation is common on older ships where new equipment was added without regard for the impact of internal heat generation/rejection. "Hey Chief, is ok to mount it here? It's the only place I can find any room for it."

Spoken as the voice of experience no doubt. Ambient conditions for locating VFDs is so often overlooked that it's not funny any more. I just had one where a user was complaining that his VFD was tripping on OT ever since it was installed and he had "tried everything" to keep it cool. When I went to look at it, he had mounted the VFD on the side wall of an OVEN! The ends of the heat sink fins were actually touching the walls of the oven, which was operating at 90C continuously. No amount air conditioning was going to be able to overcome that...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: